Default tubs and switches

switch.tub.jpg

switchtub2.jpg

Is this OK?

I don't feel good about a light switch in reach of the tub. But can't find anything against it in CodeCheck, Rex Cauldwell, or through a cursory search of this board.

Can a light switch be located within three feet of the tub?



Tom Jansson, Owner/Inspector
Acuity Home Inspection Services
Reply With Quote
  #2  
Old 10/10/08, 3:07 AM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: nord-est [ northeast] wisconsin
Posts: 125
Marc Benz is generally well trusted
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: tubs and switches

It is fine with that set up unless local code say something else.

{ expect some debate with this one and I can't quote which fourm but I know they did have good debate I think unless I goof up they did have simauir thread related to this sometime back }

Merci,Marc
Reply With Quote
  #3  
Old 10/10/08, 3:14 AM
Thomas Jansson's Avatar
Thomas Jansson Thomas Jansson is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Chicago, IL
Posts: 134
Thomas Jansson .
Default Re: tubs and switches

Thanks, Marc. Looks like it's ok after all.

Found more on this topic here



Tom Jansson, Owner/Inspector
Acuity Home Inspection Services
Reply With Quote
  #4  
Old 10/10/08, 3:18 AM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: nord-est [ northeast] wisconsin
Posts: 125
Marc Benz is generally well trusted
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: tubs and switches

That good and you got a good answer here and the old topic fourm do come handy to refering the question what you are looking for.

Merci,Marc
Reply With Quote
  #5  
Old 10/10/08, 8:01 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: tubs and switches

When ever this comes up there is always a huge debate about it.

Fact is, in the US there is nothing prohibiting it, and installed properly there is nothing unsafe about it either.
Reply With Quote
  #6  
Old 10/10/08, 9:46 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,248
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: tubs and switches

Quote:
Originally Posted by Speedy Petey View Post
When ever this comes up there is always a huge debate about it.

Fact is, in the US there is nothing prohibiting it, and installed properly there is nothing unsafe about it either.

They may be confusing the "no rule for switches" with the rule for receptacles in bathrooms:

in Canada- CEC 26-710(g)- "receptacles installed in bathrooms shall, where practicable, be located at least 1 meter (39.28") but in no case less than 500mm from the bathtub or shower...."
Reply With Quote
  #7  
Old 10/10/08, 8:42 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,937
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: tubs and switches

Hello Everyone-

Here is a link to some information regarding this question for those friends up north. AS for the NEC, AS long as the receptacle does not break the plane of the shower stall or tubs threashold it is allowed and the same goes for the switch. Keep in mind a switch COULD be within the shower IF it was manufactured as part of the shower assembly and rated as such...

Canadian Info Link :http://www.iaei.org/subscriber/magaz...nadiancode.htm

But in general it is allowed on a normal bathtub and shower location. But remember all receptacles in the bathroom must be on GFCI regardless.

For those Codies....here you go...

Receptacles - 406.8(c)

(C) Bathtub and Shower Space.
Receptacles shall not be
installed within or directly over a bathtub or shower stall.

Switches -404.4
404.4 Wet Locations.


A switch or circuit breaker in a wet
location or outside of a building shall be enclosed in a
weatherproof enclosure or cabinet that shall comply with
312.2(A). Switches shall not be installed within wet locations
in tub or shower spaces unless installed as part of a
listed tub or shower assembly.


NOW.......as for the requirements of all receptacles in a bathroom be GFCI....here you go:

210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel.
FPN: See 215.9 for ground-fault circuit-interrupter protection
for personnel on feeders.
(A) Dwelling Units.


All 125-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
(1) through (8]shall have ground-fault circuit-interrupter
protection for personnel.
(1) Bathrooms

Now as HI's....check for GFCI's and call it as you see it.....you guys save lives so go with your feelings but let the situation dictate it and keep the minimum safety standards of the evolving NEC in the back of your mind....

Here is some additional info you might like....on metal coverplate on the switches and you know the system is a non-grounded system be aware of this important info also...

FacePlates 404.9(B)
(B) Grounding.


Snap switches, including dimmer and
similar control switches, shall be effectively grounded and
shall provide a means to ground metal faceplates, whether
or not a metal faceplate is installed. Snap switches shall be
considered effectively grounded if either of the following
conditions is met:
(1) The switch is mounted with metal screws to a metal
box or to a nonmetallic box with integral means for
grounding devices.
(2) An equipment grounding conductor or equipment
bonding jumper is connected to an equipment grounding
termination of the snap switch.


Exception to (B): Where no grounding means exists within
the snap-switch enclosure or where the wiring method does
not include or provide an equipment ground, a snap switch
without a grounding connection shall be permitted for replacement
purposes only. A snap switch wired under the
provisions of this exception and located within reach of
earth, grade, conducting floors, or other conducting surfaces
shall be provided with a faceplate of nonconducting,
noncombustible material or shall be protected by a groundfault
circuit interrupter.




Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.

Last edited by pabernathy; 10/10/08 at 8:56 PM.
Reply With Quote
  #8  
Old 10/10/08, 11:59 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,248
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: tubs and switches

Quote:
Originally Posted by pabernathy View Post
Hello Everyone-

Here is a link to some information regarding this question for those friends up north. AS for the NEC, AS long as the receptacle does not break the plane of the shower stall or tubs threashold it is allowed and the same goes for the switch. Keep in mind a switch COULD be within the shower IF it was manufactured as part of the shower assembly and rated as such...

Canadian Info Link :http://www.iaei.org/subscriber/magaz...nadiancode.htm

But in general it is allowed on a normal bathtub and shower location. But remember all receptacles in the bathroom must be on GFCI regardless.


Thanks, Paul, for adding this.......I was assuming that people would know that the recepts in proximity of the tub or washbasin would be GFCI protected........but then it's always better to state something like this!!
Reply With Quote
  #9  
Old 10/11/08, 10:48 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Mike Whitt is almost always very helpful Mike Whitt is almost always very helpful Mike Whitt is almost always very helpful Mike Whitt is almost always very helpful Mike Whitt is almost always very helpful Mike Whitt is almost always very helpful
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: tubs and switches

Paul

Not wanting to highjack a thread nor turn it into a code discussion but I feel that this needs to be address here for the HI

In the exception you have highlighted with bold where no EGC is present and a nonconductive plate is used, do you think that the metal 6/32 x ½ inch screws should be replaced with nylon screws holding the cover in place?
Reply With Quote
  #10  
Old 10/11/08, 2:51 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,937
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: tubs and switches

Quote:
Originally Posted by Mike Whitt View Post
Paul

Not wanting to highjack a thread nor turn it into a code discussion but I feel that this needs to be address here for the HI

In the exception you have highlighted with bold where no EGC is present and a nonconductive plate is used, do you think that the metal 6/32 x ½ inch screws should be replaced with nylon screws holding the cover in place?
Are you asking for my opinion or code....lol.....lets look at the statement:

A snap switch wired under the
provisions of this exception and located within reach of
earth, grade, conducting floors, or other conducting surfaces
shall be provided with a faceplate of nonconducting,
noncombustible material or shall be protected by a groundfault
circuit interrupter.

IN my view the latter is the best situation for the older home that HI's see and since they are concerned alot of these locations it would not harm them to suggest it. Also I dont believe the NEC requires these nylon screws...just the nonconductive faceplate ...But is it a good suggestion....quite possibly as some may feel differently about it.

HEY...DMV was closed, he called me as I was getting ready to leave...guess he drives the bike back without a tag on it....oh well...not mine anymore...lol

Anyway.....also Mike I believe the normal switches with the normal nylon coverplates have a coating on the screws surface that make them well...not as conductive to the point I would be overly concerned about it.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.

Last edited by pabernathy; 10/11/08 at 3:04 PM.
Reply With Quote
  #11  
Old 10/13/08, 3:44 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 242
Frank P. Newman is generally well trusted
Default Re: tubs and switches

Or, if the installer wanted to be as safe as possible (under the circumstances) he could use one of the "screwless" covers now available. However, at the low cost fo a GFCI, that would be my recommendation as well.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On