  #1  
Old 12/22/08, 6:57 PM
David B. Alvares David B. Alvares is offline
InterNACHI Member
 
Join Date: May 2008
Location: Hilmar, CA
Posts: 13
Default Total Amps and missing AC breaker

1. I just wanted to get clarification on calculating total amps if there is no main disconnect. The service to the house is 200amps at the meter, but there were only 2 breakers at the main panel a 100 amp to the subpanel and a 20 amp breaker for the Garage. Does this indicate that the service at the house is only 120 amps.

2. The main panel and the subpanel did not have a breaking for the AC. But the disconnect at the unit looked to be a 60amp breaker by the marking on it's side that indicated 60A. This it ok that there is no breaker at the main panel or sub?
Attached Thumbnails
total-amps-and-missing-ac-breaker-100_0851.jpg   total-amps-and-missing-ac-breaker-100_0993.jpg   total-amps-and-missing-ac-breaker-100_0859.jpg  




David Alvares
Modesto, CA 95354
866-757-8480
Reply With Quote
  #2  
Old 12/22/08, 7:24 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Total Amps and missing AC breaker

A resource for you to review.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 12/22/08, 10:33 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Total Amps and missing AC breaker

That is a non fused AC disconnect, Square D. It is rated for 60 amps but that is NOT a circuit breaker, it is just a switch, for service disconnecting means. Your picture is too fuzzy to read but it should state the on the side. If it were an overcurrent protective device, the rating would be stamped on the handle.

There should be a circuit breaker ahead of this disco, but I don't really see on in your pics.

Last edited by brian winkle; 12/22/08 at 10:37 PM..
Reply With Quote
  #4  
Old 12/22/08, 10:44 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Total Amps and missing AC breaker

OK David I just got one from my shed. The label on the front next to the handle says "Caution: Provides No Overcurrent Protection"

The label on the side says "Molded Case Switch QO 200 60A ..........................Requires Overcurrent Protection of equivalent rating"

Since there doesn't appear to be a breaker anywhere for it or for another sub panel, when you opened the panels did you see a double tap on the mains?
Reply With Quote
  #5  
Old 12/22/08, 10:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Total Amps and missing AC breaker

You can't add-up the breaker ratings to determine the service capacity. The service capacity is determined by the lowest rated component of the service equipment, such as the panel rating, SEC size, etc. Mike gave you a good link.

It's a good practice to read the information provided on equipment. As Brian stated, the AC "breaker" is in fact, just a switch. It provides no over-current protection to the system.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 12/23/08, 12:39 AM
David B. Alvares David B. Alvares is offline
InterNACHI Member
 
Join Date: May 2008
Location: Hilmar, CA
Posts: 13
Default Re: Total Amps and missing AC breaker

Quote:
Originally Posted by brian winkle View Post
OK David I just got one from my shed. The label on the front next to the handle says "Caution: Provides No Overcurrent Protection"

The label on the side says "Molded Case Switch QO 200 60A ..........................Requires Overcurrent Protection of equivalent rating"

Since there doesn't appear to be a breaker anywhere for it or for another sub panel, when you opened the panels did you see a double tap on the mains?
As you can see in my original photos there is not label that indicates an AC unit. I have also attached a photo to show that were are no apparent double taps. This is a newer home built in 2005. Should I recommend that it appear that the AC unit does not have any overcurrent protection and needs future evaluation by an electriciton.
Attached Thumbnails
total-amps-and-missing-ac-breaker-100_0853.jpg   total-amps-and-missing-ac-breaker-100_0990.jpg  




David Alvares
Modesto, CA 95354
866-757-8480
Reply With Quote
  #7  
Old 12/23/08, 12:54 AM
David B. Alvares David B. Alvares is offline
InterNACHI Member
 
Join Date: May 2008
Location: Hilmar, CA
Posts: 13
Default Re: Total Amps and missing AC breaker

Quote:
Originally Posted by jpope View Post
You can't add-up the breaker ratings to determine the service capacity. The service capacity is determined by the lowest rated component of the service equipment, such as the panel rating, SEC size, etc. Mike gave you a good link.

It's a good practice to read the information provided on equipment. As Brian stated, the AC "breaker" is in fact, just a switch. It provides no over-current protection to the system.
Jeff,

I have read over the information provided in that link and I understand that to determine the service rating I need to determine the lowest rated component. So here is my question is if the The Panel, the meter , SEC size, etc. are all rated 200amp, but there is not service disconnect and there are 2 breakers one rated 100 amp for a sub and the other is 20 amp for that garage GFI. Is the service 120 amps. I understand that if I had 4 breakers that totaled 250 amps that the service amps would only be 200amps because of the lowest rated component. I hope that this clarifies my true question.




David Alvares
Modesto, CA 95354
866-757-8480
Reply With Quote
  #8  
Old 12/23/08, 1:08 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Total Amps and missing AC breaker

David, the label on the main service panel(with the 100 and 20) will determine your service size assuming you have correctly identified the meter and SE cable to be 200A.

That may be a 150A main panel but I can't read the label.

You still can't add breakers to determine service size.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #9  
Old 12/23/08, 1:34 AM
David B. Alvares David B. Alvares is offline
InterNACHI Member
 
Join Date: May 2008
Location: Hilmar, CA
Posts: 13
Default Re: Total Amps and missing AC breaker

Quote:
Originally Posted by mlarson View Post
David, the label on the main service panel(with the 100 and 20) will determine your service size assuming you have correctly identified the meter and SE cable to be 200A.

That may be a 150A main panel but I can't read the label.

You still can't add breakers to determine service size.
Michael, thank you for the clarification and the web link.




David Alvares
Modesto, CA 95354
866-757-8480
Reply With Quote
  #10  
Old 12/23/08, 1:37 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Total Amps and missing AC breaker

Quote:
Originally Posted by dalvares View Post
Michael, thank you for the clarification and the web link.
You also haven't determined where the over current protection is for the AC unit which should also be noted in your report.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #11  
Old 12/23/08, 1:49 AM
GARY R. EVANS GARY R. EVANS is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Coconut Creek, FL
Posts: 45
Default Re: Total Amps and missing AC breaker

David,
If the meter, panel, and subpanel are rated 200 amps then the next step is to determine the wire size to the main panel. If the wire size is 2/0 cu or 4/0 alum it is a 200 service, if the wire size is #1 cu or 2/0 alum it is a 150 amp service (see Table 310.15(B)(6) NEC) for other wire sizes and amps. The breakers in the main panel do not determine the service size in this case. You could add 4 more breakers to the main panel giving it 6 throws as long as the connected load does not exced the total calculated load.
As for the A/C If it is a split unit it could be a non coincidental load Ex. Electric Heat strip does not run when the cooling is called for and compressor does not run when the electric heat is called for. Therefore The breaker for the air handler could be feeding the air handler and then to the compressor. But I would need more info to determine that. There could even be a small panel at the air handler. Just a possibility, but like i said more info is needed.
Reply With Quote
  #12  
Old 12/23/08, 2:20 AM
David B. Alvares David B. Alvares is offline
InterNACHI Member
 
Join Date: May 2008
Location: Hilmar, CA
Posts: 13
Default Re: Total Amps and missing AC breaker

Quote:
Originally Posted by gevans2 View Post
David,
As for the A/C If it is a split unit it could be a non coincidental load Ex. Electric Heat strip does not run when the cooling is called for and compressor does not run when the electric heat is called for. Therefore The breaker for the air handler could be feeding the air handler and then to the compressor. But I would need more info to determine that. There could even be a small panel at the air handler. Just a possibility, but like i said more info is needed.
This is a Gas fired Heater with an air handler that is plunged into an outlet that is protected by a fuse and there was not small panel in the attic were the unit was located (i double checked by reviewing my pictures).




David Alvares
Modesto, CA 95354
866-757-8480
Reply With Quote
  #13  
Old 12/23/08, 10:33 AM
GARY R. EVANS GARY R. EVANS is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Coconut Creek, FL
Posts: 45
Default Re: Total Amps and missing AC breaker

The A/C breaker seems to be a mystery since the heat is gas. Good luck on this one.
Reply With Quote
  #14  
Old 12/23/08, 1:46 PM
Mark Thorman Mark Thorman is offline
Active Poster
 
Join Date: Mar 2008
Posts: 166
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Total Amps and missing AC breaker

The panel directory could be mis-labeled?
Reply With Quote
  #15  
Old 12/25/08, 11:52 PM
Keith White Keith White is offline
New User
 
Join Date: Oct 2008
Posts: 1
Please Note: Keith White is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Total Amps and missing AC breaker

I bet the 25 amp 2 pole breaker is for the ac.
Turn the breaker off, then test the ac.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 3:53 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts