Default Two meters three services......

Owner of home works for power company......I was going to call out a remote panel (garage) for not isolating the grounds and neutrals. He said this is another service. He is correct as there is no feed from the other two services to the garage. Can you feed multiple services from a single meter?
Thanks
Reply With Quote
Find an InterNACHI certified Kentucky Home Inspector (and anywhere else in North America)
  #2  
Old 7/28/09, 7:27 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Two meters three services......

I see large houses all of the time with 2-3 main panels off of a meter and common gutter. Pretty much any house that needs more than 200amps down here.

Had one house with a 1000amp service, but it was a commercial type feed/panel.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #3  
Old 7/28/09, 7:40 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Two meters three services......

As long as the service is being metered, I don't see an issue.
Reply With Quote
  #4  
Old 7/28/09, 7:41 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Two meters three services......

Quote:
Originally Posted by cevans View Post

Had one house with a 1000amp service, but it was a commercial type feed/panel.
1000 Amps...WTF. Never in my lifetime.
Reply With Quote
  #5  
Old 7/28/09, 8:03 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Two meters three services......

Well, that of course is an unknown......I hope that it runs through the meter.....but he does work for the power company
Reply With Quote
  #6  
Old 7/28/09, 11:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Two meters three services......

I'd have to see it, but it sounds wrong to me. Were the "services" bonded somehow?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 7/28/09, 11:55 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Two meters three services......

Two of the three service panels did not have a bonding strap from the neutral buss bars to panel. All three panels were supposed to be grounded to two eight ft grounding rods at the meter face.
Reply With Quote
  #8  
Old 7/29/09, 6:23 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Two meters three services......

I'm having difficulty visualizing this, but everything about it sounds wrong.

You can't have more than one service to a residence (exceptions do apply), the disconnect(s) should be in one location and the panels/components must be bonded (interconnected to each other through a conductor or metallic path).

How far from the meter(s) are the panels?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 7/29/09, 11:24 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Two meters three services......

Two of the services are in the basement with the meter sockets directly on the exterior wall ( one is an off peak meter controlled by the power company). A third service in the garage, is tapped off one of the meter sockets at the house. The main house service is grounded to a rod. The off peak ground could not be established 3-wire SEC no grounded conductor visible. The third garage, service, the owner claimed was grounded to the rod at the house?????? I deferred it to a licensed electrical contractor with numerous other difficencies.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Orange County Home Inspections whandley California Inspectors 12 5/18/11 6:35 AM


All times are GMT -4. The time now is 5:00 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts