Default Re: Three times a charm

Quote:
Originally Posted by cbottger View Post
I load tested the panel ...
I would be very careful with that wording, since you are just doing a visual inspection with a good number of circuits on.

To properly load test breakers you have to significantly exceed the rating under controlled condition (e.g. 135% and 200% of the rating following UL standards). If the 50A breaker in question didn't trip, even at a load around 60A, it tells you absolutely nothing about the reliability of the breaker. Breakers can trip anywhere from 100% to 125% of the rating. A breaker could be loaded to 120% of the rating without tripping or there being anything wrong. See this discussion, which also has an example breaker trip curve ...

http://forums.mikeholt.com/showthread.php/134611-FPE-Breaker-Amperage-amp-Time?

So for an FPE panel you are back to square one with it being a problem right off the bat from an HI's point of view, since they have a known history of problems with breakers not tripping when they should, and issues with poor bus connections.

JMO & 2-Nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 6/12/11, 7:53 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Three times a charm

Quote:
Originally Posted by roconnor View Post
A breaker could be loaded to 120% of the rating without tripping or there being anything wrong. See this discussion, which also has an example breaker trip curve ...

http://forums.mikeholt.com/showthread.php/134611-FPE-Breaker-Amperage-amp-Time?


We recently had this discussion over on the NACBI forum (that's a 15amp OCD in the photo and it never tripped while I was present). Jim Seffrin provided some very useful information http://www.nacbi.com/messageboard/sh...15-Amp-Circuit



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #18  
Old 6/12/11, 8:25 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Three times a charm

Quote:
Originally Posted by pabernathy View Post

Notice that THHN in as limited to 75 degrees due to terminal ratings has an ampacity of 200A for a 3/0 CU. Notice the acceptable temperature of the conductors at that degree rating...167 degrees F. Without going into too much detail as I would find it hard to explain it here....it would not be a problem to see a conductor with a temperature not exceeding that value.

Don't want to get too technical....just want to kinda explain it just a little.
I agree in absolute terms.

But elevated temps observed at fractional loads may well indicate a thermal exception when adjusted for full load. For instance: the 200A rated THHN circuit at an 80A actual load in 70F/21C ambient with an observed temp of 150F/66C would be considered a thermal exception.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #19  
Old 6/12/11, 9:53 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,185
Default Re: Three times a charm

Quote:
Originally Posted by cevans View Post
I agree in absolute terms.

But elevated temps observed at fractional loads may well indicate a thermal exception when adjusted for full load. For instance: the 200A rated THHN circuit at an 80A actual load in 70F/21C ambient with an observed temp of 150F/66C would be considered a thermal exception.
So what is the formula for calculating Absolute Temperature Criteria and where can this information be found?
Good luck with your Level III training this week guys!
Reply With Quote
  #20  
Old 6/13/11, 12:31 AM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,274
Default Re: Three times a charm

Quote:
Originally Posted by cbottger View Post
Nope a visual inspection only camera in hand with amp meter Joe don't start that SOP crap with me we both know better
I thought anything outside the SOP would be considered a technical inspection and not within the guidelines of a standard home inspection.



Paul Pendley
Premier Property Inspections
866-458-8516
Reply With Quote
  #21  
Old 6/13/11, 3:38 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Three times a charm

Quote:
Originally Posted by cevans View Post
... that's a 15amp OCD in the photo and it never tripped while I was present
The load usually has to be about 125% to 135% of the breaker rating to ensure a breaker trips (some trip at lower values).

So even with an 18A load on that 15A breaker there likely is nothing wrong with the breaker. The capacity of the entire circuit likely needs to be upgraded or some load removed ... but thats not a problem with the breaker. Some are amazed at that.

And I would recommend www.mikeholt.com for more information. Excellent site, tons of good info, with a lot of really knowledgeable people.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #22  
Old 6/13/11, 9:31 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Three times a charm

Quote:
Originally Posted by ldapkus1 View Post
So what is the formula for calculating Absolute Temperature Criteria and where can this information be found?
Good luck with your Level III training this week guys!
Hey Linus. That's Level-II (quantitative thermography) based on the absolute temperature criteria from the Infraspection Institute Standard for Infrared Inspection of Electrical Systems & Rotating Equipment.

Thanks for the well wishes. Class is going great!



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
More Signs of the Times: At foreclosure auctions, broken dreams on sale jburkeson1 Miscellaneous Discussion for Inspectors 0 10/15/09 11:36 AM
How to Cope With Hard Economic Times mcyr Miscellaneous Discussion for Inspectors 6 8/7/09 8:39 AM
Surviving Bad Times mcyr Miscellaneous Discussion for Inspectors 13 1/10/09 11:19 AM


All times are GMT -4. The time now is 7:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts