Old 10/26/07, 11:01 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Is There Anything to Report Here?

This is the exterior heat pump box. They ran a 4 wire feed to the box and combined the neutral and grounds. This is of course a no-no, but the load is 240 volts with no neutral. It seems like the neutral wire, which is not necessary, should dead end at a wire nut. But as there is no neutral current, I suppose it does not matter if the neutral wire is terminated at the ground bus. Does anyone read this differently? Is there any reason to call this out?
Attached Thumbnails
there-anything-report-here-p1030481.jpg  
Reply With Quote
  #2  
Old 10/27/07, 10:29 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is There Anything to Report Here?

You are definitely correct about the bonded neutral and capping it off. I don't like that it is terminated.

Also, I see no connector at the back of the enclosure.
Reply With Quote
  #3  
Old 10/27/07, 10:50 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Is There Anything to Report Here?

The right hand fuse is upside down as well and may have damaged the top fuse clip and fuse reject device.
Reply With Quote
  #4  
Old 10/27/07, 11:19 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Is There Anything to Report Here?

Looks like everyone covered what could be distinguished from this photo. I would point out that if the lid opens easily and exposes those components, that a comment be made about securing the lid. A small lock, a loop of wire tie, etc, to protect curious children.

tom
Reply With Quote
  #5  
Old 10/27/07, 11:30 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is There Anything to Report Here?

Since there is no neutral current present I don't see any real electrical problem. I suppose he could have reidentified the wire green to be perfectly legal. Then it would be "hospital safe".
Reply With Quote
  #6  
Old 10/27/07, 2:02 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is There Anything to Report Here?

The wire could use a proper connector where it comes through the back of the box.
Reply With Quote
  #7  
Old 10/28/07, 11:02 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is There Anything to Report Here?

Conductors of that small of a gauge are not permitted to be paralleled. Even though you have no neutral current, what you effectively have there is a parallel equipment grounding path. The equipment ground is also not permitted to be white... it must be green or bare. That white wire should be capped off to comply with the code, but I'd be hard pressed to tell you that any special hazard is created by letting it remain as-is.
Reply With Quote
  #8  
Old 10/28/07, 12:12 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is There Anything to Report Here?

You can parallel grounding paths Marc, we do it all the time (conduit with a green wire). In fact it is required in patient care areas, hence my reference.
We also reidentify grounding conductors in IG circuits all the time.
If you really wanted to be pedantic and never be able to go back, you could strip it.
Reply With Quote
  #9  
Old 10/29/07, 12:56 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Is There Anything to Report Here?

Thanks for the comments all. The upside down fuse is a new one to me. I didn't realize you could put a fuse in the wrong way. I see the groove at one end of the fuses. I will look for that in the future.
Reply With Quote
  #10  
Old 10/29/07, 8:44 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Is There Anything to Report Here?

For those interested, the following explains reh=hection type fuses:

Class R Fuses
Class R (“R” for rejection) fuses are high performance, ⁄Ω¡º to 600
ampere units, 250V and 600V, having a high degree of current-limitation
and a short-circuit interrupting rating of up to 300,000
amperes (RMS symmetrical). BUSS® Class R’s include Classes
RK1 LOW-PEAK® YELLOW and LIMITRON fuses, and RK5
FUSETRON® fuses. They have replaced BUSS® K1 LOW-PEAK®
and LIMITRON fuses and K5 FUSETRON® fuses. These fuses are
identical, with the exception of a modification in the mounting configuration
called a “rejection feature”. This feature permits Class R
to be mounted in rejection type fuseclips. “R” type fuseclips prevent
older type Class H, ONE-TIME and RENEWABLE fuses from
being installed. Since Class H fuses are not current-limiting and
are recognized by regulatory agencies as having only a 10,000
ampere interrupting rating, serious damage could result if a Class
R fuse were replaced by a Class H fuse. The use of Class R fuseholders
is thus an important safeguard. The application of Class R
fuses in such equipment as disconnect switches permits the
equipment to have a high short-circuit current rating. NEC® 110.9
requires that protective devices have adequate capacity to interrupt
short-circuit currents. NEC® 240.60(B) requires fuseholders for current-
limiting fuses to reject non-current-limiting type fuses.
In the above illustration, the fuse on the right has a grooved
ring in one ferrule, providing the rejection feature of the Class R
fuse in contrast to the lower interrupting rating, non-rejection type.
[IMG]file:///C:/DOCUME%7E1/COMPAQ%7E1/LOCALS%7E1/Temp/moz-screenshot.jpg[/IMG]

More Fuse Info(PDF)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
**HOT** Texas Inspectors use of REI-7A-0 escanlan Legislation, Licensing & Legal Issues for Inspectors 27 11/20/07 12:09 AM
New Report Upload Technology cdemsky Miscellaneous Discussion for Inspectors 49 5/1/07 10:19 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM