Default How are these grounded?

Home had a mid 60's fuse 100 amp service. I had a difficult time inspecting as the panel was in a closet behind a picture. There are 2 pics showing the closet and framing, shelving.

I noted the closet & clearance issues.

The home had mostly 2 wire but all the receptacles where indicating they where grounded. I double checked with the sure test.

I didnt see any conduit. Why are these showng that they are grounded.

I also thru in a pic of the spagetti wiring in attic. The knob & tube was special as well. FIRE SALE
Attached Thumbnails
these-grounded-86906-brookpark-036-small-.jpg.jpg
Views:	104
Size:	43.0 KB
ID:	7534   these-grounded-86906-brookpark-032-small-.jpg.jpg
Views:	87
Size:	41.6 KB
ID:	7535   these-grounded-86906-brookpark-033-small-.jpg.jpg
Views:	62
Size:	39.1 KB
ID:	7536   these-grounded-86906-brookpark-026-small-.jpg.jpg
Views:	95
Size:	42.1 KB
ID:	7537   these-grounded-86906-brookpark-017-small-.jpg.jpg
Views:	135
Size:	46.6 KB
ID:	7538  

Reply With Quote
  #2  
Old 12/5/06, 8:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: How are these grounded?

Your last picture shows the grounding conductor, which was added to the original two-wire K&T (poorly, I might add).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 12/5/06, 8:29 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: How are these grounded?

interesting connection on the last picture in regards to the EGC....last I checked K & T did not come with a EGC....and you should not splice a conductor WITH a EGC onto a circuit that has no EGC....



Paul W. Abernathy
Reply With Quote
  #4  
Old 12/5/06, 8:30 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: How are these grounded?

Bootleg ground?

Like this pic I pilfered from somewhere:
Attached Thumbnails
these-grounded-bootleg-ground1.jpg  



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 12/5/06, 8:31 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: How are these grounded?

I would have said the same Larry, if he hadn't checked it with the SureTest. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 12/5/06, 8:34 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: How are these grounded?

Sorry david....I did not answer the other part.....they are showing grounded possibly because someone went and individually grounded each receptacle to a grounded source.

Otherwise it could not be a bootleg because you used a suretest and it would detect that effect.

Now could it be that someone strung a EGC around like the last picture in the set....and everything is connected to that and then all the receptacles have been updated with NM cable with ground...and done like the last picture....quite possible....... dont like it........

I would defer.......something smells here and I WOULD love to be the electrician you call to look it over.....but alas...too far of a commute.

Did you pull the panel....got any pictures from the inside of those panels...showing if their are EGC's present and so on....might tell us more.



Paul W. Abernathy
Reply With Quote
  #7  
Old 12/5/06, 8:36 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: How are these grounded?

Quote:
Originally Posted by lkage
Bootleg ground?

Like this pic I pilfered from somewhere:
ewww..nice one Larry.....and in Wiremold no less.....classy



Paul W. Abernathy
Reply With Quote
  #8  
Old 12/5/06, 8:38 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: How are these grounded?

Quote:
Originally Posted by jpope
I would have said the same Larry, if he hadn't checked it with the SureTest. . .
Yes, thank you...I'll have to get a Suretest. I've been somewhat reluctant due to my research, in the past, indicating premature and regular failure of the plug connections. A little expensive for that or maybe it has improved.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 12/5/06, 8:39 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: How are these grounded?

Quote:
Originally Posted by pabernathy
ewww..nice one Larry.....and in Wiremold no less.....classy
Thank you, I try to steal only the best.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #10  
Old 12/5/06, 8:40 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: How are these grounded?

Hey Larry...I have had my 65-155 for a few years now.....and still going strong....worth the investment and the ends can be replaced as well if needed.



Paul W. Abernathy
Reply With Quote
  #11  
Old 12/5/06, 11:06 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: How are these grounded?

Hi to all,

That is the most screwed up installation onto K&T that I have ever seen, I thought I had just about seen it al but adding a 3rd conductor to support the ground on an old K&T circuit thats a first.

BTW, great call Jeff, I had to look at the picture several times before I got what had been done.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #12  
Old 12/5/06, 11:07 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How are these grounded?

That grounded K&T looks pretty "real". It has the same style knobs and loom. I wonder if the electrician who installed the original did think a ground was a good idea and pulled one in along with the 2 circuit conductors.
It wasn't the usual way to install K&T but I can't think of a reason it wouldn't have been legal.
I agree the Romex guy could have used a bug or some solder to make his taps. Makes you wonder what is under that tape huh?
Reply With Quote
  #13  
Old 12/5/06, 11:10 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: How are these grounded?

Quote:
Originally Posted by lkage
Thank you, I try to steal only the best.
You have class Larry, I posted that image in a QOD a couple of years ago

Problem is I flitched it of someone even better, but forgot to put the attribution on it at the time. it is a great image

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #14  
Old 12/5/06, 11:25 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How are these grounded?

I found one in my father in laws house a couple weeks ago that made me say huh. I pulled out the receptacle in the bathroom and it was pigtailed with bare wire, all 3. Fortunately I am not a "he man" who works live when I don't absolutely have to so it was turned off at the breaker.
I wish I had a camera but you get the picture. I guess the installer ran out of insulated wire.
The amazing thing was this was a GFCI and the box was still over wire count. I don't have a clue how he got all of that bare wire in there without shorting something, even with a plastic box.
Reply With Quote
  #15  
Old 12/6/06, 1:00 AM
jschulte jschulte is offline
Active Poster
 
Join Date: Jul 2006
Location: Moberly, MO
Posts: 445
Please Note: jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How are these grounded?

I can't imagine the time they would have spent installing new tubes to run the grounding conductor. Would have been easier to just run romex. There must have been another circuit there that they disposed of to make room for the grounding conductor.

Quote:
That grounded K&T looks pretty "real". It has the same style knobs and loom. I wonder if the electrician who installed the original did think a ground was a good idea and pulled one in along with the 2 circuit conductors.
Would they have had appropriate (three prong or some other method of grounding) outlets at the time of knob and tube?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
GFI not grounded rtruluck Electrical Inspections 14 3/7/07 11:02 PM
So...Do you think THIS panel is Grounded? pabernathy Electrical Inspections 3 1/22/07 7:52 PM
opinions on GFCI outlets for non grounded oputlets jmerritt1 Electrical Inspections 23 5/11/06 7:22 PM
Electrical Inspection Training for Home Inspectors jtedesco1 Inspection Education & Training 6 4/27/06 10:43 PM


All times are GMT -4. The time now is 8:45 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts