Here are what appeared to be two twisted pairs of #10s on a 60 A breaker feeding a range. It has obviously been that way for quite some time (house built in 1980). What, if anything, would you have to say about the arrangement?
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
| Need a home inspection in Colorado? Check out InterNACHI's listing of Colorado certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
I would say that it's a very unsafe installation. Parallel conductors are required to be #1/0 and larger and that breaker is not rated for terminating two twisted conductors.
|
|