  #1  
Old 5/20/09, 2:25 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 19,589
Default Is there an electrician who can proof this graphic for me please?

http://www.nachi.org/gallery/electri...quirements.jpg



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
Find an InterNACHI certified Colorado Home Inspector (and anywhere else in North America)
  #2  
Old 5/20/09, 2:25 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 19,589
Default Re: Is there an electrician who can proof this graphic for me please?

Download in hi-res by clicking bottom link on page.



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #3  
Old 5/20/09, 7:21 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Is there an electrician who can proof this graphic for me please?

Hi Nick,

there is more to this issue than you are showing, firstly some habitable spaces require fixed lighting rather than switched outlets, secondly; area like attics and crawl spaces also require lighting (and receptacles) if they contain servicable equipment (HVAC for example).

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #4  
Old 5/20/09, 7:24 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,733
Default Re: Is there an electrician who can proof this graphic for me please?

Quote:
Originally Posted by gbeaumont View Post
Hi Nick,

there is more to this issue than you are showing, firstly some habitable spaces require fixed lighting rather than switched outlets, secondly; area like attics and crawl spaces also require lighting (and receptacles) if they contain servicable equipment (HVAC for example).

Regards

Gerry
Okay, let's talk about the difference between outlets and receptacles...



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #5  
Old 5/20/09, 7:29 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Is there an electrician who can proof this graphic for me please?

Quote:
Originally Posted by lkage View Post
Okay, let's talk about the difference between outlets and receptacles...
Good point

I'm not an electrician ............. but I did stay at a holiday inn express last night

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #6  
Old 5/20/09, 7:45 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,733
Default Re: Is there an electrician who can proof this graphic for me please?

You're a gracious man, Gerry...



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #7  
Old 5/20/09, 7:45 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Is there an electrician who can proof this graphic for me please?

Quote:
Originally Posted by lkage View Post
Okay, let's talk about the difference between outlets and receptacles...
That's really pretty simple, I think.

Outlets are any point where power is obtained for fixtures and appliances, including receptacles and lighting.

Receptacles are installed at outlets. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 5/20/09, 7:48 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,733
Default Re: Is there an electrician who can proof this graphic for me please?

Quote:
Originally Posted by jpope View Post
That's really pretty simple, I think.

Outlets are any point where power is obtained for fixtures and appliances, including receptacles and lighting.

Receptacles are installed at outlets. . .
Yes, thank you...



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #9  
Old 5/21/09, 12:04 AM
ccurrins's Avatar
ccurrins ccurrins is offline
Active Poster
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 3,233
Please Note: ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is there an electrician who can proof this graphic for me please?

Nice responses from from great inspectors. But what happened to the electricians that used to jump on questions like this within minutes?
Reply With Quote
  #10  
Old 5/21/09, 8:29 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Is there an electrician who can proof this graphic for me please?

We have a LIFE Mr. Currins.........

Now since you all defined Outlets and Receptacles........understand that Receptacles are Devices.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #11  
Old 5/21/09, 8:32 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Is there an electrician who can proof this graphic for me please?

I believe the attempt was to convey the requirements of 210.70 only. If I were to say add something then I would mention in regards to the RED area, not just storage but also "Equipment Space" as well.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 5/21/09 at 8:36 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Roy the proof you asked for wdevries Canadian Inspectors 55 7/8/08 11:30 AM


All times are GMT -4. The time now is 12:06 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts