Default There's nothing wrong here !!!

Had a "so called" electrician call me up today to tell me that he was inspecting a panel I checked the other day. I called out the double tap that you obviously can see below. The "so called" electrician was arguing with me that this is standard practice and that I should find another career!!! Needless to say I started to talk a little more up to their level to feel out what type of person I was dealing with, they were lost and had no clue about anything with an electrical system. I continued on to tell them that they should contact the owner and tell them that they need to find another electrician to fix the problem, as this is obvisouly to difficult of a repair for the "electrician" that I was on the phone with to fix (Maybe I will call ). I guess that I just had to share how some people can be so obsured and claim to be someone they are not, because this person obviously was not the "electrician" that they were claiming to be, probably just another real estate agent or owner tring to pull a fast one.

I am curious if anyone else has had this experience and how you handled it?
Attached Thumbnails
theres-nothing-wrong-here-13.jpg  




Timothy Lower
Centerville, Ohio

Reply With Quote
  #2  
Old 5/18/08, 4:42 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: There's nothing wrong here !!!

Quote:
Originally Posted by tlower
I am curious if anyone else has had this experience and how you handled it?
I can't tell from your small pic what type of breaker it is. Post a larger pic and a one with a view of the panel.

A number of mfgs. permit two wires on a breaker.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 5/18/08, 4:54 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: There's nothing wrong here !!!

That's a Cutler-Hammer CH breaker, and what you picture is permitted for that brand and model.

Don't you feel silly now? Your post, manifesto style, is an example of what's wrong with some uneducated home inspectors.
Reply With Quote
  #4  
Old 5/18/08, 4:59 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: There's nothing wrong here !!!

Since I can't tell from the picture...

Mark, does that type of breaker have positions for two wires where they can be connected without the two wires physically touching each other?

I am thinking all breakers that allow two wires have two positions for the wires, right?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 5/18/08, 5:03 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: There's nothing wrong here !!!

Quote:
Originally Posted by bking
I am thinking all breakers that allow two wires have two positions for the wires, right?
Yeah, but the CH's have sort of an oval where the wires enter, so it's hard to tell without up-close pics of the actual termination whether one is on each side of the screw or not. I think it probably is terminated correctly, however, because it's pretty hard to get it wrong on a CH. The way that oval window is, if you have one conductor on the bottom already, it's downright hard to get another in there.
Reply With Quote
  #6  
Old 5/18/08, 5:04 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: There's nothing wrong here !!!

You're so harsh Marc.
Let's try to be nice.
We don't want to scare people away from being able to learn and interact.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #7  
Old 5/18/08, 5:08 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: There's nothing wrong here !!!

Quote:
Originally Posted by mlarson
You're so harsh Marc.
Let's try to be nice.
We don't want to scare people away from being able to learn and interact.
As long as they don't start out with a manifesto, I'm game. You know I'm "nice" 99% of the time, but I reserve that 1% for special occasions. This was the right time for that. The OP started out bashing this EC, so he opened that Pandora's Box and I obliged. Matter of fact, I should quote his OP for posterity, since this is the sort of stuff that gets edited when the OP returns:

Quote:
Had a "so called" electrician call me up today to tell me that he was inspecting a panel I checked the other day. I called out the double tap that you obviously can see below. The "so called" electrician was arguing with me that this is standard practice and that I should find another career!!! Needless to say I started to talk a little more up to their level to feel out what type of person I was dealing with, they were lost and had no clue about anything with an electrical system. I continued on to tell them that they should contact the owner and tell them that they need to find another electrician to fix the problem, as this is obvisouly to difficult of a repair for the "electrician" that I was on the phone with to fix (Maybe I will call ). I guess that I just had to share how some people can be so obsured and claim to be someone they are not, because this person obviously was not the "electrician" that they were claiming to be, probably just another real estate agent or owner tring to pull a fast one.

I am curious if anyone else has had this experience and how you handled it?
Reply With Quote
  #8  
Old 5/18/08, 5:10 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: There's nothing wrong here !!!

Quote:
Originally Posted by Marc D. Shunk
As long as they don't start out with a manifesto, I'm game. You know I'm "nice" 99% of the time, but I reserve that 1% for special occasions. This was the right time for that. The OP started out bashing this EC, so he opened that Pandora's Box and I obliged.
I understand if you thought he was ripping an electrician.
But he is contending that the guy wasn't.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #9  
Old 5/18/08, 5:29 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: There's nothing wrong here !!!

electrician was arguing with me that this is standard practice and that I should find another career!!!

That may have caused an angry post from anyone.

We all make mistakes, though we are not %100 positive if the conductors are correct to the breaker yet.
Reply With Quote
  #10  
Old 5/18/08, 5:38 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: There's nothing wrong here !!!

Quote:
Originally Posted by relliott
We all make mistakes, though we are not %100 positive if the conductors are correct to the breaker yet.
I'm 100% postitive and I also would have questioned the OP's career choice and whether the OP has the knowledge required to make such an analysis.
Reply With Quote
  #11  
Old 5/18/08, 6:02 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: There's nothing wrong here !!!

As long as we're on the subject Marc, can you tell who all alow double taps please? Thanks, Ken
Reply With Quote
  #12  
Old 5/18/08, 6:03 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: There's nothing wrong here !!!

Quote:
Originally Posted by klott
As long as we're on the subject Marc, can you tell who all alow double taps please? Thanks, Ken
Certainly, for a nominal fee. Would you like my PayPal address?

The one in the pic in this post absolutely does. Square D QO and Cutler Hammer CH are the two popular one's, in 15 and 20 amp. There's a couple others, but they escape me at the moment. It is notated on the breaker, however.
Reply With Quote
  #13  
Old 5/18/08, 6:06 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: There's nothing wrong here !!!

Fair enough. Pay him Michael!
Reply With Quote
  #14  
Old 5/18/08, 6:17 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: There's nothing wrong here !!!

Quote:
Originally Posted by klott
Fair enough. Pay him Michael!
Why? I already knew the two Marc mentioned allowed it.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #15  
Old 5/18/08, 6:19 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: There's nothing wrong here !!!

Marc, is there a date change on those CH panels? I just checked mine. I have one from about 1977, nothing in the panel or on any of the 13 single pole breakers states OK for two wires. I checked each side of each breaker and the two interior labels. Zip. Although I see the oval access hole does appear to have room for two conductors.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Free Books And Articles For Electrical jtedesco1 Electrical Inspections 14 1/6/08 6:45 PM
Grandpa, what is wrong with the patio? mcyr Exterior Inspections 1 5/12/07 10:29 PM
What's wrong here? wwarner Structural Inspections 15 9/12/06 7:47 PM


All times are GMT -4. The time now is 8:45 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts