Default Two circuits in one cable

This mornings inspection had some interesting features courtesy of Home Depot Harry. A 12/3 w/ground was found in the service panel. One wire (and the grounding conductor) landed on the neutral bus, one on a 30-amp breaker (for the dryer) and one on a 15-amp breaker for the lights in another room). I know that the 12awg wire being on a 30-amp breaker is wrong and I suspect the shared circuits in the cable is wrong but can't find the proper wording for that. Any thoughts?



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #2  
Old 11/5/06, 8:47 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 841
Default Re: Two circuits in one cable

How did he get 220v off of one wire. I'm sure that there are 110v dryers out there, but most require a 220v breaker, a 220v receptacle and of course at least 10 gage wire depending on distance of the circuit.

Dryer circuit improperly wired. This could be a fire hazard.
(Brown outing equipment can cause fores too!!)

Dryer circuit - Electrical wire size appears to be under sized on circuits that routinely carry heavy loads. This is a safety and fire hazard.

Non-conventional electrical wiring of multipal circuits. This may cause electrical hazards and/or fire. This may also be an electrical code violation. Your Home Inspector is not a Code Inspector an strongly suggests that the electrical system be inspected by a qualified, licensed, electrical contractor.

The third one I thinks looks the best, but may need some tweeking.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #3  
Old 11/5/06, 8:49 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two circuits in one cable

This is called a "multi-wire" circuit and is perfectly normal. Provided it is wired properly.

"Properly" would be, obviously, breaker sized according to wire size, and the two breakers being on different legs of the panel. Better yet, in a typical panel right next to each other. Many will suggest a two-pole, or handle-tied breaker.

**Edit - On re-reading, I assumed a gas 120v dryer. If this is a 120/240v electric dryer all bets are off.
Reply With Quote
  #4  
Old 11/5/06, 8:56 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 841
Default Re: Two circuits in one cable

Quote:
Originally Posted by Speedy Petey
This is called a "multi-wire" circuit and is perfectly normal. Provided it is wired properly.

"Properly" would be, obviously, breaker sized according to wire size, and the two breakers being on different legs of the panel. Better yet, in a typical panel right next to each other. Many will suggest a two-pole, or handle-tied breaker.

**Edit - On re-reading, I assumed a gas 120v dryer. If this is a 120/240v electric dryer all bets are off.
You know what, I thought electric dryer when I read it was on a 30 amp breaker. But after reading your post, who knows if it is a gas dryer or electric?



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #5  
Old 11/5/06, 10:32 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 667
Default Re: Two circuits in one cable

It was a gas dryer. Only one side of the double breaker was used for that (improperly).

My question really was about the two different circuits being fed by different conductors in a common cable. Shouldn't dedicated lines have been run for each circuit?



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #6  
Old 11/5/06, 10:49 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two circuits in one cable

Quote:
Originally Posted by bsmith
Shouldn't dedicated lines have been run for each circuit?
Absoultely not. A multi-wire circuit is perfectly fine, if wire right.
Reply With Quote
  #7  
Old 11/5/06, 10:52 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two circuits in one cable

Quote:
Originally Posted by bsmith
It was a gas dryer. Only one side of the double breaker was used for that (improperly).

My question really was about the two different circuits being fed by different conductors in a common cable. Shouldn't dedicated lines have been run for each circuit?
No. It is a common and efficient wiring method. If you think about it, it's the same as the power coming into the house from the transformer. It is also done this way in conduit most of the time to decrease conductor count for pipe fill.
Reply With Quote
  #8  
Old 11/5/06, 10:54 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 667
Default Re: Two circuits in one cable

Interesting. I know multi-wire circuits for the same circuit (240-volt dryer, etc) are fine, but the differrent circuit thing threw me. Thanks Pete. Thnaks Brian.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #9  
Old 11/5/06, 11:06 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two circuits in one cable

In the case of a dryer for instance, it is not considered a multi-wire circuit.
That is simply a 120/240v circuit.

It really is kind of odd. A dryer is not considered a multi-wire, and the circuit terminates on a single device yoke.
Yet a multi-wire circuit, terminating only on a split duplex receptacle IS still a multi-wire.
Reply With Quote
  #10  
Old 11/5/06, 11:34 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 667
Default Re: Two circuits in one cable

Thanks again Pete.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #11  
Old 11/6/06, 9:19 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Two circuits in one cable

Bill,

yes, multi-wire circuits are fine if done correctly. It is also a good example of why you want the netural terminating on the neutral buss correctly when it comes to a multi-wire circuit....remove that neutral on the circuit and well.....you burn up equipment and a hazard is produced....

So people should not do multi-wire circuits unless they truly understand what is going on with them......and one important note is to ensure the multi-wire circuit has each circuit on a different leg in the panel.....lke peter said side by side on the same side ensures that.........if split up in the panel YOU run the risk of it being wrong and a neutral conductor that could be overloaded........very important to know how they work....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical 5 2/16/07 1:19 PM
Did you KNOW this about NM Cable? pabernathy Electrical 0 12/19/06 9:46 AM
Hey Joe Tedesco pbolliger Electrical 7 4/11/06 1:17 AM
Ceilings falling with wires in it. jsmith3 Interior 8 3/16/06 8:24 PM


All times are GMT -4. The time now is 7:27 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts