Besides Broken?
Greg Liebig, Owner Sheboygan Wisconsin Home Inspector 4-Square Home Inspections, LLC Where Knowledge will put your Mind at Ease © Sheboygan, WI 53081 (920) 451-4646 www.sheboyganhomeinspector.com www.4squarehi.com Like Us on Facebook Follow Us on Linked-In |
| Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Ouch. I hope that they have a city water piping system.
|
|
#3
|
||||
|
||||
|
They do, but it appears to be a 10 gauge solid GEC. Home was built in 1964.
Greg Liebig, Owner Sheboygan Wisconsin Home Inspector 4-Square Home Inspections, LLC Where Knowledge will put your Mind at Ease © Sheboygan, WI 53081 (920) 451-4646 www.sheboyganhomeinspector.com www.4squarehi.com Like Us on Facebook Follow Us on Linked-In |
|
#4
|
||||
|
||||
|
It's called a "messenger".
|
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Well if the connections aren't all corroded that might be just big enough to carry the unbalanced current and keep the voltages near 120 volts. |
|
#6
|
||||
|
||||
|
I refer to it as the service-neutral.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
I would called it the grounded conductor being used a messenger cable.
|
|
#8
|
||||
|
||||
|
That was the word I was looking for. In the report, I used Jeff's description as the service neutral conductor (cable).
Thanks! Greg Liebig, Owner Sheboygan Wisconsin Home Inspector 4-Square Home Inspections, LLC Where Knowledge will put your Mind at Ease © Sheboygan, WI 53081 (920) 451-4646 www.sheboyganhomeinspector.com www.4squarehi.com Like Us on Facebook Follow Us on Linked-In |
|
#9
|
||||
|
||||
|
The messenger is the support cable.(just to be clear)
|
|
#10
|
||||
|
||||
|
I have heard the word "common" before.
I still call it busted, and call the Power Company quick. |
|
#11
|
||||
|
||||
|
That electrical service should be turned off immediately! Loss of the neutral is a major cause of house fires. It should be reported to the electric utility company as a need for a emergency repair. As soon as they learn that it is a loss of neutral, they will usually dispatch someone immediately. I tell my clients to get the name of the person they speak with, record the time and date of the call and so on.
The home owner's insurance company will want to subrogate against the utility company after the fire. They will also be willing to pay you to testify on their behalf as a witness of fact. BestInspectors.Net
& Real Estate Training Academy Inspection Report Software for Windows - iOS - Mac - Android Continuing Education Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921 http://www.bestinspectors.net est. 1992 |
|
#12
|
||||
|
||||
|
Quote:
Many do not understand how important the neutral is . Double Taps with a neutral in house panel needs to be written up hard also . ... Roy Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#13
|
||||
|
||||
|
... ditto ...
And the IRC calls is a "grounded bare messenger wire" Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
| Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
I was told the power company went over to repair this yesterday. I would like to revisit the property after the repair to listen to the service panel to determine if the buzzing stopped. It would be an interesting observation. I'll see what I can do.
Greg Liebig, Owner Sheboygan Wisconsin Home Inspector 4-Square Home Inspections, LLC Where Knowledge will put your Mind at Ease © Sheboygan, WI 53081 (920) 451-4646 www.sheboyganhomeinspector.com www.4squarehi.com Like Us on Facebook Follow Us on Linked-In |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Service Neutral Shorted to Mast | pdickerson | Electrical Inspections | 7 | 3/8/10 7:38 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Metal Rigid or PVC Rigid what is code | bpotts | Electrical Inspections | 5 | 12/4/06 2:40 PM |
| Proposed Definition of Neutral Conductor and Point | jtedesco1 | Electrical Inspections | 1 | 4/22/06 10:19 AM |