Default Terminations of Grounding & Bonding Equipment



The termination of equipment grounding and bonding conductors must be by exothermic welding, listed pressure connectors of the set screw or compression type, listed clamps, or other listed fittings. Sheet-metal screws cannot be used to connect grounding (earthing) or bonding conductors or connection devices to enclosures.

Obervations- As Mr. Holt so well put on this....note that drywall screws or wood screws are not mentioned here as being prohibited in the 2002 NEC.

When the HI is browsing around in the ole' electrical panel have you ever seen nice shinny sheet metal screws wrapped with a EGC or on in the older panels when they TRY to add EGC's doing this...

Why it is a problem ( and personally why the wood screws and drywall screws are also wrong in my opinion even though the NEC does not call it out ) is because the threads on these types of screws to not make enough contact with the enclosure to ensure a good bond...pre-threaded holes do with at all points within the thread count...but not with the screws listed above.

In a situation where their is a fault and it travels through that "sheet metal " screw the lack of contact could provide a less efficiant bond...and could actually loose the effective bond.

Just figured you all would like to know...Educational Moments...

Images Courtesy of Mr. Mike Holt



Paul W. Abernathy
Reply With Quote
  #2  
Old 3/15/06, 9:36 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Terminations of Grounding & Bonding Equipment

Bump.....



Paul W. Abernathy
Reply With Quote
  #3  
Old 3/15/06, 10:57 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Terminations of Grounding & Bonding Equipment

Welcome back Paul



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 3/15/06, 3:56 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Terminations of Grounding & Bonding Equipment

lol......Educational Fella....Only educational....



Paul W. Abernathy
Reply With Quote
  #5  
Old 3/15/06, 8:39 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Talking Re: Terminations of Grounding & Bonding Equipment

...

Better change that last thing I did...DANG!
Reply With Quote
  #6  
Old 3/15/06, 9:28 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Terminations of Grounding & Bonding Equipment

Paul, is it true that when using a #10 machine screw it must be a 10/32 and not a 10/24? We have a er, well I'll just say strict, county inspector here who is always trying to nail us on trivia like this. Last week he grilled me on the thread count on my bonding screws.
Reply With Quote
  #7  
Old 3/17/06, 11:01 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Terminations of Grounding & Bonding Equipment

Brian,

Man, I would think that AHJ would have better things to do...lol....

Anyway the NEC states that the screw should be " Connection means that are listed, are part of listed equipment, or are exothermically welded are required to ensure a permanent and low -resistance connection"

Now the issue he is probably bringing up is if a screw is used that is not designed to work directly with the equipment...much like stated about machine screws and so on...the funny thing is as I believe I posted in another topic...the NEC does not specifically rule out Sheetrock Screws and so on.....just Sheet Metal Screws in the NEC 2002 Verbage....

My opinion would be...I would never use Sheet Metal, Sheet Rock or Wood Screws anyway.....BUT to his point I am sure he is trying to say if the equipment is machined for 10/32 screws ( 32 thread count Spacing ) then anything other than that is not per the manufacturers listing.....

However......I have YET to see an AHJ say anything about this in my everyday experience..so it would be one nit picky AHJ....Here is the deal....When you BUY these unit it is kinda standardized anyway so chances are most all green bonding screws and so on designed for this will meet the manufacturers specs.......he is pushing it a bit.....

has he turned anything DOWN because of this...?



Paul W. Abernathy
Reply With Quote
  #8  
Old 3/19/06, 10:28 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Terminations of Grounding & Bonding Equipment

"has he turned anything DOWN because of this...?" So far he has not caught me up on anything..............

The screws he was referring to were ones I had drilled and tapped into J & P boxes.

He also requires us to install a breaker holdown in the new Cutler Hammer meter combos that come from the factory without one on the backfed main, even though the code says "on field installed backfed devices"
Reply With Quote
  #9  
Old 7/7/06, 10:56 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Terminations of Grounding & Bonding Equipment

Bump....Good Info



Paul W. Abernathy
Reply With Quote
  #10  
Old 12/6/07, 1:26 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Terminations of Grounding & Bonding Equipment

Bump Again...I was looking around and found this.......enjoy !

OPPS...did anyone notice I said Low Resistance Connection....thehehe..Shame on me.....Low Impedance Connection.....Love It...lol



Paul W. Abernathy
Reply With Quote
  #11  
Old 12/6/07, 3:29 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Terminations of Grounding & Bonding Equipment

Quote:
Originally Posted by brian winkle
Paul, is it true that when using a #10 machine screw it must be a 10/32 and not a 10/24? We have a er, well I'll just say strict, county inspector here who is always trying to nail us on trivia like this. Last week he grilled me on the thread count on my bonding screws.
2008 NEC 250.8

(5) Machine screw-type fasteners that engage not less than
two threads or are secured with a nut

(6) Thread-forming machine screws that engage not less
than two threads in the enclosure
Reply With Quote
  #12  
Old 12/6/07, 3:33 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Terminations of Grounding & Bonding Equipment

lol....the date on the original post was PRE-2008 NEC acceptance fella...lol



Paul W. Abernathy
Reply With Quote
  #13  
Old 12/6/07, 3:40 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Terminations of Grounding & Bonding Equipment

Quote:
Originally Posted by pabernathy
lol....the date on the original post was PRE-2008 NEC acceptance fella...lol
yes, ...... and in the 2008 NEC SECTION 250.8 includes this new requirement for anyone who is interested!


(5) Machine screw-type fasteners that engage not less than
two threads or are secured with a nut

(6) Thread-forming machine screws that engage not less
than two threads in the enclosure
Reply With Quote
  #14  
Old 12/6/07, 3:42 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Terminations of Grounding & Bonding Equipment

Most Excellent.......I wish more states would just JUMP right to the 2008 NEC and bypass all the redtape. In Virginia, we wont see the 2008 NEC until about 2010 or 2011...sad to say.....



Paul W. Abernathy
Reply With Quote
  #15  
Old 12/6/07, 3:48 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Terminations of Grounding & Bonding Equipment

I just finished two one day 2005 NEC Changes seminar for a few counties in Virginia, and they said that they are adopting the 2005 NEC in March:

PS: I was also told that the utility company is responsible for most of the service equipment, and the AHJ has no say on this issue, can you expand?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 1:10 AM


All times are GMT -4. The time now is 2:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts