Default This is a test: what's wrong with this common method of wiring?

Anyone?

test-whats-wrong-common-method-wiring-improper-wiring.jpg test-whats-wrong-common-method-wiring-improper-wiring2.jpg test-whats-wrong-common-method-wiring-improper-wiring3.jpg

Photo 1 is in a crawl space.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 12/10/10 at 12:46 PM..
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/10/10, 12:16 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: This is a test: what's wrong with this common method of wiring?

It's a prohibited application of NM wiring. Thats what the photos say anyway...

I see the prohibited hvac wiring at 95% of my inspections.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #3  
Old 12/10/10, 12:18 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This is a test: what's wrong with this common method of wiring?

[quote=jfunderburk;720015]Anyone?


Subject to physical/mechanical damage
Reply With Quote
  #4  
Old 12/10/10, 1:02 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: This is a test: what's wrong with this common method of wiring?

As stated in other post you need to study more Joe . why is everyone coming here for us to do their home work. lol just teasing . to much slack by tank and no protection as the others said .



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #5  
Old 12/10/10, 1:02 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: This is a test: what's wrong with this common method of wiring?

But it is neat. I think a phone guy ran the wires



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #6  
Old 12/10/10, 6:24 PM
Robert Manley Robert Manley is offline
InterNACHI Member
 
Join Date: Oct 2009
Posts: 17
Default Re: This is a test: what's wrong with this common method of wiring?

Are there staples as well, because I have seen these wires be stapled to floor joists.




Robert Manley
7 County Home Inspection, LLC
612-919-3844
www.7countyhomeinspection.com
Thermal Infrared Certified


Reply With Quote
  #7  
Old 12/10/10, 7:00 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: This is a test: what's wrong with this common method of wiring?

lol......I will let you all have at it but think of this....code change and bottom of floor joists in 2008...lol.....not run with the surface of the building....and improperly secured in a few ways...lol..even to itself and.....well...thats enough hints.

let me throw some STUDY code sections at [NEC 2011]

334.15(A)
334.15(B)
334.15(C)
334.30
300.11(C)

enjoy.....can you name any others????



Paul W. Abernathy
Reply With Quote
  #8  
Old 12/11/10, 6:44 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: This is a test: what's wrong with this common method of wiring?

[quote=pabernathy;720248...code change and bottom of floor joists in 2008

...not run with the surface of the building

....and improperly secured in a few ways...lol..even to itself...[/quote]

I think you got it.

I'll have to say I wouldn't feel comfortable calling out that method of wiring in the crawl space as a defect. You never see it in a crawl space run through the floor joists, as the code calls for. A basement is another matter and should be run through the joists in anticipation of a future ceiling.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 12/11/10, 8:35 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This is a test: what's wrong with this common method of wiring?

Quote:
Originally Posted by jfunderburk View Post
You never see it in a crawl space run through the floor joists, as the code calls for. A basement is another matter and should be run through the joists in anticipation of a future ceiling.
If the EC didn't want to drill holes in the crawl space you can simply nail up a few strips of wood and make running boards. Complying with this section isn't very difficult.
Reply With Quote
  #10  
Old 12/11/10, 9:18 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,795
Default Re: This is a test: what's wrong with this common method of wiring?

As Robert mentioned, boards are installed to the bottom of the floor joist and the wiring is stapled to it. That method was used many years ago by electricians that new their trade.

Drilling holes perpendicular to the joist to run wiring is a no no.

Not all basement ceilings get installed. Then you start seeing coat hangers, rope and all kinds of homeowner ingenuities to hang stuff from the wires.

Another area where people like to run wiring is on the face of the girder or main carrying beam.
When the time comes to install a ceiling and wrap the beam for a finished basement, it becomes a problem.

What is so difficult to plan your wiring routes, install a 1x6 board and run the wiring on it and then jump in the joist space to go where needed.

It is all about the green back, takes to much wire.
Reply With Quote
  #11  
Old 12/11/10, 10:06 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This is a test: what's wrong with this common method of wiring?

Quote:
Originally Posted by mcyr View Post

Not all basement ceilings get installed. Then you start seeing coat hangers, rope and all kinds of homeowner ingenuities to hang stuff from the wires.

Another area where people like to run wiring is on the face of the girder or main carrying beam.
When the time comes to install a ceiling and wrap the beam for a finished basement, it becomes a problem.

What is so difficult to plan your wiring routes, install a 1x6 board and run the wiring on it and then jump in the joist space to go where needed.

It is all about the green back, takes to much wire.
IMO there is nothing wrong with running NM cables through bored holes, with the exception of having to actually drill them. And running along a main beam is actually a good idea if you're looking to avoid the drilling or running board methods. In many instances a 1X6 board won't be larger enough to accommodate all of the cabling required to wire a modern home.
Reply With Quote
  #12  
Old 12/13/10, 6:51 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: This is a test: what's wrong with this common method of wiring?

If in the case of pic #1 was there was an incloser , there would be no problem with that type of installation . In fact it is quite common in industial use . In the other two pics the cable of course should be armoured and fastened .



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
  #13  
Old 12/13/10, 7:19 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,795
Default Re: This is a test: what's wrong with this common method of wiring?

Quote:
Originally Posted by Robert Meier View Post
IMO there is nothing wrong with running NM cables through bored holes, with the exception of having to actually drill them. And running along a main beam is actually a good idea if you're looking to avoid the drilling or running board methods. In many instances a 1X6 board won't be larger enough to accommodate all of the cabling required to wire a modern home.
I don't mean to say there is anything wrong with bored holes. There is something wrong with that when they are not strategically located so future upgrades to the basement ceiling is possible.

We all know about the clothes line affect in running nm cable through bored holes all over the place.

Stapleing wires on the beam can be done in the middle and not the top and bottom, so allows for capsulation later if needed.

Wires can run on running boards 6" away from the exterior walls, and not against it. Again allowing for future ceiling up grades.
I have heard about guard boards in my travels here also for wiring going through bored holes to prevent the clothes line affect. Does that ring a bell for you?

Here are a few pics for all, in case it helps.


test-whats-wrong-common-method-wiring-running-cable-framing.jpg

test-whats-wrong-common-method-wiring-wiring-exposed-basements.jpg
Attached Thumbnails
test-whats-wrong-common-method-wiring-nfpa-rough-wiring-floors.jpg  

Last edited by mcyr; 12/13/10 at 7:23 PM..
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/13/10, 7:31 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,795
Default Re: This is a test: what's wrong with this common method of wiring?

Here is the bigger article.

test-whats-wrong-common-method-wiring-nfpa-rough-wiring.jpg

Reply With Quote
  #15  
Old 12/13/10, 7:46 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This is a test: what's wrong with this common method of wiring?

Quote:
Originally Posted by mcyr View Post
I don't mean to say there is anything wrong with bored holes. There is something wrong with that when they are not strategically located so future upgrades to the basement ceiling is possible.

We all know about the clothes line affect in running nm cable through bored holes all over the place.

Stapleing wires on the beam can be done in the middle and not the top and bottom, so allows for capsulation later if needed.

Wires can run on running boards 6" away from the exterior walls, and not against it. Again allowing for future ceiling up grades.
I have heard about guard boards in my travels here also for wiring going through bored holes to prevent the clothes line affect. Does that ring a bell for you?

Here are a few pics for all, in case it helps.

You bring up valid points but I would add that none of them are required by code. Future planning might seem like a good idea but tell that to the average electrician who want's the fastest, easiest and cheapest way to go from point A to point B with his cables.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
No Ground Rod - Sure Test Says Wiring OK away Electrical Inspections 16 6/22/06 1:44 AM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 4:52 AM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM


All times are GMT -4. The time now is 8:42 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts