Default Two Quick Questions On Receptacles

I have two quick electrical questions. On the first picture, what are the spacing requirements for receptacles at counter top level? On the second picture; should these receptacles be GFCI protected? They are in a laundry room, but not on a counter top with the sink. It is a galley style laundry room with the laundry sink on one side and work space on the other.



Thanks
Russell Train
Attached Thumbnails
two-quick-questions-receptacles-img_0024b.jpg   two-quick-questions-receptacles-img_0016jh.jpg  
Reply With Quote
  #2  
Old 11/27/07, 1:27 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 746
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Quick Questions On Receptacles

If this were a kitchen a new install would require that no wall space was more than 2' from a receptacle, ie 4' spacing. Also any countertop 12" wide or more would require a receptacle. There are other rules regarding islands and penisulas.

A new laundry room would require GFI protection for receptacles within 6' of the laundry tub. It would also require a circuit dedicated to just the laundry room receptacles. This would include the receptacle for the washer if within the 6'.

What year was the house built? Is this a kitchen or a wet bar?
Reply With Quote
  #3  
Old 11/27/07, 1:33 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Quick Questions On Receptacles

Here is a quick link from 2005 NEC on that area.
http://www.ul.com/regulators/ode/0105.pdf
Reply With Quote
  #4  
Old 11/27/07, 1:36 PM
rtrain's Avatar
rtrain rtrain is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Las Vegas, NV
Posts: 60
Default Re: Two Quick Questions On Receptacles

Its new construction and it's a wet bar.
Reply With Quote
  #5  
Old 11/27/07, 1:56 PM
rtrain's Avatar
rtrain rtrain is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Las Vegas, NV
Posts: 60
Default Re: Two Quick Questions On Receptacles

Ok. So what I can gather is… on the counter top of the wet bar you would only need one receptacle, because it’s not a food prep. area , but the counter top is more the 12” wide so it requires at least one receptacle (the outlet shown is GFCI protected). For the laundry room those receptacles would need GFCI protection because they are within 6 feet of the washer (even though the washer is front loading and under the counter top)? Thanks for your help guys.

Russell
Reply With Quote
  #6  
Old 11/27/07, 4:36 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Quick Questions On Receptacles

The laundry does NOT need to be GFCI. The 2005 rule is 6' from the sink, not the washer.
Reply With Quote
  #7  
Old 11/28/07, 12:10 AM
rtrain's Avatar
rtrain rtrain is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Las Vegas, NV
Posts: 60
Default Re: Two Quick Questions On Receptacles

Thanks Greg
Reply With Quote
  #8  
Old 11/28/07, 12:24 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Quick Questions On Receptacles

See below:
Attached Thumbnails
two-quick-questions-receptacles-elect-gfci-utillty-laundry.jpg  
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Receptacles not having acceptable blade retention jtedesco1 Electrical Inspections 12 1/28/12 9:40 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
open ground on 3 garage receptacles dnasser Electrical Inspections 14 10/30/06 6:53 PM
Some good questions that always need answers jtedesco1 Electrical Inspections 5 6/16/06 10:10 PM