I was taught that you never tap into the main conductors. Today had a 1989 rancher that has a 32x40 pole barn. Shouldnt there be a breaker in this situation ? Any suggested verbiage is welcome.
Thanks , John G. Jones www.alltechinspect.com |
|
#2
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Its wrong because the tap is the wrong gauge wire. And yes the tap should have its own fuse/breaker.
Most likely there is no room in the panel for this circuit so whoever installed it did it this way. |
|
#3
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Double tapped main feeds considered improper. Recommend repair by a licensed electrician.
Keep it simple and let the electrician figure out how to make it right. |
|
#4
|
||||
|
||||
|
Quote:
I had an inspection where the owner tapped 8AWG wire onto the main lugs Peter Doane Realty Check Inspection Service NACHI ID# 05120681
|
|
#5
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Its very common to see this sort of double tap, at least in my area.
I recently inspected a house that an ESA (Electrical Safety Authority) inspection had been done. Guess what I found when I pulled the main panel cover? You guessed right a double tap on the mains! The vendor was flabbergasted having just paid ESA for a certificate of inspection saying all was okay. Obviously the ESA inspector did not take the cover off. My client was happy too. |
|
#6
|
||||
|
||||
|
Quote:
I will try and get more information this week end and let you know what I find out If I can answer any questions please send me email Roycooke@hotmail.com On an inspection and need immediate help call my cell 613-827-2011 |
|
#7
|
||||
|
||||
|
Most likely there is no room in the panel for this circuit so whoever installed it did it this way.[/quote]
That is the funny part. there is atleast 10 slots not used in this 200 amp panel. thanks for the quick replys, time to finish and send report John |
|
#8
|
|||
|
|||
|
Don't forget to explain to your client that this is hazardous because 1) the terminals are not rated for this use and my arc if the connection is not good 2) the smaller gauge wires can draw too much current and overheat without tripping the breaker and 3) there is no overcurrent protection for the wires in the event of a direct short.
|
|
#9
|
||||
|
||||
|
I think in the verbiage I would keep it flowing and simple.
" Improper tap to the service conductors resulting in a unprotected feeder conductor to the barn and potentially hazardous connection at the termination lugs that were not designed for this type of installation." Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 8:28 PM |
| Subpanel wired as main panel. | jlybolt | Electrical Inspections | 15 | 5/23/07 5:10 PM |
| Main Panel location | dmacy | Electrical Inspections | 5 | 12/6/06 7:32 PM |
| Main disconnect at meter instead of main panel. OK? | kshepard | Electrical Inspections | 14 | 11/8/06 7:24 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |