If a GFCI is added to a two wire circuit, will the GFCI trip if there is a fault on another receptacle on that circuit?
Dale Duffy 602.402.5305 Inspect Arizona Companies, Inc. Phoenix Home Inspectors, Inc. Your Leaking House-- Your Leaking House Message Board InterNACHI 2007 U.S.A Member of the Year |
|
#2
|
|||
|
|||
|
Quote:
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#3
|
||||
|
||||
|
Quote:
But your 3 lite tester won't work in any downstream outlets that are 3 wire becaue the tester requires a ground to function. hth "Never underestimate the difficulty of changing false beliefs by facts." |
|
#4
|
||||
|
||||
|
and as stated above it must be wired for downstream protection..not all are
|
|
#5
|
||||
|
||||
|
Quote:
"Never underestimate the difficulty of changing false beliefs by facts." |
|
#6
|
||||
|
||||
|
Quote:
|
|
#7
|
||||
|
||||
|
Quote:
I told her yesterday the guy was trying to rip her off, but I wanted to make sure I wasn't loosing my mind. Thanks Dale Duffy 602.402.5305 Inspect Arizona Companies, Inc. Phoenix Home Inspectors, Inc. Your Leaking House-- Your Leaking House Message Board InterNACHI 2007 U.S.A Member of the Year |
|
#8
|
||||
|
||||
|
Quote:
|
|
#9
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Tread very carefully, Dale. There have been many instances were in order to GFCI protect an existing 2-wire circuit with a GFCI receptacle, I had to put a GFCI at each and every receptacle location. With K&T, in particular, each receptacle is tapped off the main run of K&T. No conductors exist at any receptacle location that "feed through" to the next one in the chain. Indeed, there were installers back in the day that favored this wiring methodology for 2-wire romex also. They'd run the wire into the lighting box, and drop a single romex down to each receptacle. There's no single place to put a GFCI in such an installation to protect everything downstream. Nothing's downstream in certain wiring arrangements; all the receptacles are essentially dead end spurs. |
|
#10
|
||||
|
||||
|
When you have an original two-wire system that needs this type of upgrade, it's usually easier, and less expensive to install GFCI breakers for the branch circuit(s) at the panel.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#11
|
||||
|
||||
|
Quote:
"Never underestimate the difficulty of changing false beliefs by facts." |
|
#12
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#13
|
||||
|
||||
|
Quote:
I told the lady to get a couple more electricians to give her quotes, she wants to add three prong receptacles, but wanted them protected by means of a GFCI at one of the receptacles, not all of them if it was possible so the circuit is essentially protected if a fault occurred. There was no K&T in the house, just old cloth covered two wire conductors. Dale Duffy 602.402.5305 Inspect Arizona Companies, Inc. Phoenix Home Inspectors, Inc. Your Leaking House-- Your Leaking House Message Board InterNACHI 2007 U.S.A Member of the Year |
|
#14
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#15
|
||||
|
||||
|
Quote:
And this house did not have any ceiling lighting except one in the living room and kitchen, the bedrooms didn't even have ceiling lights, built in the 50's I think. Dale Duffy 602.402.5305 Inspect Arizona Companies, Inc. Phoenix Home Inspectors, Inc. Your Leaking House-- Your Leaking House Message Board InterNACHI 2007 U.S.A Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| What's this video worth? | jtedesco1 | Education | 5 | 4/18/08 10:24 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical | 0 | 7/2/07 1:35 PM |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical | 0 | 7/7/06 1:24 PM |