Rigid conduit from meter to service disconnect.
Is this pull elbow OK for "buried" use? If not, code cite of possible, please. Thanks. |
|
#2
|
||||
|
||||
|
It looks like an aluminum "LB" as opposed to being a malleble iron type. I wouldn't want either one underground. The aluminum one will corrode very quickly in this application. NEC 300.6 Raceways, cable trays....fittings... shall be of materials suitable for the environment in which they are installed.
|
|
#3
|
|||
|
|||
|
Here's the other side of the meter, BTW:
|
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
That is called an LB fitting. Buried is not the trouble. The fact that the cover is not accessible is trouble.
NEC 314.29 Boxes, Conduit Bodies, and Handhole Enclosures Boxes, conduit bodies, and handhole enclosures shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade.to Be Accessible. |
|
#5
|
||||
|
||||
|
I attended Oakton School in Evanston 40 yrs. ago. Is it still there?
|
|
#6
|
||||
|
||||
|
Won't it be accessible when the fitting completely corrodes away in the next couple of years?
|
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#8
|
||||
|
||||
|
Isn't it prone to galvanic action with the soil which would be different than just being in a wet environment?
|
|
#9
|
|||
|
|||
|
Please Note:
tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Mr. Shunk it looks like you will be an asset to our little community.
Welcome to the show. |
|
#10
|
||||
|
||||
|
If it is okay to bury the LB, how can it ever be accessible?
|
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Even if burial has some deleterious effect on the LB (a topic on which there is some doubt), it is much easier to cite the more direct violation of the cover not being accessible. Either reason might make the installation "wrong". One reason just has more clear text on the matter. Last edited by Marc D. Shunk; 12/31/06 at 8:54 PM.. |
|
#12
|
||||
|
||||
|
But we only do that when we are running a conduit to CHINA.....
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#13
|
|||
|
|||
|
Please Note:
tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
As far as I can remember it is not OK to bury a JB wether it be an LB, LR or a 4 square. I seem to remember that they all must be accesible to qualified personel. I would look it up, but I dont want to.
|
|
#14
|
|||
|
|||
|
Please Note:
tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
It's cool Joe you do not need to post under a different name. |
|
#15
|
|||
|
|||
|
Please Note:
tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
I take it back Mark.
I was just informed that you are NOT Joe Tedescoe, but a close cousin. lol However, I would like to check. Here you go. The primary of a transformer draws 4 amps at 7,200 volts.A reading at the secondary shows 110 amps at 240 volts. What is the efficiantcy of the transformer at this load? Last edited by tallen; 12/31/06 at 9:19 PM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Fire rating | abolt | Structural | 13 | 9/21/07 9:45 PM |
| Surface type panel box | abolt | Electrical | 2 | 9/4/07 11:44 PM |
| Roof type & excessive leaking | dmacy | Exterior | 7 | 9/12/06 1:07 PM |
| Massachusetts Board of Registration of Home Inspectors | jtedesco1 | Legislation, Licensing & Legal Issues | 0 | 2/14/06 4:38 AM |