  #1  
Old 11/6/07, 2:34 PM
Russell Truluck Russell Truluck is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Travelers Rest, SC
Posts: 22
Default Try again, what's wrong?

This plug goes to and supplies power for the gas furnace about 3 feet away in the crawl space. No other form of disconnect. Furnace installed in 1992. Any problems?
Attached Thumbnails
try-again-whats-wrong-picture-044.jpg  
Reply With Quote
  #2  
Old 11/6/07, 2:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Try again, what's wrong?

A cord and plug is a means of disconnect, however, that doesn't appear to be a listed assembly. In other words, it looks "home made."

Secondly, The furnace needs to be listed for a cord and plug. Most modern furnaces are not listed as such.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 11/6/07, 2:45 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Try again, what's wrong?

Missing coverplate on the duplex receptacle too.

Check mfg. specs for any required overlaod protection ahead of the furnace.
Reply With Quote
  #4  
Old 11/6/07, 3:08 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Try again, what's wrong?

If there is a condensate pump and its within 6 feet of it, it should be a GFCI.
Reply With Quote
  #5  
Old 11/6/07, 4:15 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Try again, what's wrong?

In addition to the problems already mentioned.....It is hard to see in the picture, but the ground wire in the cord appears to be folded back and not terminated in the plug.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #6  
Old 11/6/07, 7:34 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Try again, what's wrong?

Quote:
Originally Posted by Ian Gills
If there is a condensate pump and its within 6 feet of it, it should be a GFCI.
Why?
Reply With Quote
  #7  
Old 11/6/07, 9:02 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Try again, what's wrong?

Quote:
Originally Posted by jpope

Secondly, The furnace needs to be listed for a cord and plug. Most modern furnaces are not listed as such.
Jeff, do you have some info to support that? In my area I have yet to see an indoor gas furnace/air handler that was NOT plug and cord connected, even the new ones. At rough in we supply a 20 amp circuit to a fused receptacle for all indoor units, have never been failed yet.
Reply With Quote
  #8  
Old 11/6/07, 9:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Try again, what's wrong?

Quote:
Originally Posted by brian winkle
Jeff, do you have some info to support that?
Which part?

I haven't seen a cord & plug furnace/airhandler installed in anything newer than about '96, in quite some time.

The units I see in newer construction are hardwired to a switched outlet and are not listed for cord & plug attachments.

I'm certainly not saying they don't exist, but C&P units seem to be a thing of the past in our parts.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 11/6/07, 10:15 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Try again, what's wrong?

Romex?



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 11/6/07, 10:57 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Try again, what's wrong?

Cord and plug air handlers seem to be a local thing. I hear a lot of people say that is a regular thing, other places never see it. C&P water heaters are a similar thing.
Reply With Quote
  #11  
Old 11/6/07, 11:38 PM
gporter's Avatar
gporter gporter is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Orlando, fl
Posts: 3,281
Default Re: Try again, what's wrong?

I have never saw one but it still must be connected to a double throw breaker. I know payne does make some.



Gary Porter

GLP's Home and Mold Inspections
321-239-0621

Certified Commercial Mold Inspector

Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford
Orange County, Seminole County, Volusia County, Osceola County

www.homeandmoldinspections.com
Reply With Quote
  #12  
Old 11/7/07, 8:25 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,153
Default Re: Try again, what's wrong?

Thats all I see here in AZ. Plugged in..




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #13  
Old 11/7/07, 6:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Try again, what's wrong?

Quote:
Originally Posted by gporter
I have never saw one but it still must be connected to a double throw breaker.
I assume you mean a two-pole (240 volt) breaker? I have never seen a 240 volt furnace/airhandler. The condenser, on the other hand, usually requires 240 volts.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 11/7/07, 6:54 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Try again, what's wrong?

You see 240v air handlers if that is also where the heat comes from (toaster heaters) and most of the time it is A/C. I know that is a foreign concept to folks in the frozen north but here below the 27th parallel "heat" as a 3 or 4 day a year thing. Nobody has a "furnace".
Reply With Quote
  #15  
Old 11/9/07, 9:03 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Try again, what's wrong?

Personally...I'll give my opinions on it for what it is worth...lol

1.) Last time I checked NM Cable was not considered a cord and putting an attachment plug onto it and allowing it to be used also as perm. wiring is well probably a problem...

2.) As someone stated...seems they have NO use for the EGC to be used at the furnace itself, they simply DID bend back the EGC within the NM Cable...and if it is gas..connected to electricity then in opinion it is " likely to become energized " since it DOES have a common connection so since this happens...guess you can't use the exception of the EGC as the bond......BUT wait...probably no EGC's in the whole house....yet 3 prong plug in the outlet....dont know...only the orginal poster knows that.

3.) Also we could argue dedicated equipment....BUT we have an open duplex that allows for serving as well I see.....and the NEC says receptacles in crawl spaces at or below grade need to be GFCI.....so if we argued the dedicated receptacle theory...in my " INT " I would make them replace the receptacle with a single receptacle...and oh yeah..add the cover also...

Just my thoughts on it......but then again I have JET LAG from flying late last night.....



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Grandpa, what is wrong with the patio? mcyr Exterior Inspections 1 5/12/07 10:29 PM
see anything wrong jmaisano Electrical Inspections 16 10/31/06 5:23 PM
Anything Wrong Here? scosta Inspecting HVAC Systems 12 6/29/06 9:06 AM