#1
|
||||
|
||||
|
The main disconnect was on the little panel and the larger panel
controlled the branch circuits. I need help on writing this configuration up. I could not read the amperage on the main disconnect. 60 amp ? plz help.
|
|
#2
|
||||
|
||||
|
The cover below the meter should have a municipal lock on it.
As for amperage, I need a closer picture. The panel on the left appears to have an FPE beaker. Not good. |
|
#3
|
|||
|
|||
|
Typically, the main is where the service disconnect is and the other is a sub panel. The enclosure on the left looks field modified. I mean, I've never seen wood framing when I opened a panel before.
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#4
|
||||
|
||||
|
Quote:
If this is a commercial property, I agree it should have a lock on it. The panel on the right would be the main, and the panel on the left would be a sub panel. I'm not sure what is going on with the big outer box, and smaller inner box. That's kind of weird, maybe it was some sort of upgrade at some point in history. Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#5
|
||||
|
||||
|
There is only one service panel, with a disconnect. The other is a "sub" panel, and should be wired as such.
This is a pretty standard installation for the late '40's and '50's in CA. The original panel (with the meter) did not have enough room for additional circuits and the other panel (on the left) was added for "expansion." No lock is required on the service equipment. There is nothing wrong with this "setup" (assuming the sub panel has a cover), but it's difficult to tell whether or not they're wired properly. These are both FPE's, as David mentioned. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Defer it to an electrician as these panels are designed to be surface mounted and must have an air gap between the enclosure and the surface on which they are mounted per 312.2
|
|
#7
|
||||
|
||||
|
I understand 312.2 Mike, but what are you basing your observations on?
I see this type of original panel installation several times a week. It's very predominate in the San Fernando Valley where most homes were built in the early fifties or prior. Usually when I see the sub panel installation like this, it's not listed for wet locations, and therefore, placed inside an additional box. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I see this type of installation as being more of a danger than some of the other items mentioned throuhg out this web site and repeated daily on this forum. |
|
#9
|
||||
|
||||
|
Interesting. . .
I'll try and get the listing info from one of these panels if it's available. I'll post it here when/if I do. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#10
|
||||
|
||||
|
Thanks everybody....Nachi is the eyes for the neophyte Home Inspector.
|
|
#11
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
What is the hazard Mike?
|
|
#12
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
312.2 Damp, Wet, or Hazardous (Classified) Locations. (A) Damp and Wet Locations. In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6-mm (¼-in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof. For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations. Exception: Nonmetallic enclosures shall be permitted to be installed without the airspace on a concrete, masonry, tile, or similar surface. 240.32 Damp or Wet Locations. Enclosures for overcurrent devices in damp or wet locations shall comply with 312.2(A). 404.4 Wet Locations. A switch or circuit breaker in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2(A). Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly. 408.37 Panelboards in Damp or Wet Locations. Panelboards in damp or wet locations shall be installed to comply with 312.2(A). As clearly stated if it has overcurrent devices or switches and is in a wet location it must comply with 312.2. The installation in the pictures of the original post does not comply with 312.2. To carry this a little deeper into discussion it could be pointed out that on these type of installations one will find more than one white wire under one screw and lots of times there will not be GFCI protection for receptacles located outside, in baths and kitchens. Although these doubled white wires and lack of GFCI protection will be called out although at the time of installation they were not required but the panel and meter enclosure being install against code is mostly overlooked. From my first day on this forum I have listened to some who make thier inspections based on the UL Srandards outlined for the manufacturing process and some that make their inspections from the UL listing and labeling. I have even listened to some who will argue that by simply changing an electrical motor will make an ornamental pool into a Permanently Installed Swimming pool. Most of these calls could be based totally on the opinion of the person doing the inspection. The installation in the picture can not be based on anyone's opinion as it clearly is a violation of the NEC at least four different times. Does this answer your question? |
|
#13
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Always verify any meter installations with the local utility company specifications. |
|
#14
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
My thought is if there is water behind that stucco in the wall, corrosion of the electrical cabinet is not going to be their biggest problem.
|
|
#15
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
There has been MILLIONS of the double tapped grounded (neutral) conductors installed trough the South, North, East and West that were approved and inspected and are still in use, think double ground! Just because something has pased inspection is no indication that it was done correctly now is it? |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Main panel question, pic included | dnasser | Electrical Inspections | 2 | 7/16/08 7:26 AM |
| Main Panels in Closets | rwashington | Electrical Inspections | 9 | 2/17/07 12:17 AM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |