Default How to tell single from 3 phase

How do youtell if a building has 3 phase electric service. Do you see anything wrong with this.
Attached Thumbnails
tell-single-3-phase-wires.jpg  
Reply With Quote
  #2  
Old 7/18/07, 4:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: How to tell single from 3 phase

The four-conductor service-drop is the indicator. 3-phase.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 7/18/07, 4:45 PM
Kenneth Rentz Kenneth Rentz is offline
InterNACHI Member
 
Join Date: May 2006
Location: Cary, NC
Posts: 61
Default Re: How to tell single from 3 phase

I thought so. Do you think the mast head is turn to far up? Looks like water will get inside. Also these wires are right upagainst the building, it is a block wall.
Reply With Quote
  #4  
Old 7/18/07, 5:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: How to tell single from 3 phase

Personally, I don't like the orientation of the "goose-neck," but I'd be reluctant to say it is not within "compliance." However, one of the conductors looks to be entering on a downhill slope, which would be improper.

As for the conductors. The one's that are touching the block are part of the service drop - i.e., property of the utility company - and were likely attached by employees of the utility company. Generally speaking, utility companies "set their own rules" with regards to their equipment/systems.

If there is no visible damage, I would leave it alone. This is just my opinion. Your mileage may vary



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 7/18/07, 5:38 PM
Kenneth Rentz Kenneth Rentz is offline
InterNACHI Member
 
Join Date: May 2006
Location: Cary, NC
Posts: 61
Default Re: How to tell single from 3 phase

Thanks Jeff that is the way I was leaning. I appreciate your time.
Reply With Quote
  #6  
Old 7/18/07, 5:48 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: How to tell single from 3 phase

Look for water damage at the panel and along the conduit, I can see where water would go back down that (1) line and into the mast head. The orientation of that mast head is wrong as well.



Paul W. Abernathy
Reply With Quote
  #7  
Old 7/18/07, 10:25 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: How to tell single from 3 phase

How about the messenger attachment,as people are always pointing out lack of the ceramic insulator.
Reply With Quote
  #8  
Old 7/24/07, 11:42 AM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: How to tell single from 3 phase

It definitely looks like one of the conductors slopes downward, and at least 2 of them were swung above the insulator connection (why?!?!?!). I'd recommend calling the power company to re-connect them properly, and of course note any signs of water entry into the system and/or corrosion.

Last edited by fbartlo; 7/24/07 at 2:37 PM..
Reply With Quote
  #9  
Old 7/25/07, 12:28 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How to tell single from 3 phase

Pictures can always be misleading. But...from this picture, I would definitely have an issue with the service weatherhead. For issues like this, it is always better to err on the side of safety.
Reply With Quote
  #10  
Old 7/25/07, 12:13 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: How to tell single from 3 phase

You will need to look at the transformer connection to determine whether it is single phase or three phase. You cannot base a determination on the number of conductors because the utility company may not have used the steel cable as the system's neutral. You also need to look at the transformer to determine whether it is a Delta or a Wye connection.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #11  
Old 7/25/07, 12:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: How to tell single from 3 phase

There are four conductors entering the mast-head. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 7/28/07, 6:38 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: How to tell single from 3 phase

The number or size of conductors entering a building does not provide enough information to determine the Voltage, number of phases, or the capacity of the electrical service. Single-phase services will usually have two to four conductors. Two-phase services will usually have three to five conductors, and three phase services will usually have three to five conductors.

There are at least five distinct arrangements possible with a service drop having four conductors. The service can be Single-phase, Two-phase, or Three-phase. The five possible arrangements of a four wire service entrance are Single-phase, Two-phase, Three-phase center-tapped Delta, Three phase corner-grounded Delta, and Three-phase Wye.

For anyone who is interested, I have posted an excerpt from one of my electrical courses, which goes into much greater detail, on my web site at: http://www.bestinspectors.com/electr...vice-types.htm





BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #13  
Old 7/28/07, 9:08 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: How to tell single from 3 phase

Two phase does not exist

rlb
Reply With Quote
  #14  
Old 7/29/07, 1:03 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: How to tell single from 3 phase

A standard residential, single-phase, 240 volt drop, is three conductors. A two conductor system would imply a 120 volt, single phase system. I can usually confirm this when I look into the service panel.

If I see four conductors, I'm thinking "three-phase." I can usually confirm this when I look into the service panel.

I have no idea what a "Delta" is, but apparently I don't really need to know.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 7/29/07, 1:54 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: How to tell single from 3 phase

George, you are spot on. But most home inspectors will never see some of the more interesting power configurations that are found in commercial and industrial installations around the country. The missing information in the original post is what kind of building this is. If this is an appartment building or condos (most of us are probably assuming so), than we are almost certainly looking at 3 phase. If this is a manufacturing facility, well then who the heck knows.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
600 amp single phase service bking Electrical Inspections 3 9/12/07 6:21 PM
single story res. in CA Erik W. Jordan Structural Inspections 7 12/27/06 2:36 AM
New home construction phase inspections dlane General Inspection Discussion 35 6/25/06 10:06 PM
Phase inspections ecox1 General Inspection Discussion 15 3/19/06 11:09 AM
3-Phase Explained ( Commerical Electrical ) pabernathy Electrical Inspections 26 1/6/06 2:53 PM


All times are GMT -4. The time now is 2:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts