Default Trumbull Electric panel

Found this panel in a 1960's home. How many issues do you see? Sorry the pics aren't more clear. Aluminum strand wiring, 70 amp undersized, no grounds only neutrals, lugs on the sides of panel double tapped feeding both the range and dryer, no disconnect unless the linked breaker top center is the main (my guess), otherwise 7 hand movements ...water heater on another meter. I have not seen this panel before.
Attached Thumbnails
trumbull-electric-panel-215-3rd-st-sw-139-small-.jpg.jpg
Views:	54
Size:	23.6 KB
ID:	29285   trumbull-electric-panel-215-3rd-st-sw-142-small-.jpg.jpg
Views:	57
Size:	45.1 KB
ID:	29286   trumbull-electric-panel-215-3rd-st-sw-141-small-.jpg.jpg
Views:	56
Size:	37.9 KB
ID:	29287   trumbull-electric-panel-215-3rd-st-sw-140-small-.jpg.jpg
Views:	55
Size:	41.5 KB
ID:	29288  
Reply With Quote
Find an InterNACHI certified Nevada Home Inspector (and anywhere else in North America)
  #2  
Old 6/15/09, 10:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,032
Default Re: Trumbull Electric panel

Old and obsolete. Are you sure about the date? These are generally found in much older buildings - like 40's or 50's.

I don't believe that you have AL wiring in that panel. It looks to me like tinned-copper - hard to tell for sure.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 6/15/09, 10:38 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 243
Default Re: Trumbull Electric panel

Hi Jeff,
No I am not sure about the date, the realtor gave me that date, I was thinking it might be older as well. It could be copper tin coated but I didn't see the cut end. Am I correct about this panel having a main disconnect? Would that open the circuits to the dryer and range that are on the sides?
Reply With Quote
  #4  
Old 6/15/09, 11:55 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,032
Default Re: Trumbull Electric panel

I've never seen one of these used as service equipment. Usually it's a load-side panel (subpanel) with a service disconnect somewhere else.

The two double-tapped lugs on the side are likely for the feeders from the service disconnect. It's not likely that the two-pole breaker acts as the disconnect.

How did you determine that it's a 70 amp service?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 6/16/09, 12:11 AM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 243
Default Re: Trumbull Electric panel

I used a gauge on the alum service entry wires #4. Also the dead front panel concured stating that it was 70 amp max. I believe that you maybe right, The lugs on the side are probably double tapped mains which probably fed the dryer disconnect. The double breaker is probably used for the range. That helps alot. So after all with seven hand movements and one not disconnected at the panel.
Reply With Quote
  #6  
Old 6/16/09, 12:17 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,032
Default Re: Trumbull Electric panel

You have good enough information to defer this panel - between the tinned copper, double taps and age of the panel.

Next time, concentrate on getting clearer photos



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Electrical Safety Media Center jtedesco1 Electrical 1 3/15/08 9:18 AM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical 72 3/12/08 12:19 AM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 3:46 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts