Default Two ground wires

Inspected home with meter base outside with ground from meter base to ground rod. Inside of home there was one service panel with the main shutoff and another ground wire run back to the same accorn ground clamp. Why would they have grounded the meter can and service panel?
Is a ground wire from the meter base an acceptable grounding method?
Both meter and panel are within 15 feet of each other. Meter outside and service equipment panel inside.
Reply With Quote
  #2  
Old 8/9/06, 11:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Two ground wires

James,

Probably due to the LACK of understanding of the NEC requirements I care to venture. The NEC states the GEC can take place at the Meter Can, Service Enclosure or believe it or not at the Service Mast Messenger Wire point.....

My guess is the ground was put in at the meter first ( which our local POCO will not allow...even if the NEC allows it..they are FAST to say it is THERE meter cab and they dont want it in their...)

Then quite possibly the local AHJ said they do not want it in the meter can and want it from the panel...so they just ran another one.....

Can't really tell you why they did both....but to answer your question BOTH locations are accepted as approved attachmenet points by the NEC....as points to which you can connect the GEC to the GE.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #3  
Old 8/9/06, 11:39 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two ground wires

Could also be a POCO requirement.
In my area we did actually have to do exactly what you describe in years past. They then changed it so that NO GEC connections were in "their" meter pan.
Reply With Quote
  #4  
Old 8/9/06, 11:43 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two ground wires

Paul, service wire messenger point? Can you explain please.
Reply With Quote
  #5  
Old 8/9/06, 11:49 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Two ground wires

How about I do ya one better my fine fellow...




(A) Grounding. Services supplied from a utility transformer that is grounded to the earth must have the grounded neutral conductor grounded to a suitable grounding electrode [250.50] in accordance with the following:

(1) Accessible Location. A grounding electrode conductor must connect the grounded neutral conductor to the grounding electrode and this connection can be made at any accessible location, from the load end of the service drop or service lateral, up to and including the service disconnecting means. Figure 250–51
Author’s Comment: Some inspectors require the grounding electrode conductor to terminate at the meter enclosure, while other inspectors insist that the grounding electrode conductor terminate at the service disconnect.

The Code allows this grounding (earthing) connection to be made at either of these locations.
(4) Main Bonding Jumper. When the grounded neutral conductor is bonded to the service disconnecting means [250.24(B)] by a wire or busbar [250.28], the grounding electrode conductor can terminate to either the grounded neutral terminal or the equipment grounding terminal within the service disconnect.

(5) Load-Side Neutral-to-Case Bonding. A neutral-to-case bond cannot be made on the load side of the service disconnecting means, except as permitted for separately derived systems [250.30(A)(1)] or separate buildings [250.32(B)(2)] in accordance with 250.142. Figure 250–52
Author’s Comment: If an improper neutral-to-case bond is made on the load side of service equipment, dangerous objectionable current will flow on conductive metal parts of electrical equipment in violation of 250.6(A). Objectionable current on metal parts of electrical equipment can cause electric shock and even death from ventricular fibrillation. Figure 250–53
(B) Main Bonding Jumper. An unspliced main bonding jumper complying with 250.28 must be installed between the grounded neutral terminal and the metal parts of the service disconnecting means enclosure in accordance with 250.24(C).

OK.....just for short we call the bare wire that supports the service drop the messenger wire...which is also the neutral wire.....or # 1 location in the image I posted....courtesy of Mr. Mike Holt.....



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 8/10/06, 8:47 AM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two ground wires

Your good, thanks Paul and everyone for your comments.
Reply With Quote
  #7  
Old 8/10/06, 9:06 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,607
Default Re: Two ground wires

Paul,
Where do you get your illustrations from?
</IMG>
Reply With Quote
  #8  
Old 8/10/06, 1:59 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Two ground wires

Bruce,

I get them from Mike Holt's Website...www.mikeholt.com and the bottom link on the left. You have to have his permission to use them....which I have so I post them alot...lol



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 8/10/06, 3:06 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two ground wires

Pete, it's funny how POCOs work. FPL wants the GEC in the meter can.
I like it that way too since it might shunt lightning to ground before it gets in the house.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Ground Wires Inside a Panel mveitenhans Electrical 13 10/29/06 12:39 PM
Ground Wires Grouped Together psmothers Electrical 7 5/24/06 8:53 AM
4 ground wires into 1 in main panel psiposs Electrical 13 5/18/06 2:27 PM
Comments on ground wires (left side) jweinberg Electrical 22 1/9/06 6:27 AM


All times are GMT -4. The time now is 5:17 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts