Default Two prong receptacles.

I have been inspecting many older homes recently that have two prong receptacles throughout most of the home. I have been recommending upgrading. I was curious if other inspectors are letting this go.

What is your opinion?
Reply With Quote
  #2  
Old 6/25/08, 6:35 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Two prong receptacles.

Definatly recomment upgrading. Ungrounded Outlets do not meet modern safety standards. GFCI's will work with no ground, but I wouldnt try it. The wiring must be 40 or so years old... probably time anyway. If the client chooses to NOT upgrade, you have your butt covered.
Reply With Quote
  #3  
Old 6/25/08, 7:07 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two prong receptacles.

Quote:
Originally Posted by mroberson
GFCI's will work with no ground, but I wouldnt try it.
Why not?
Reply With Quote
  #4  
Old 6/25/08, 7:14 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Two prong receptacles.

Please advise what the "significant deficiency" of a 2 prong outlet is?

Having a 3 prong on a two wire circuit IS an issue, but why would I want to upgrade my entire electrical system?

There are only one or two appliances I own that have a 3 prong plug (computer). What is your point?

This is not me talking, it is what you will be asked by Client, Agent, Electrician.

What is your reply?

Are you saying we must "upgrade" old homes to today's standard?

Does the SOP or your State Law require this reporting?
Do you have any earthly Idea what it takes to re-wire a house ("it about time anyway") ?
Reply With Quote
  #5  
Old 6/25/08, 8:49 AM
Mike W. Cole Mike W. Cole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Hickory, NC
Posts: 65
Default Re: Two prong receptacles.

When ever we see ungrounded three prong outlets we will recommend that they be changed to two prong or marked 'grounded'.
Were all homes built 40 years ago or more not safe? From our standpoint we are very carefull about using terms such as 'must' or 'significant upgrade' in any verbal or written communication with our clients. The attorneys love it, the realtors hate it and most of our clients don't care!
Reply With Quote
  #6  
Old 6/25/08, 8:57 AM
bemelander bemelander is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Grand Rapids, MI
Posts: 341
Default Re: Two prong receptacles.

I would not recomend an upgrade for two prong outlets in general. I would recommend if I felt it was a safety issue, (kitchen, baths, basements, etc).
i would also recommend changes to standard 3-prong outlets on a two wire system.

Bill



Bill Emelander
Professional Edge Home Inspection
Grand Rapids and all of West Michigan
NACHI #03111914
www.proedgehi.com
Reply With Quote
  #7  
Old 6/25/08, 10:11 AM
Vince Santos's Avatar
Vince Santos Vince Santos is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Canton, MI - Serving Souteast Michigan
Posts: 1,786
Default Re: Two prong receptacles.

If I'm inspecting a home with two prong receptacles I mention in the report how some appliances do require a three prong receptacle but I would never recommend a system upgrade based on the presence of two prong.

If I come across open ground three prong receptacles I would recommend they replace the receptacle with a two prong.

It's not about covering your butt it's about providing your client with valid, relevant, professional advice.



Vince Santos
StepByStep Home Services LC
(734) 748-9584
Providing Home Inspection Services to Southeast Michigan
facebook
ITA Trained and Certified

Reply With Quote
  #8  
Old 6/25/08, 10:14 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Two prong receptacles.

Quote:
Originally Posted by vsantos
If I come across open ground three prong receptacles I would recommend they replace the receptacle with a two prong.
Other options available:

406.3(D) Replacements Replacement of receptacles shall comply with 406.3(D)(1), (D)(2), and (D)(3) as applicable.

(1) Grounding-Type Receptacles Where a grounding means exists in the receptacle enclosure or a grounding conductor is installed in accordance with 250.130(C), grounding-type receptacles shall be used and shall be connected to the grounding conductor in accordance with 406.3(C) or 250.130(C).

(2) Ground-Fault Circuit Interrupters Ground-fault circuit-interrupter protected receptacles shall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this Code.

(3) Non–grounding-Type Receptacles Where grounding means does not exist in the receptacle enclosure, the installation shall comply with (D)(3)(a), (D)(3)(b), or (D)(3)(c).

(a) A non–grounding-type receptacle(s) shall be permitted to be replaced with another non–grounding-type receptacle(s).

(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked ``No Equipment Ground.'' An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.

(c) A non–grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked ``GFCI Protected'' and ``No Equipment Ground.'' An equipment grounding conductor shall not be connected between the grounding-type receptacles.




InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 6/25/08, 10:23 AM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two prong receptacles.

Quote:
Originally Posted by lkage
(a) A non–grounding-type receptacle(s) shall be permitted to be replaced with another non–grounding-type receptacle(s).
NEC says 2-prong receptacles are OK in an existing system.

Make sure you check for reverse polarity though.
Reply With Quote
  #10  
Old 6/25/08, 1:04 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Two prong receptacles.

Quote:
It's not about covering your butt it's about providing your client with valid, relevant, professional advice.
Amen!

I do advise client that when they have a 3 prong plug appliance, do not shortcut and add an adapter which may not ground the appliance. If they need a grounded receptacle, it should be checked and professionally installed.
Reply With Quote
  #11  
Old 6/25/08, 4:38 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two prong receptacles.

Quote:
Originally Posted by vsantos
If I'm inspecting a home with two prong receptacles I mention in the report how some appliances do require a three prong receptacle but I would never recommend a system upgrade based on the presence of two prong.

If I come across open ground three prong receptacles I would recommend they replace the receptacle with a two prong.

It's not about covering your butt it's about providing your client with valid, relevant, professional advice.
VERY well said.
Reply With Quote
  #12  
Old 6/25/08, 4:52 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Two prong receptacles.

Let me clarify my previous statement. I recommend upgraging to GFCI's. If they are 2 prong, They obviously arnt.
Reply With Quote
  #13  
Old 6/25/08, 5:33 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Two prong receptacles.

[quote=vsantos]\. It's not about covering your butt it's about providing your client with valid, relevant, professional advice.[/quote]

Actually, valid, relevant, professional advice is covering your butt.

Education is the absolute best way...



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #14  
Old 6/25/08, 10:12 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Two prong receptacles.

You need to cover your butt, but you do not have to document it where it is so obvious. Every report section you don't understand.
Reply With Quote
  #15  
Old 6/25/08, 10:48 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: Two prong receptacles.

Quote:
Originally Posted by dryerson
I have been inspecting many older homes recently that have two prong receptacles throughout most of the home. I have been recommending upgrading. I was curious if other inspectors are letting this go.

What is your opinion?
I educate the client about the "old" home and systems in it they are purchasing.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
3 prong receptacle w/out equipment ground wire mbrown5 Electrical Inspections 4 8/24/07 1:55 AM
2 prong and 3 prong? gbrasseur Electrical Inspections 4 3/2/07 4:50 PM
2 Prong Receptacles dnasser Electrical Inspections 5 2/26/07 11:24 AM
open ground on 3 garage receptacles dnasser Electrical Inspections 14 10/30/06 5:53 PM
Two prong outlets and GFCI's crichiii Electrical Inspections 8 3/15/06 10:41 PM


All times are GMT -4. The time now is 7:20 AM.