This is the exterior heat pump box. They ran a 4 wire feed to the box and combined the neutral and grounds. This is of course a no-no, but the load is 240 volts with no neutral. It seems like the neutral wire, which is not necessary, should dead end at a wire nut. But as there is no neutral current, I suppose it does not matter if the neutral wire is terminated at the ground bus. Does anyone read this differently? Is there any reason to call this out?
|
|
#2
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
You are definitely correct about the bonded neutral and capping it off. I don't like that it is terminated.
Also, I see no connector at the back of the enclosure. |
|
#3
|
||||
|
||||
|
The right hand fuse is upside down as well and may have damaged the top fuse clip and fuse reject device.
|
|
#4
|
||||
|
||||
|
Looks like everyone covered what could be distinguished from this photo. I would point out that if the lid opens easily and exposes those components, that a comment be made about securing the lid. A small lock, a loop of wire tie, etc, to protect curious children.
tom |
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Since there is no neutral current present I don't see any real electrical problem. I suppose he could have reidentified the wire green to be perfectly legal. Then it would be "hospital safe".
|
|
#6
|
||||
|
||||
|
Please Note:
cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The wire could use a proper connector where it comes through the back of the box.
|
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Conductors of that small of a gauge are not permitted to be paralleled. Even though you have no neutral current, what you effectively have there is a parallel equipment grounding path. The equipment ground is also not permitted to be white... it must be green or bare. That white wire should be capped off to comply with the code, but I'd be hard pressed to tell you that any special hazard is created by letting it remain as-is.
|
|
#8
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
You can parallel grounding paths Marc, we do it all the time (conduit with a green wire). In fact it is required in patient care areas, hence my reference.
We also reidentify grounding conductors in IG circuits all the time. If you really wanted to be pedantic and never be able to go back, you could strip it. |
|
#9
|
|||
|
|||
|
Thanks for the comments all. The upside down fuse is a new one to me. I didn't realize you could put a fuse in the wrong way. I see the groove at one end of the fuses. I will look for that in the future.
|
|
#10
|
||||
|
||||
|
For those interested, the following explains reh=hection type fuses:
Class R Fuses Class R (“R” for rejection) fuses are high performance, ⁄Ω¡º to 600 ampere units, 250V and 600V, having a high degree of current-limitation and a short-circuit interrupting rating of up to 300,000 amperes (RMS symmetrical). BUSS® Class R’s include Classes RK1 LOW-PEAK® YELLOW and LIMITRON fuses, and RK5 FUSETRON® fuses. They have replaced BUSS® K1 LOW-PEAK® and LIMITRON fuses and K5 FUSETRON® fuses. These fuses are identical, with the exception of a modification in the mounting configuration called a “rejection feature”. This feature permits Class R to be mounted in rejection type fuseclips. “R” type fuseclips prevent older type Class H, ONE-TIME and RENEWABLE fuses from being installed. Since Class H fuses are not current-limiting and are recognized by regulatory agencies as having only a 10,000 ampere interrupting rating, serious damage could result if a Class R fuse were replaced by a Class H fuse. The use of Class R fuseholders is thus an important safeguard. The application of Class R fuses in such equipment as disconnect switches permits the equipment to have a high short-circuit current rating. NEC® 110.9 requires that protective devices have adequate capacity to interrupt short-circuit currents. NEC® 240.60(B) requires fuseholders for current- limiting fuses to reject non-current-limiting type fuses. In the above illustration, the fuse on the right has a grooved ring in one ferrule, providing the rejection feature of the Class R fuse in contrast to the lower interrupting rating, non-rejection type. [IMG]file:///C:/DOCUME%7E1/COMPAQ%7E1/LOCALS%7E1/Temp/moz-screenshot.jpg[/IMG] More Fuse Info(PDF) |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| **HOT** Texas Inspectors use of REI-7A-0 | escanlan | Legislation, Licensing & Legal Issues for Inspectors | 27 | 11/20/07 12:09 AM |
| New Report Upload Technology | cdemsky | Miscellaneous Discussion for Inspectors | 49 | 5/1/07 10:19 AM |
| PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. | gromicko | Miscellaneous Discussion for Inspectors | 53 | 8/30/06 5:58 PM |
| Massachusetts Board of Registration of Home Inspectors | jtedesco1 | Legislation, Licensing & Legal Issues for Inspectors | 0 | 2/14/06 3:38 AM |