Does anyone have a good explanation of tandem breakers and WHERE they are authorized for use.

I seem to have this problem OVER AND OVER that licensed ELECTRICIANS have no idea what I am talking about and I try and explain it and they say its OK with the NEC and then I try to tell them its not the NEC its the panel manufacture that dictates where and IF they can be installed and it goes on and on...

I take pictures of the legend on the panel, pictures of the tandem breakers and where they are and ARE not to be installed according to the legend and they STILL seem dazed and confused.

All help would be appreciated.



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/2/11, 12:12 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tandem breaker usage

Russell, you are correct that the label determines if tandems can be used. The NEC rules would be 110.3(B) that items must be used as listed and labeled.

Often times the part number will also show that tandems can be used. For example a Square D part number like QO200M3040 would allow up to ten tandems whereas the QO200M40 would not.
Reply With Quote
  #3  
Old 4/2/11, 1:19 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Tandem breaker usage

I understand this....the electricians don't. Thats the problem! Now I have to find a way to educate them. Thanks for the response



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #4  
Old 4/2/11, 1:33 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tandem breaker usage

Quote:
Originally Posted by rhensel View Post
I understand this....the electricians don't. Thats the problem! Now I have to find a way to educate them. Thanks for the response
Good luck with that.
I sit through 32 hours of CEU classes every new code cycle and I'm frequently amazed at some of the questions that licensed electrical contractors ask.
Reply With Quote
  #5  
Old 4/2/11, 10:17 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Tandem breaker usage

Most of my panels are so old, there is no label left to dictate where or if they go. Im just happy they are the same make.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Federal Electric 100A standalone main breaker -- OK or problematic? fbartlo Electrical Inspections 16 9/6/10 5:17 PM
Re-Inspection apolillo Electrical Inspections 7 11/14/09 7:01 PM
Breaker Question rsole Electrical Inspections 6 11/23/08 9:57 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 9:04 AM


All times are GMT -4. The time now is 8:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts