1. I just wanted to get clarification on calculating total amps if there is no main disconnect. The service to the house is 200amps at the meter, but there were only 2 breakers at the main panel a 100 amp to the subpanel and a 20 amp breaker for the Garage. Does this indicate that the service at the house is only 120 amps.
2. The main panel and the subpanel did not have a breaking for the AC. But the disconnect at the unit looked to be a 60amp breaker by the marking on it's side that indicated 60A. This it ok that there is no breaker at the main panel or sub? David Alvares Modesto, CA 95354 866-757-8480 |
|
#2
|
||||
|
||||
"Never underestimate the difficulty of changing false beliefs by facts." |
|
#3
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
That is a non fused AC disconnect, Square D. It is rated for 60 amps but that is NOT a circuit breaker, it is just a switch, for service disconnecting means. Your picture is too fuzzy to read but it should state the on the side. If it were an overcurrent protective device, the rating would be stamped on the handle.
There should be a circuit breaker ahead of this disco, but I don't really see on in your pics. Last edited by brian winkle; 12/22/08 at 10:37 PM.. |
|
#4
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
OK David I just got one from my shed. The label on the front next to the handle says "Caution: Provides No Overcurrent Protection"
The label on the side says "Molded Case Switch QO 200 60A ..........................Requires Overcurrent Protection of equivalent rating" Since there doesn't appear to be a breaker anywhere for it or for another sub panel, when you opened the panels did you see a double tap on the mains? |
|
#5
|
||||
|
||||
|
You can't add-up the breaker ratings to determine the service capacity. The service capacity is determined by the lowest rated component of the service equipment, such as the panel rating, SEC size, etc. Mike gave you a good link.
It's a good practice to read the information provided on equipment. As Brian stated, the AC "breaker" is in fact, just a switch. It provides no over-current protection to the system. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
|||
|
|||
|
Quote:
David Alvares Modesto, CA 95354 866-757-8480 |
|
#7
|
|||
|
|||
|
Quote:
I have read over the information provided in that link and I understand that to determine the service rating I need to determine the lowest rated component. So here is my question is if the The Panel, the meter , SEC size, etc. are all rated 200amp, but there is not service disconnect and there are 2 breakers one rated 100 amp for a sub and the other is 20 amp for that garage GFI. Is the service 120 amps. I understand that if I had 4 breakers that totaled 250 amps that the service amps would only be 200amps because of the lowest rated component. I hope that this clarifies my true question. David Alvares Modesto, CA 95354 866-757-8480 |
|
#8
|
||||
|
||||
|
David, the label on the main service panel(with the 100 and 20) will determine your service size assuming you have correctly identified the meter and SE cable to be 200A.
That may be a 150A main panel but I can't read the label. You still can't add breakers to determine service size. "Never underestimate the difficulty of changing false beliefs by facts." |
|
#9
|
|||
|
|||
|
Quote:
David Alvares Modesto, CA 95354 866-757-8480 |
|
#10
|
||||
|
||||
|
You also haven't determined where the over current protection is for the AC unit which should also be noted in your report.
"Never underestimate the difficulty of changing false beliefs by facts." |
|
#11
|
|||
|
|||
|
David,
If the meter, panel, and subpanel are rated 200 amps then the next step is to determine the wire size to the main panel. If the wire size is 2/0 cu or 4/0 alum it is a 200 service, if the wire size is #1 cu or 2/0 alum it is a 150 amp service (see Table 310.15(B)(6) NEC) for other wire sizes and amps. The breakers in the main panel do not determine the service size in this case. You could add 4 more breakers to the main panel giving it 6 throws as long as the connected load does not exced the total calculated load. As for the A/C If it is a split unit it could be a non coincidental load Ex. Electric Heat strip does not run when the cooling is called for and compressor does not run when the electric heat is called for. Therefore The breaker for the air handler could be feeding the air handler and then to the compressor. But I would need more info to determine that. There could even be a small panel at the air handler. Just a possibility, but like i said more info is needed. |
|
#12
|
|||
|
|||
|
Quote:
David Alvares Modesto, CA 95354 866-757-8480 |
|
#13
|
|||
|
|||
|
The A/C breaker seems to be a mystery since the heat is gas. Good luck on this one.
|
|
#14
|
|||
|
|||
|
Please Note:
Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
The panel directory could be mis-labeled?
|
|
#15
|
|||
|
|||
|
Please Note:
Keith White is a non-member guest and is in no way affiliated with InterNACHI or its members.
I bet the 25 amp 2 pole breaker is for the ac.
Turn the breaker off, then test the ac. |
![]() |