Default Is the there a 'bonding' screw that I don't see.

????



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #2  
Old 10/12/06, 5:52 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,078
Default Re: Is the there a 'bonding' screw that I don't see.

Here's the pic....
Attached Thumbnails
there-bonding-screw-dont-see-s4020325.jpg  



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #3  
Old 10/12/06, 6:00 PM
Dennis DiVito Dennis DiVito is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Fairfield, VA
Posts: 34
Default Re: Is the there a 'bonding' screw that I don't see.

If this is a sub panel (there would be a main disconnect next to the meter) then the grounding busbar to the left which is connected to the panel enclosure completes the bonding.

The picture shows a properly wired sub panel.
Reply With Quote
  #4  
Old 10/12/06, 6:19 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,078
Default Re: Is the there a 'bonding' screw that I don't see.

It's the main. The disconnect is outside next to the meter...
Attached Thumbnails
there-bonding-screw-dont-see-s4020328.jpg  



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #5  
Old 10/12/06, 6:28 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is the there a 'bonding' screw that I don't see.

No, it is not the main. The main disconnect is outside. The panel is treated as a sub. This is why it is fed with a 4-wire feeder. Notice how the grounds and neutrals are separate and there are separate ground and neutral conductors?
All is well here.
Reply With Quote
  #6  
Old 10/12/06, 6:31 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,078
Default Re: Is the there a 'bonding' screw that I don't see.

Just figured that out after I looked at my first reply.
Thanks for clearing my head...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #7  
Old 10/12/06, 6:37 PM
Dennis DiVito Dennis DiVito is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Fairfield, VA
Posts: 34
Default Re: Is the there a 'bonding' screw that I don't see.

When there is a disconnect next to the meter that one is the main disconnect. The interior panel is a subpanel even though there is a diconnect in that panel. These subpanels are wired so the neutrals are floating and the bare grounding wires are on a seperate busbar attached to the enclosure. Be aware of this. If there is a disconnect next to the meter then that is the main disconnect and that neutral needs to be bonded to the panel.

It is so firemen can easily shut off the power without having to hunt for the panel in the house.
Reply With Quote
  #8  
Old 10/12/06, 7:00 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Is the there a 'bonding' screw that I don't see.



There is service equipment. . .

Service Equipment.
The necessary equipment, usually consisting of a circuit breaker(s) or switch(es) and fuse(s) and their accessories, connected to the load end of service conductors to a building or other structure, or an otherwise designated area, and intended to constitute the main control and cutoff of the supply.

and there is load-side equipment (everything else after the service equipment).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #9  
Old 10/12/06, 10:00 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,733
Default Re: Is the there a 'bonding' screw that I don't see.

Quote:
Originally Posted by jpope


There is service equipment. . .

Service Equipment.
The necessary equipment, usually consisting of a circuit breaker(s) or switch(es) and fuse(s) and their accessories, connected to the load end of service conductors to a building or other structure, or an otherwise designated area, and intended to constitute the main control and cutoff of the supply.

and there is load-side equipment (everything else after the service equipment).
Keep it up Jeff, we'll get it sooner or later.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #10  
Old 10/13/06, 11:31 AM
Michael Martin Michael Martin is offline
New User
 
Join Date: May 2005
Location: Cleveland, Ohio
Posts: 24
Please Note: Michael Martin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is the there a 'bonding' screw that I don't see.

Although having the main outside may be intended for the fire department to have quick access to shut down power, if that were my home I'd be tempted to throw a padlock on it. Too much potential for juvenile mischief...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Subpanel Bonding Screw away Electrical 24 1/9/08 3:46 PM
Bonding Piping 101....Good To Know ! pabernathy Electrical 37 4/28/07 12:25 PM
Steel post question sspradling Structural 42 3/2/07 9:59 PM
Demystify Grounding & Bonding Class pabernathy Education 5 12/24/06 2:10 AM


All times are GMT -4. The time now is 12:53 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147