Default Two panels or one

Ok guys here is another puzzle from today's inspect would you say by looking at the IR image that it is the same panel as the digital image yes or no please?????
Attached Thumbnails
two-panels-one-1302-w-wabash-enid-7-11-11-046.jpg   two-panels-one-1302-w-wabash-enid-7-11-11-107.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/11/11, 8:36 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two panels or one

Looks to be the same to me except the IR photo seems to be shooting upward more so than the first image.
Reply With Quote
  #3  
Old 7/11/11, 8:39 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Two panels or one

I'm seeing a second image of something in the IR photo going to the right lug. I think it's two similar units.

But what do I know???...I'm too old for this.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #4  
Old 7/11/11, 8:49 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Two panels or one

Quote:
Originally Posted by jwilliams4 View Post
I'm seeing a second image of something in the IR photo going to the right lug. I think it's two similar units.

But what do I know???...I'm too old for this.
Well for an old fart your eyes are pretty good sure appears to me in the IR image there is two somethings on the right lug



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 7/11/11, 8:51 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Two panels or one

Quote:
Originally Posted by Robert Meier View Post
Looks to be the same to me except the IR photo seems to be shooting upward more so than the first image.
Hi Robert I am taking your post as a vote yes same panel



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 7/11/11, 8:55 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two panels or one

Looking at the angle of the separation between the two hot feeder conductors IMO they're the same panel. The likelihood that the same angle between two conductors in two different panels seems unlikely.
Reply With Quote
  #7  
Old 7/11/11, 9:00 PM
Jeffrey Moore Jeffrey Moore is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Mesa, AZ
Posts: 282
Default Re: Two panels or one

Charley I know you are older than I am but why are you taking measurements of an acute specular anomaly?














PS I like the one you had posted before of the reflections



Jeff Moore
www.quantumhomeinspections.com
Flir (ITC) Level II Thermographer
Mesa, AZ
Reply With Quote
  #8  
Old 7/11/11, 9:05 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Two panels or one

Quote:
Originally Posted by jmoore5 View Post
Charley I know you are older than I am but why are you taking measurements of an acute specular anomaly?
PS I like the one you had posted before of the reflections
Just for fun SHHHHHHHH



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 7/11/11, 9:11 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Two panels or one

Quote:
Originally Posted by Robert Meier View Post
Looking at the angle of the separation between the two hot feeder conductors IMO they're the same panel. The likelihood that the same angle between two conductors in two different panels seems unlikely.
For a Yankee your pretty sharp, Ya know of all of the panels I have looked at I don't thing any two had the very same pattern on the incoming conductors.

PS I Sneaked into NJ a couple of week ago went to MT Laural and Vineland



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 7/11/11, 9:22 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Two panels or one

Quote:
Originally Posted by cbottger View Post
appears to me in the IR image there is two somethings on the right lug
The "two somethings" include a conductor and a reflection, no?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 7/11/11, 9:31 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Two panels or one

Quote:
Originally Posted by jpope View Post
The "two somethings" include a conductor and a reflection, no?
Well this one did not get very far I must admit it is a reflection and depending on how I stood in relation to the panel I could create two reflections one on each conductor.

The only reason I posted this image was to show how easy it is to mix panels when shooting multiple panels not always easy to tell by just looking at the images the next day or two later. One has to get his numbering system documented correctly



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 7/11/11, 9:50 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two panels or one

Quote:
Originally Posted by cbottger View Post
For a Yankee your pretty sharp, Ya know of all of the panels I have looked at I don't thing any two had the very same pattern on the incoming conductors.

PS I Sneaked into NJ a couple of week ago went to MT Laural and Vineland

IMO the conductor shape gave it away.

SO you visited NJ, quite a ways from home.
Reply With Quote
  #13  
Old 7/11/11, 10:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Two panels or one

Quote:
Originally Posted by cbottger View Post
Well this one did not get very far
Didn't mean to spoil yer fun



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/11/11, 11:29 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Two panels or one

Quote:
Originally Posted by Robert Meier View Post
IMO the conductor shape gave it away.

SO you visited NJ, quite a ways from home.
Yes I got some CE while there and visited wife's relatives I must say I have never liked driving in your State the roads are crazy no pattern they just build a road from point A to B with no rhyme or reason this State is set up on square miles easy to get around



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #15  
Old 7/11/11, 11:32 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Two panels or one

Quote:
Originally Posted by jpope View Post
Didn't mean to spoil yer fun
No never mind was tired for games anyway an old historical two story with full basement today



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
SEC and panels also CEU course material dhostetter Electrical Inspections 3 10/3/08 5:49 PM
Distribution panels bking Electrical Inspections 2 3/11/07 10:29 AM
FPE Panel - Do you open them up? menser Electrical Inspections 11 2/7/06 6:31 PM


All times are GMT -4. The time now is 7:18 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts