Default Tiny service entrance question

Anyone ever seen anything like this? The neutral at the service mast is spliced to a tiny, solid (perhaps size six or eight) conductor from the utility line. This is the smallest neutral I've ever seen. Don't recall ever seeing a splice like this.

tiny-service-entrance-question-052611-027.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/27/11, 11:19 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tiny service entrance question

Quote:
Originally Posted by jfunderburk View Post
Anyone ever seen anything like this? The neutral at the service mast is spliced to a tiny, solid (perhaps size six or eight) conductor from the utility line. This is the smallest neutral I've ever seen. Don't recall ever seeing a splice like this.

Attachment 45044
Canadian:

Size of neutral conductor

(1) The size of the neutral conductor shall have sufficient ampacity to carry the unbalanced load

(3) The size of the service neutral shall not be smaller than the size of a neutral selected in accordance in subrule (1) and shall not be smaller than:
(a) #10 AWG copper or #8 AWG aluminum

Last edited by Brian A. MacNeish; 5/27/11 at 3:09 PM..
Reply With Quote
  #3  
Old 5/27/11, 11:27 AM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Tiny service entrance question

A local line worker once told me the current standard is the neutral cannot be no smaller than the power.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #4  
Old 5/27/11, 11:53 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tiny service entrance question

Given the fact that it hasn't burnt up I'm guessing that the size isn't a problem. Could have been left over from an old 30 amp service that was upgraded at some point.
Reply With Quote
  #5  
Old 5/27/11, 12:22 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Tiny service entrance question

Just have it evaluated when the lack of a drip loop gets corrected.
Reply With Quote
  #6  
Old 5/27/11, 12:44 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Tiny service entrance question

Utility companies pretty much get to do what they want, and they get to make the call here. It's an open-air conductor and probably capable of carrying more load than would ever be necessary.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 5/27/11, 3:04 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tiny service entrance question

Quote:
Originally Posted by jbraun View Post
A local line worker once told me the current standard is the neutral cannot be no smaller than the power (?????).
Please explain what "the power" is?
Reply With Quote
  #8  
Old 5/27/11, 3:05 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tiny service entrance question

The NEC not have a rule on the neutral conductor size??
Reply With Quote
  #9  
Old 5/28/11, 8:45 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Tiny service entrance question

Quote:
Originally Posted by Brian A. MacNeish View Post
The NEC not have a rule on the neutral conductor size??
There are several. However, the service drop conductors in this photo would not fall under the purview of the NEC.
Reply With Quote
  #10  
Old 5/29/11, 10:49 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: Tiny service entrance question

Jeffrey is correct . The electrical companies make their own rules . Here the codes starts after the meter .



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service Entrance Switch and SubPanels Steve S. Onyak Electrical Inspections 11 5/4/11 12:53 AM
Service Entrance Question jgromkoski Electrical Inspections 4 5/18/09 10:27 PM
Service entrance and a raised garden tjansson Electrical Inspections 18 9/7/07 8:47 AM
Service panel Question cpetty Electrical Inspections 4 1/24/07 9:36 PM
Service Entrance Panels gwhite1 Electrical Inspections 4 5/15/06 8:33 PM