  #1  
Old 8/1/08, 1:39 AM
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 267
Default Two Main panels? Pic included

The main disconnect was on the little panel and the larger panel
controlled the branch circuits. I need help on writing this configuration up.
I could not read the amperage on the main disconnect. 60 amp ? plz help.

Reply With Quote
  #2  
Old 8/1/08, 7:34 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Two Main panels? Pic included

The cover below the meter should have a municipal lock on it.

As for amperage, I need a closer picture.

The panel on the left appears to have an FPE beaker. Not good.
Reply With Quote
  #3  
Old 8/1/08, 9:15 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Two Main panels? Pic included

Typically, the main is where the service disconnect is and the other is a sub panel. The enclosure on the left looks field modified. I mean, I've never seen wood framing when I opened a panel before. Let an electrician sort it out.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 8/1/08, 11:02 AM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,946
Default Re: Two Main panels? Pic included

Quote:
Originally Posted by dnasser
The main disconnect was on the little panel and the larger panel
controlled the branch circuits. I need help on writing this configuration up.
I could not read the amperage on the main disconnect. 60 amp ? plz help.
I can't tell the amperage from the pic. I'd guess either 60, or more likely 100.

If this is a commercial property, I agree it should have a lock on it.

The panel on the right would be the main, and the panel on the left would be a sub panel.

I'm not sure what is going on with the big outer box, and smaller inner box. That's kind of weird, maybe it was some sort of upgrade at some point in history.
Reply With Quote
  #5  
Old 8/1/08, 12:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Two Main panels? Pic included

There is only one service panel, with a disconnect. The other is a "sub" panel, and should be wired as such.

This is a pretty standard installation for the late '40's and '50's in CA. The original panel (with the meter) did not have enough room for additional circuits and the other panel (on the left) was added for "expansion." No lock is required on the service equipment.

There is nothing wrong with this "setup" (assuming the sub panel has a cover), but it's difficult to tell whether or not they're wired properly.

These are both FPE's, as David mentioned.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 8/1/08, 1:27 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Main panels? Pic included

Defer it to an electrician as these panels are designed to be surface mounted and must have an air gap between the enclosure and the surface on which they are mounted per 312.2
Reply With Quote
  #7  
Old 8/1/08, 1:55 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Two Main panels? Pic included

I understand 312.2 Mike, but what are you basing your observations on?

I see this type of original panel installation several times a week. It's very predominate in the San Fernando Valley where most homes were built in the early fifties or prior.

Usually when I see the sub panel installation like this, it's not listed for wet locations, and therefore, placed inside an additional box.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 8/1/08, 2:02 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Main panels? Pic included

Quote:
Originally Posted by jpope
I understand 312.2 Mike, but what are you basing your observations on?

I see this type of original panel installation several times a week. It's very predominate in the San Fernando Valley where most homes were built in the early fifties or prior.

Usually when I see the sub panel installation like this, it's not listed for wet locations, and therefore, placed inside an additional box.
The meter main combo is surface mounted equipment and the installation is in violation of both the NEC and the manufacturer's installation instructions.

I see this type of installation as being more of a danger than some of the other items mentioned throuhg out this web site and repeated daily on this forum.
Reply With Quote
  #9  
Old 8/1/08, 2:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Two Main panels? Pic included

Interesting. . .

I'll try and get the listing info from one of these panels if it's available. I'll post it here when/if I do.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 8/2/08, 12:57 AM
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 267
Default Re: Two Main panels? Pic included

Thanks everybody....Nachi is the eyes for the neophyte Home Inspector.
Reply With Quote
  #11  
Old 8/2/08, 1:35 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Main panels? Pic included

What is the hazard Mike?
Reply With Quote
  #12  
Old 8/2/08, 10:21 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Main panels? Pic included

Quote:
Originally Posted by Greg Fretwell
What is the hazard Mike?
In order to answer this question one is forced to post NEC code.

312.2 Damp, Wet, or Hazardous (Classified) Locations.
(A) Damp and Wet Locations. In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6-mm (¼-in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof. For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations.

Exception: Nonmetallic enclosures shall be permitted to be installed without the airspace on a concrete, masonry, tile, or similar surface.

240.32 Damp or Wet Locations.
Enclosures for overcurrent devices in damp or wet locations shall comply with 312.2(A).

404.4 Wet Locations.
A switch or circuit breaker in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2(A). Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.

408.37 Panelboards in Damp or Wet Locations.
Panelboards in damp or wet locations shall be installed to comply with 312.2(A).

As clearly stated if it has overcurrent devices or switches and is in a wet location it must comply with 312.2. The installation in the pictures of the original post does not comply with 312.2.

To carry this a little deeper into discussion it could be pointed out that on these type of installations one will find more than one white wire under one screw and lots of times there will not be GFCI protection for receptacles located outside, in baths and kitchens.

Although these doubled white wires and lack of GFCI protection will be called out although at the time of installation they were not required but the panel and meter enclosure being install against code is mostly overlooked.

From my first day on this forum I have listened to some who make thier inspections based on the UL Srandards outlined for the manufacturing process and some that make their inspections from the UL listing and labeling. I have even listened to some who will argue that by simply changing an electrical motor will make an ornamental pool into a Permanently Installed Swimming pool.

Most of these calls could be based totally on the opinion of the person doing the inspection. The installation in the picture can not be based on anyone's opinion as it clearly is a violation of the NEC at least four different times.

Does this answer your question?
Reply With Quote
  #13  
Old 8/2/08, 11:20 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Arrow Re: Two Main panels? Pic included

Quote:
Originally Posted by Greg Fretwell
What is the hazard Mike?
Nothing is wrong with the meter/main installation on the right, there are no hazards, MILLIONS of these have been installed throughout the South West, etc., approved and inspected, and are in still use, think SEMI-FLUSH!

Always verify any meter installations with the local utility company specifications.





Reply With Quote
  #14  
Old 8/2/08, 12:36 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Main panels? Pic included

My thought is if there is water behind that stucco in the wall, corrosion of the electrical cabinet is not going to be their biggest problem.
Reply With Quote
  #15  
Old 8/2/08, 5:15 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Main panels? Pic included

Quote:
Originally Posted by jtedesco1
Nothing is wrong with the meter/main installation on the right, there are no hazards, MILLIONS of these have been installed throughout the South West, etc., approved and inspected, and are in still use, think SEMI-FLUSH!

Always verify any meter installations with the local utility company specifications.
Now Joe you know that that installation is in violation of UL Standard 67 as well as the above mentioned code articles.

There has been MILLIONS of the double tapped grounded (neutral) conductors installed trough the South, North, East and West that were approved and inspected and are still in use, think double ground!

Just because something has pased inspection is no indication that it was done correctly now is it?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main panel question, pic included dnasser Electrical 2 7/16/08 7:26 AM
Main Panels in Closets rwashington Electrical 9 2/17/07 12:17 AM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 3:25 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts