I've only been inspecting a short while and today I did my first house with two prong outlets.
This is probably a dumb question but, what do you do? My three prong tester wouldn't go into the three prong outlets. How do I know they were even working?
Reply With Quote
  #2  
Old 4/6/07, 5:53 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Two Prong Outlets

May I suggest a cheater plug or a test light?
Reply With Quote
  #3  
Old 4/6/07, 5:59 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Two Prong Outlets

Pick up one of the grounding adapters for a dollar. Just verify that is a polarized one. (The hot prong will be smaller than the neutral prong) The tester you are probably using should only show an open ground when using the 3 prong adapter. That will indicate correct polarity.
Reply With Quote
  #4  
Old 4/6/07, 9:45 PM
Yuri Olhovsky's Avatar
Yuri Olhovsky Yuri Olhovsky is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Richmond Hill, ON
Posts: 432
Default Re: Two Prong Outlets

Quote:
Originally Posted by jallingham
I've only been inspecting a short while and today I did my first house with two prong outlets.
This is probably a dumb question but, what do you do? My three prong tester wouldn't go into the three prong outlets. How do I know they were even working?
John, you can check if the receptacle is operable by using volt stick or voltmeter. Regardless, since two prone receptacles are ungrounded you should recommend upgrade to grounded ones (at least those that will be used for computers) or GFCIs as a bare minimum.



Yuri Olhovsky CMI, CEA, PHPI, RASDT
National Home Inspector NHICC #00372
Richmond Hill, ON Canada
NACHI ID 04070207
Reply With Quote
  #5  
Old 4/7/07, 7:53 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Two Prong Outlets

Plain ole' Ticker will work....you can verify it is working, you can determine if it has proper polarity and it will only cost you about $ 15.00-$20.00 bucks.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 4/7/07, 9:24 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Prong Outlets

Quote:
Originally Posted by pabernathy
Plain ole' Ticker will work....you can verify it is working, you can determine if it has proper polarity and it will only cost you about $ 15.00-$20.00 bucks.
That'll let you know if it's got a hot wire, but it won't let you know if the rec is functional (open neutral). I'd rather test for polarity with a TIC tracer and plug a test lamp in to verify functionality, if a functional test is what is intended.
Reply With Quote
  #7  
Old 4/7/07, 10:33 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Prong Outlets

If it is an old receptacle, predating the 3 prongers both holes will probably be the same size so how will you determine polarity? It may just be installed upside down
Reply With Quote
  #8  
Old 4/7/07, 11:03 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Two Prong Outlets

Don't forget to note the ones that have lost their tension. Most will be bad in an older home to the point of plugs falling out easily.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #9  
Old 4/8/07, 12:44 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Two Prong Outlets

Correct me if I am incorrect, but Yuri's statement regarding a 2 prong being ungrounded is innacurate.

If the system is grounded, and the ground is extended to the box, and the receptacle is mechanically bonded to the box, then the receptacle is "grounded", no?

My thoughts are that the difference between a 2 and 3 prong is that they are both technically grounded, but the 3-prong allows the system ground to extend to the applicance it connects to, if a ground plug is required.

Cheater plugs should have the green wirre, or green metallic thingie, securely fastened via center screw on the receptacle cover, otherwise using them is a no no.

So, assuming the system is indeed "grounded", am I right or wrong here?
Reply With Quote
  #10  
Old 4/8/07, 1:01 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Two Prong Outlets

Quote:
Originally Posted by jfarsetta

Correct me if I am incorrect, ...

....am I right or wrong here?
I will disagree merely to draw a response as my curiosity runs concurrent with yours.




Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #11  
Old 4/8/07, 1:02 AM
Yuri Olhovsky's Avatar
Yuri Olhovsky Yuri Olhovsky is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Richmond Hill, ON
Posts: 432
Default Re: Two Prong Outlets

Joe, old houses that have two prong receptacles most likely were wired with old cloth-covered wiring that did not contain ground wire. How could the outlets be grounded?



Yuri Olhovsky CMI, CEA, PHPI, RASDT
National Home Inspector NHICC #00372
Richmond Hill, ON Canada
NACHI ID 04070207
Reply With Quote
  #12  
Old 4/8/07, 1:04 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Two Prong Outlets

Yuri,

1930-40 Homes wired with BX are quite common.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #13  
Old 4/8/07, 1:08 AM
Yuri Olhovsky's Avatar
Yuri Olhovsky Yuri Olhovsky is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Richmond Hill, ON
Posts: 432
Default Re: Two Prong Outlets

Joe, I agree with BX, but this is expensive and was not so common here. Anyway, two prong receptacles are outdated to comply with "modern days requirements"



Yuri Olhovsky CMI, CEA, PHPI, RASDT
National Home Inspector NHICC #00372
Richmond Hill, ON Canada
NACHI ID 04070207
Reply With Quote
  #14  
Old 4/8/07, 1:15 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Two Prong Outlets

Quote:
Originally Posted by yolhovsky
Joe, I agree with BX, but this is expensive and was not so common here. Anyway, two prong receptacles are outdated to comply with "modern days requirements"
Geographic differences noted.

While BX may not have been commonplace in your area, BX was quite common in this area.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #15  
Old 4/8/07, 2:30 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Two Prong Outlets

Yuri,

If the receptacle is not damaged, and the system is indeed grounded (easy to determine when the dead front cover is removed), and the 2-prong is grounded, then what is the problem? Is the receptacle defective, or not?

Also, what does "outdated by today's requirements" mean? I submit that a majority of today's plug-in electrical devices do not require a system ground (except for vacuums, cleaning machines, some other motor-driven appliances, etc). Some double-wound electric motors no longer require it, either. I'm not poo-pooing the idea, by the way. I'm going back to the initial question and Yuri's statement.

As to any assumption whether a ground conductor is present in the branch distribution cable, this is the reason the dead front cover is removed. As I stated, we'll assume that the distribution system is grounded. That was what my comment was directed at. There are some clowns who take a cable, absent of grond conductor, and bootleg the neutral. Just because it has a "grounding" receptacle doesnt mean it's correctly wired.

Now, (again) the original question went to testing. If you have a cheater plug (which is not a way to cheat, really, but a way to extend the system ground to a device that requires it), then a wiring tester is adequate. I touch the green wite to the center screw on the receptacle cover...

I'll bet that some of these original systems and receptacles are sometimes safer then when Harry The Homeowner strikes.

Last edited by jfarsetta; 4/8/07 at 2:43 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Properly Testing GFCI Outlets tchristopher Electrical Inspections 17 3/17/07 12:19 PM
2 prong and 3 prong? gbrasseur Electrical Inspections 4 3/2/07 5:50 PM
Two Prong Outlets sboyd2 Electrical Inspections 79 9/4/06 8:05 PM
Two prong outlets and GFCI's crichiii Electrical Inspections 8 3/15/06 11:41 PM