Default Two wire circuit

If a GFCI is added to a two wire circuit, will the GFCI trip if there is a fault on another receptacle on that circuit?
Reply With Quote
  #2  
Old 8/16/08, 3:06 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: Two wire circuit

Quote:
Originally Posted by dduffy
If a GFCI is added to a two wire circuit, will the GFCI trip if there is a fault on another receptacle on that circuit?
If it's wired properly and the fault is downsteam of the GFCI it will.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #3  
Old 8/16/08, 9:41 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Two wire circuit

Quote:
Originally Posted by dduffy
If a GFCI is added to a two wire circuit, will the GFCI trip if there is a fault on another receptacle on that circuit?
Absolutely. The ground is irrelevant for GFCI operation.

But your 3 lite tester won't work in any downstream outlets that are 3 wire becaue the tester requires a ground to function.

hth



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #4  
Old 8/16/08, 9:58 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 4,403
Default Re: Two wire circuit

and as stated above it must be wired for downstream protection..not all are



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #5  
Old 8/16/08, 10:01 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Two wire circuit

Quote:
Originally Posted by jmckee
and as stated above it must be wired for downstream protection..not all are
Not sure what you mean James but as long as the downstream outlets are wired to the load side of the GFCI all should be fine.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #6  
Old 8/16/08, 10:06 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 4,403
Default Re: Two wire circuit

Quote:
Originally Posted by mlarson
Not sure what you mean James but as long as the downstream outlets are wired to the load side of the GFCI all should be fine.
thanks exactly what I meant ...I've seen them all wired to the line side for single outlet protection...the downstream outlets must be wired to the load side for protection...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #7  
Old 8/16/08, 1:28 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,697
Default Re: Two wire circuit

Quote:
Originally Posted by mlarson
Not sure what you mean James but as long as the downstream outlets are wired to the load side of the GFCI all should be fine.
That is was I meant, a electrician was telling one of my customers who has a two wire system she needed GFCI's installed at all the receptacles to protect them all at a cost of $89.00 per receptacle. She probably could have gotten the entire house rewired at that cost per receptacle to just install GFCI's.

I told her yesterday the guy was trying to rip her off, but I wanted to make sure I wasn't loosing my mind.

Thanks
Reply With Quote
  #8  
Old 8/16/08, 1:32 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 4,403
Default Re: Two wire circuit

Quote:
Originally Posted by dduffy
That is was I meant, a electrician was telling one of my customers who has a two wire system she needed GFCI's installed at all the receptacles to protect them all at a cost of $89.00 per receptacle. She probably could have gotten the entire house rewired at that cost per receptacle to just install GFCI's.

I told her yesterday the guy was trying to rip her off, but I wanted to make sure I wasn't loosing my mind.

Thanks
I think You did your customer a good service Dale ....as far as your mind goes well...that could be another thread altogether.....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #9  
Old 8/16/08, 3:29 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two wire circuit

Quote:
Originally Posted by dduffy
That is was I meant, a electrician was telling one of my customers who has a two wire system she needed GFCI's installed at all the receptacles to protect them all at a cost of $89.00 per receptacle....

I told her yesterday the guy was trying to rip her off, but I wanted to make sure I wasn't loosing my mind.
WAIT!!!

Tread very carefully, Dale.

There have been many instances were in order to GFCI protect an existing 2-wire circuit with a GFCI receptacle, I had to put a GFCI at each and every receptacle location. With K&T, in particular, each receptacle is tapped off the main run of K&T. No conductors exist at any receptacle location that "feed through" to the next one in the chain. Indeed, there were installers back in the day that favored this wiring methodology for 2-wire romex also. They'd run the wire into the lighting box, and drop a single romex down to each receptacle. There's no single place to put a GFCI in such an installation to protect everything downstream. Nothing's downstream in certain wiring arrangements; all the receptacles are essentially dead end spurs.
Reply With Quote
  #10  
Old 8/16/08, 3:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Two wire circuit

When you have an original two-wire system that needs this type of upgrade, it's usually easier, and less expensive to install GFCI breakers for the branch circuit(s) at the panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 8/16/08, 3:31 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Two wire circuit

Quote:
Originally Posted by jpope
When you have an original two-wire system that needs this type of upgrade it's usually easier, and cheaper to install GFCI breakers for the branch circuit(s) at the panel.
Yah, but in the land of basements resetting them is a pain.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #12  
Old 8/16/08, 3:32 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two wire circuit

Quote:
Originally Posted by jpope
When you have an original two-wire system that needs this type of upgrade, it's usually easier, and less expensive to install GFCI breakers for the branch circuit(s) at the panel.
This is true, but if the main goal is enhanced ground fault safety, and a fusepanel exists, the requisite service upgrade/panel change required might often exceed the cost of GFCI receptacles in the right places.
Reply With Quote
  #13  
Old 8/16/08, 3:40 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,697
Default Re: Two wire circuit

Quote:
Originally Posted by Marc D. Shunk
WAIT!!!

Tread very carefully, Dale.

There have been many instances were in order to GFCI protect an existing 2-wire circuit with a GFCI receptacle, I had to put a GFCI at each and every receptacle location. With K&T, in particular, each receptacle is tapped off the main run of K&T. No conductors exist at any receptacle location that "feed through" to the next one in the chain. Indeed, there were installers back in the day that favored this wiring methodology for 2-wire romex also. They'd run the wire into the lighting box, and drop a single romex down to each receptacle. There's no single place to put a GFCI in such an installation to protect everything downstream. Nothing's downstream in certain wiring arrangements; all the receptacles are essentially dead end spurs.
Marc,

I told the lady to get a couple more electricians to give her quotes, she wants to add three prong receptacles, but wanted them protected by means of a GFCI at one of the receptacles, not all of them if it was possible so the circuit is essentially protected if a fault occurred. There was no K&T in the house, just old cloth covered two wire conductors.
Reply With Quote
  #14  
Old 8/16/08, 3:49 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two wire circuit

Quote:
Originally Posted by dduffy
There was no K&T in the house, just old cloth covered two wire conductors.
Right, and quite possibly all the receptacles were dead ends. It was quite popular to feed each receptacle with a drop from the light box in the room, or up from the basement lighting boxes. All I'm trying to say is that it is quite possible the sparky was not trying to rip her off.
Reply With Quote
  #15  
Old 8/16/08, 3:58 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,697
Default Re: Two wire circuit

Quote:
Originally Posted by Marc D. Shunk
Right, and quite possibly all the receptacles were dead ends. It was quite popular to feed each receptacle with a drop from the light box in the room, or up from the basement lighting boxes. All I'm trying to say is that it is quite possible the sparky was not trying to rip her off.
There are no basements in Arizona----

And this house did not have any ceiling lighting except one in the living room and kitchen, the bedrooms didn't even have ceiling lights, built in the 50's I think.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
What's this video worth? jtedesco1 Education 5 4/18/08 10:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 1:35 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM


All times are GMT -4. The time now is 6:59 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts