  #1  
Old 9/19/10, 7:10 AM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Trimmed SEC

Hey Guys-

I found this on a 1995 home. The SEC was trimmed because it wouldn't fit in the lug. The label on the breaker states "...torque to 180 LB in 2/0 AWG..." I know the conductor going into the house was a 4/0 AWG from the jacket on the interior. But I don't see on the conductor from the meter a label listing it's size even though the info on the conductor is quite clear...unless I'm missing something. Anyway, in order to get it to fit, it looks like they trimmed off the outside section of strands. I was going to write it up but wasn't for sure how big of deal to make about it. Is this something I should recommend for an electrician to come repair?

Kenny
Attached Thumbnails
trimmed-sec-img_8885.jpg   trimmed-sec-img_8887.jpg   trimmed-sec-img_8889.jpg   trimmed-sec-img_8891.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/19/10, 7:17 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Trimmed SEC

Yes not allowed .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #3  
Old 9/19/10, 7:25 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Trimmed SEC

The line side conductors are 350 kcmil. Their marking is visible in photo#3. Yes this is a violation. It could be fixed with a pin adapter product like this:


Last edited by Robert Meier; 9/19/10 at 10:17 AM.. Reason: Added image
Reply With Quote
  #4  
Old 9/19/10, 9:11 AM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Trimmed SEC

350 Kcmil are rated for 300 amps on a feeder. The problem is computing how much of the conductor is left after trimming and the resulting ampacity. RM posted a good solution that would not involve needing new conductors.
Reply With Quote
  #5  
Old 9/19/10, 11:23 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Trimmed SEC

Well......that would be ok but as for needing new conductors...but this conductor I would say the adapter is pointless at this point. The conductor has been altered and so I would make them replace it if I was the municipal inspector inspecting this.

As an HI....let them know about it in your report and let them decide.



Paul W. Abernathy
Reply With Quote
  #6  
Old 9/20/10, 4:50 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Trimmed SEC

Quote:
Originally Posted by pabernathy View Post
Well......that would be ok but as for needing new conductors...but this conductor I would say the adapter is pointless at this point. The conductor has been altered and so I would make them replace it if I was the municipal inspector inspecting this.

As an HI....let them know about it in your report and let them decide.
Paul, the problem is with the termination not the conductor. Are you saying that you would make someone install new conductors as opposed to properly terminating the existing ones?
Reply With Quote
  #7  
Old 9/20/10, 9:31 AM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Trimmed SEC

Quote:
Originally Posted by pabernathy View Post
Well......that would be ok but as for needing new conductors...but this conductor I would say the adapter is pointless at this point. The conductor has been altered and so I would make them replace it if I was the municipal inspector inspecting this.

As an HI....let them know about it in your report and let them decide.
The end of the conductor has been altered, not the whole conductor. I fail to see how cutting off 3/4" of the reduced conductor and adding a pin adapter to the full cross sectional area would not be compliant. How would this be any different than pulling new over-sized conductors and adding a pin adapter?

Sorry Paul, not with you on this one.
Reply With Quote
  #8  
Old 9/20/10, 5:22 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Trimmed SEC

I said I would make them REDO it.......if they can cut it off where they attemtped to alter the conductor and then strip it back and install the adapter then fine....thats for them to decide....as a municpal I FAIL them until they meet the intent of the conductor, without altering it and then installing the adapter.....

Replace......as in REDO....attempt this again.......cut away the damage.....start over.....do a proper termination...how they achieve it is not my concern.



Paul W. Abernathy
Reply With Quote
  #9  
Old 9/20/10, 5:27 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Trimmed SEC

Quote:
Originally Posted by Jim Port View Post
The end of the conductor has been altered, not the whole conductor. I fail to see how cutting off 3/4" of the reduced conductor and adding a pin adapter to the full cross sectional area would not be compliant. How would this be any different than pulling new over-sized conductors and adding a pin adapter?

Sorry Paul, not with you on this one.
Because the contractor has no authority to alter the conductor. he is not a manufacturer, he cant account for the circular mil it is now and I am not assuming anything.....so the question is you would condone them having a larger conductor than needed and trimming away a few strands?

I dont get paid to RECONFIGURE the circular mils of a conductor that was altered. Not my fault they ran the wrong size conductors so they can cut it back...start fresh, install the adapter that is proper or change the lug to fit that size conductor and be compliant...there choice.

I will never attempt to give someone a GREEN light to alter a conductor and have it hold up in court on what the Circular Mils are now.....not my job and not my engineering going into the job.

You can allow it any way you wish.....where I am the municipal inspector it aint gonna happen.....call me what you will...

Just my opinions....ok not to agree with me....many dont !



Paul W. Abernathy
Reply With Quote
  #10  
Old 9/20/10, 6:10 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Trimmed SEC

Nice catch Kenny!
How many get picky by calling out damaged insulation when the contractor got carried away removing the outer jacket?

trimmed-sec-dsc00575.jpgtrimmed-sec-dsc00575-1.jpg




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...

Last edited by wwarner; 9/20/10 at 6:16 PM..
Reply With Quote
  #11  
Old 9/20/10, 6:54 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Trimmed SEC

Quote:
Originally Posted by pabernathy View Post
Because the contractor has no authority to alter the conductor. he is not a manufacturer, he cant account for the circular mil it is now and I am not assuming anything.....so the question is you would condone them having a larger conductor than needed and trimming away a few strands?

I dont get paid to RECONFIGURE the circular mils of a conductor that was altered. Not my fault they ran the wrong size conductors so they can cut it back...start fresh, install the adapter that is proper or change the lug to fit that size conductor and be compliant...there choice.

I will never attempt to give someone a GREEN light to alter a conductor and have it hold up in court on what the Circular Mils are now.....not my job and not my engineering going into the job.

You can allow it any way you wish.....where I am the municipal inspector it aint gonna happen.....call me what you will...

Just my opinions....ok not to agree with me....many dont !
Paul, I think that you need to re-read Jim's post. He's not saying what you think he's saying.
Reply With Quote
  #12  
Old 9/20/10, 7:41 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Trimmed SEC

Thanks Robert. I was not in any way condoning or approving the modified circular mils of the conductor. I was saying cut the reduced end off and start anew with the full sized conductor and add the pin reducer.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Verbage for trees rwashington Structural Inspections 14 8/10/09 6:55 PM


All times are GMT -4. The time now is 7:17 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts