Default Are there standards for stipping cable?

Here are a couple of pictures that concern me. The first one shows the service connected to the main disconnect. The insulation was stripped correctly, but there is a significant amount of exposed conductor. Just wondering if there are any standards for this.

The second picture shows an additional problem. Not only is the length is excessive, the cable has been doubled and has visible corrosion. The corrosion is enough for me to call it out.
Attached Thumbnails
there-standards-stipping-cable-p1250937.jpg   there-standards-stipping-cable-p1250936.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/29/11, 10:19 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Are there standards for stipping cable?

Hello Gregary:

You can tell by the cut that a certified electrician did not do this.
Yes there are requirements for proper amount of sheathing showing.
However we cannot mention what a code allows unless we are code officials and some cases the code will not.
Some breakers have written info on the proper installation including length to remove for sheathing.
Rule of thumb is no more then a 1/4 inch passed connection but only for visual to see if it is loose.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #3  
Old 3/29/11, 5:15 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Are there standards for stipping cable?

As far as the lug is concerned this is no different than a double tap.

Reply With Quote
  #4  
Old 3/30/11, 8:00 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Are there standards for stipping cable?

If you don't mind ( I know I am not here much anymore ) I would like to comment on the torque of the breaker. I notice that the one with the corrosion has a set screw that is not turned into is setting as much as the one beside it....would lead me to think the conductor is loose, on load arcing takes place which adds to the problem.

Now I don't know this for fact...it is only an observation but notice the number of threads on the black conductors termination lug than on the red one. Sure looks like it was not properly torques to me...and to be honest with you that can be a problem. As was mentioned before it would be nothing different than a double lug for your review BUT with the corrosion and possible torque ( which can lead to a safety issue so don't feel bad about ASSUMING in that case) ...have it looked at as I also see discoloration around the plastic ( ps. Plastic does not corrode) so something else is going on and my guess would be a loose connection as well.

Again....I hate commenting via pictures but it would cross my mind....just a thought.



Paul W. Abernathy
Reply With Quote
  #5  
Old 3/30/11, 9:18 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Are there standards for stipping cable?

Quote:
Originally Posted by pabernathy View Post
If you don't mind ( I know I am not here much anymore ) I would like to comment on the torque of the breaker. I notice that the one with the corrosion has a set screw that is not turned into is setting as much as the one beside it....would lead me to think the conductor is loose, on load arcing takes place which adds to the problem.

Now I don't know this for fact...it is only an observation but notice the number of threads on the black conductors termination lug than on the red one. Sure looks like it was not properly torques to me...and to be honest with you that can be a problem. As was mentioned before it would be nothing different than a double lug for your review BUT with the corrosion and possible torque ( which can lead to a safety issue so don't feel bad about ASSUMING in that case) ...have it looked at as I also see discoloration around the plastic ( ps. Plastic does not corrode) so something else is going on and my guess would be a loose connection as well.

Again....I hate commenting via pictures but it would cross my mind....just a thought.
Hi Paul, Thanks for your observations. I did call is a safety concern with many other issues (not posted) to be evaluated by a licensed electrical contractor. BTW, I did watch your video on how to prepare for the electrical exam. I have a few suggestions...as I recently passed the WI code exam. But my HI clients don't know that. I appreciate your comments and respect your opinion. THANKS!



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #6  
Old 4/1/11, 8:58 AM
Stephen Douglas Stephen Douglas is offline
New User
 
Join Date: Mar 2011
Posts: 3
Please Note: Stephen Douglas is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Are there standards for stipping cable?

Is there anything to be said about the bottom breaker. Set screw is turned all the way in, almost counter sunk, and the wire looks like it should be in my chevy truck.

Stephen
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical Inspections 10 4/17/11 1:43 PM
A Mission to Change the Standards - Let's Debate krichardson Miscellaneous Discussion for Inspectors 74 12/19/07 8:29 PM
Did you KNOW this about NM Cable? pabernathy Electrical Inspections 0 12/19/06 8:46 AM
Texas Warranty Inspection Standards badair General Inspection Discussion 5 9/30/06 5:12 PM