Default Is this type of elbow OK for "buried" use?

Rigid conduit from meter to service disconnect.

Is this pull elbow OK for "buried" use?

If not, code cite of possible, please.

Thanks.
Attached Thumbnails
type-elbow-ok-buried-use-elect-conda.jpg   type-elbow-ok-buried-use-elect-condb.jpg  
Reply With Quote
  #2  
Old 12/31/06, 8:24 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Is this type of elbow OK for "buried" use?

It looks like an aluminum "LB" as opposed to being a malleble iron type. I wouldn't want either one underground. The aluminum one will corrode very quickly in this application. NEC 300.6 Raceways, cable trays....fittings... shall be of materials suitable for the environment in which they are installed.
Reply With Quote
  #3  
Old 12/31/06, 8:24 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: Is this type of elbow OK for "buried" use?

Here's the other side of the meter, BTW:
Attached Thumbnails
type-elbow-ok-buried-use-elect-serviceconduitc.jpg   type-elbow-ok-buried-use-electserviceconduita.jpg  
Reply With Quote
  #4  
Old 12/31/06, 8:25 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

That is called an LB fitting. Buried is not the trouble. The fact that the cover is not accessible is trouble.





NEC 314.29 Boxes, Conduit Bodies, and Handhole Enclosures
to Be Accessible.
Boxes, conduit bodies, and handhole enclosures shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade.
Reply With Quote
  #5  
Old 12/31/06, 8:25 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Is this type of elbow OK for "buried" use?

I attended Oakton School in Evanston 40 yrs. ago. Is it still there?
Reply With Quote
  #6  
Old 12/31/06, 8:31 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Is this type of elbow OK for "buried" use?

Won't it be accessible when the fitting completely corrodes away in the next couple of years?
Reply With Quote
  #7  
Old 12/31/06, 8:40 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

Quote:
Originally Posted by rromoser
Won't it be accessible when the fitting completely corrodes away in the next couple of years?
. http://database.ul.com/cgi-bin/XYV/t...693&sequence=1
Reply With Quote
  #8  
Old 12/31/06, 8:45 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Is this type of elbow OK for "buried" use?

Isn't it prone to galvanic action with the soil which would be different than just being in a wet environment?
Reply With Quote
  #9  
Old 12/31/06, 8:45 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

Mr. Shunk it looks like you will be an asset to our little community.

Welcome to the show.
Reply With Quote
  #10  
Old 12/31/06, 8:48 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Is this type of elbow OK for "buried" use?

If it is okay to bury the LB, how can it ever be accessible?
Reply With Quote
  #11  
Old 12/31/06, 8:50 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

Quote:
Originally Posted by rromoser
If it is okay to bury the LB, how can it ever be accessible?
If it was pointed downwards, cover facing up (for instance).

Even if burial has some deleterious effect on the LB (a topic on which there is some doubt), it is much easier to cite the more direct violation of the cover not being accessible. Either reason might make the installation "wrong". One reason just has more clear text on the matter.

Last edited by Marc D. Shunk; 12/31/06 at 8:54 PM..
Reply With Quote
  #12  
Old 12/31/06, 8:52 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Is this type of elbow OK for "buried" use?

But we only do that when we are running a conduit to CHINA.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 12/31/06, 8:57 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

As far as I can remember it is not OK to bury a JB wether it be an LB, LR or a 4 square. I seem to remember that they all must be accesible to qualified personel. I would look it up, but I dont want to.
Reply With Quote
  #14  
Old 12/31/06, 9:01 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

Quote:
Originally Posted by Marc D. Shunk
If it was pointed downwards, cover facing up (for instance).

Even if burial has some deleterious effect on the LB (a topic on which there is some doubt), it is much easier to cite the more direct violation of the cover not being accessible. Either reason might make the installation "wrong". One reason just has more clear text on the matter.
Hmmm, me smells a Joe Tedescoe. lol

It's cool Joe you do not need to post under a different name.
Reply With Quote
  #15  
Old 12/31/06, 9:12 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

I take it back Mark.

I was just informed that you are NOT Joe Tedescoe, but a close cousin. lol

However, I would like to check.

Here you go.

The primary of a transformer draws 4 amps at 7,200 volts.A reading at the secondary shows 110 amps at 240 volts. What is the efficiantcy of the transformer at this load?

Last edited by tallen; 12/31/06 at 9:19 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fire rating abolt Structural 13 9/21/07 9:45 PM
Surface type panel box abolt Electrical 2 9/4/07 11:44 PM
Roof type & excessive leaking dmacy Exterior 7 9/12/06 1:07 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues 0 2/14/06 4:38 AM


All times are GMT -4. The time now is 9:04 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts