Default Three times a charm

I inspect FP panels almost on a daily biases and If I must say so I am dam good at it practice makes perfect.

Here is an example of a bad one found recently. I do not condemn just based on the name Federal Pacific I judge each panel independently.

This panel was inspected in January by another inspector and he just condemned based on the name which in turned brought out the electrical contractor who inspected it again and put in writing the panel was just fine.

These first two inspections were brought about as the result of a re-location company purchasing the property my inspection was for a perspective buyer. I load tested the panel with in house circuits and built in appliances and exceeded the 80% rule again. The top left breaker was for the cook stove rated at 50 amps the cook stove drew 49 amps and tripped the breaker but by looking at the breaker could not tell it was tripped. So after 3 inspection this home appears to be getting a updated panel.

My client was very happy and after speaking with the selling RE agent I could tell by the sound of her voice which was very quite she was not to happy with the outcome. How do I know this just from the tone of her voice I have been sleeping with her for almost 43 years yes all is disclosed up front and on the table
Attached Thumbnails
three-times-charm-1921-el-camino-pc-6-8-11-048.jpg   three-times-charm-1921-el-camino-pc-6-8-11-049.jpg   three-times-charm-1921-el-camino-pc-6-8-11-042.jpg   three-times-charm-1921-el-camino-pc-6-8-11-108.jpg   three-times-charm-1921-el-camino-pc-6-8-11-114.jpg  




Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 6/8/11 at 4:58 PM..
Reply With Quote
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/8/11, 5:04 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Three times a charm

What's the 80% rule? And at what temperature do you consider there to be a problem?
Reply With Quote
  #3  
Old 6/8/11, 5:09 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Three times a charm

Quote:
Originally Posted by Robert Meier View Post
What's the 80% rule? And at what temperature do you consider there to be a problem?
80% of the rating of the panel the 100 amp panel should not carry more than 80 amps. I start looking for problems when the temp is 30 degrees above ambient of the panel also I look for an un-balanced load temp wise on a 220 volt double pole breaker both legs should be almost the same in temp



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 6/8/11 at 5:14 PM..
Reply With Quote
  #4  
Old 6/8/11, 5:19 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Three times a charm

Charley, are you a licensed electrician?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 6/8/11, 5:22 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Three times a charm

Quote:
Originally Posted by jfunderburk View Post
Charley, are you a licensed electrician?
Nope a visual inspection only camera in hand with amp meter Joe don't start that SOP crap with me we both know better



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 6/8/11, 5:26 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Three times a charm

I would question the use of 80% as a rule. Sounds like a good guideline but it's not supported by the NEC. A panel can be loaded to 125% of it's continuous load plus 100% of it non-continuous load. In a dwelling just about every load is non-continuous with the exception of some lighting loads. A cook top on a 50 amp circuit running at 49 amps is OK according to the NEC.
Reply With Quote
  #7  
Old 6/8/11, 5:32 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Three times a charm

Quote:
Originally Posted by Robert Meier View Post
A cook top on a 50 amp circuit running at 49 amps is OK according to the NEC.
Until it trips at 49 amps



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 6/8/11, 5:34 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Three times a charm

Quote:
Originally Posted by cbottger View Post
Until it trips at 49 amps
Yes that definitely would be a problem. Ususally inverse-time CB's can operate slightly above their rating for quite some time before tripping.
Reply With Quote
  #9  
Old 6/8/11, 5:40 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Three times a charm

So Robert you are telling me say take a 200 amp panel in today's world and load that baby up to 200 amps continuously full load and that is perfectly fine. According to NEC



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 6/8/11, 5:46 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Three times a charm

Quote:
Originally Posted by cbottger View Post
So Robert you are telling me say take a 200 amp panel in today's world and load that baby up to 200 amps continuously full load and that is perfectly fine. According to NEC
No, that would be 200 amp non-continuous. The NEC definition of continuos load is that it is operated at it's maximum ampacity for 3 or more hours. So if you use your range as an example it is permitted to operate at 49 amps on a 50 amp circuit because it will never operate at it's maximum for 180 or more minutes.

Quote:
Article 100
Continuous Load. A load where the maximum current is expected to continue for 3 hours or more.
Reply With Quote
  #11  
Old 6/8/11, 5:57 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Three times a charm

The 87.9 amps on the 100 amp breaker was what my reference was about and the 87 amps could be in use for many many hours especially on a heavy cook day like thanksgiving. I have never been questioned about exceeding the amp draw by 80% for extended time or the capabilities of extended time.

The breaker tripping on the cook stove at 49 amps within 30 seconds of turning the appliance on was just icing on the cake



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 6/11/11, 12:15 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Three times a charm

Lets also not forget that a conductor as listed in Table 310.15(B)(16) in the 90 degee column is rated for that ampacity continuously....and the temperature rating of the column is exactly what the conductors insulation is rated for...continuously. Now, the reason we limit the ampacity to an 80% value is due to the limitations of the terminations to Overcurrent Devices as prescribed by UL for the device. I can load up a conductor at it's full ampacity for 2 Hours, 59 Minutes and 59 Seconds....and everything is fine. The moment it gets to 3 hours or more....we got a problem.

Notice that THHN in as limited to 75 degrees due to terminal ratings has an ampacity of 200A for a 3/0 CU. Notice the acceptable temperature of the conductors at that degree rating...167 degrees F. Without going into too much detail as I would find it hard to explain it here....it would not be a problem to see a conductor with a temperature not exceeding that value.

Don't want to get too technical....just want to kinda explain it just a little.



Paul W. Abernathy
Reply With Quote
  #13  
Old 6/12/11, 8:57 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Three times a charm

Quote:
Originally Posted by cbottger View Post
the electrical contractor ... inspected it again and put in writing the panel was just fine.
WOW ... ... not many sparkies out there willing to put their license on the line for an FPE panel with known problems. Probably isn't aware of the issues. Put this link in your reports ... www.inspectapedia.com/fpe/fpepanel.htm


Quote:
Originally Posted by cbottger View Post
the selling RE agent ... was not to happy with the outcome. How do I know this just from the tone of her voice I have been sleeping with her for almost 43 years yes all is disclosed up front and on the table
Wouldn't fly here in NY ... You cant do an inspection where a relative or business partner has a financial interest. Period ... no disclosure provision for that.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 6/12/11, 9:46 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Three times a charm

Quote:
Originally Posted by cbottger View Post

I inspect FP panels almost on a daily biases and If I must say so I am dam good at it practice makes perfect.

Here is an example of a bad one found recently. I do not condemn just based on the name Federal Pacific I judge each panel independently.

This panel was inspected in January by another inspector and he just condemned based on the name which in turned brought out the electrical contractor who inspected it again and put in writing the panel was just fine.

These first two inspections were brought about as the result of a re-location company purchasing the property my inspection was for a perspective buyer. I load tested the panel with in house circuits and built in appliances and exceeded the 80% rule again. The top left breaker was for the cook stove rated at 50 amps the cook stove drew 49 amps and tripped the breaker but by looking at the breaker could not tell it was tripped. So after 3 inspection this home appears to be getting a updated panel.

My client was very happy and after speaking with the selling RE agent I could tell by the sound of her voice which was very quite she was not to happy with the outcome. How do I know this just from the tone of her voice I have been sleeping with her for almost 43 years yes all is disclosed up front and on the table

Additionally, how much do you Charge for these type of extended scope inspections?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #15  
Old 6/12/11, 10:04 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,567
Default Re: Three times a charm

so Charley has been sleeping with the enemy.....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
More Signs of the Times: At foreclosure auctions, broken dreams on sale jburkeson1 Miscellaneous Discussion for Inspectors 0 10/15/09 11:36 AM
How to Cope With Hard Economic Times mcyr Miscellaneous Discussion for Inspectors 6 8/7/09 8:39 AM
Surviving Bad Times mcyr Miscellaneous Discussion for Inspectors 13 1/10/09 11:19 AM


All times are GMT -4. The time now is 7:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts