Need some input. Yesterdays inspection - One meter with two service panels. Both were 150 amp with their own breakers. One is on the exterior wall and one is inside in the hall. Wire coming from the meter is #1 copper wire. It is bugged in the outside panel and runs to each panel box. Are the wires large enough to handle this and is it compliant.
|
| Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Did each panel have a it's own service disconnect? If so they need to be grouped at one location. And yes the #1 AWG might be too small for both 150 amp panels. Do you have any photo's?
Last edited by Robert Meier; 11/29/10 at 5:08 AM.. Reason: Spelling/wording correction |
|
#3
|
||||
|
||||
|
Quote:
BestInspectors.Net
& Real Estate Training Academy Inspection Report Software for Windows - iOS - Mac - Android Continuing Education Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921 http://www.bestinspectors.net est. 1992 |
|
#4
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I have a photo but cannot figure out how to upload it. No longer being a member, it does not give me that option. |
|
#5
|
||||
|
||||
|
Maybe its time to be a member again.
Now you see the resources. May I ask you why you left? If you do not answer, that is OK , I will totally understand your privacy. Good luck with your question. I have to get back to electrical chapter and review before I go out. montrealbuildinginspectionservice.com montreal-home-inspection-services.com home-inspections-montreal.com homeinspectionsservicesmontreal.com ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC. Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI) OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816 |
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| PLEASE HELP! Need to change the SOPs, per NEMA | ktarasenko | Electrical Inspections | 76 | 4/19/10 8:15 PM |
| New article on electrical service panels | inxil | InterNACHI & RealMatcher Blogs | 0 | 1/8/10 7:00 PM |
| New Washington Legislation Submitted | gdomagala | Legislation, Licensing & Legal Issues for Inspectors | 294 | 2/10/08 1:20 AM |
| Service Equipment Grounding | mthomas2 | Electrical Inspections | 2 | 11/29/06 12:30 AM |