Default Re: Is this type of elbow OK for "buried" use?

Quote:
Originally Posted by mthomas2
Rigid conduit from meter to service disconnect.

Is this pull elbow OK for "buried" use?

If not, code cite of possible, please.

Thanks.

NO it is not.
Reply With Quote
  #17  
Old 12/31/06, 9:24 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

Quote:
Originally Posted by tallen
The primary of a transformer draws 4 amps at 7,200 volts.A reading at the secondary shows 110 amps at 240 volts. What is the efficiantcy of the transformer at this load?
91-2/3%. Let's move on... I'm only here to help where I can.
Reply With Quote
  #18  
Old 12/31/06, 9:29 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,091
Default Re: Is this type of elbow OK for "buried" use?

Close. lol

Efficiency= output 110x 240 26,400
______ = ________ ______ = 91.67%
input 4 x7,200 28,800


Ok, OK I am just having fun.

Please carry on and again welcome to the show.
Reply With Quote
  #19  
Old 12/31/06, 9:31 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,091
Default Re: Is this type of elbow OK for "buried" use?

Hey that did not show up like I typed it. lol
Reply With Quote
  #20  
Old 12/31/06, 9:32 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

Quote:
Originally Posted by tallen
Hey that did not show up like I typed it. lol
To maintain spacing, for math formulas and the like, you need to begin and end your text with {code} and {/code}, except replace the {} with [].
Reply With Quote
  #21  
Old 12/31/06, 9:35 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,918
Default Re: Is this type of elbow OK for "buried" use?

Pardon my ignorance to cite the NEC here, but wouldn't the fact that this question is from Illinois and Maine would have slightly if not more frost issues, mandate an installation to alleviate possible damage to the meter enclosure as shown in one of the pics.?

In any case, I would write this up hard and would explain that any underground service from the meter enclosure be sleeve protected and LB's are not to be buried and should be accessible.
This LB shown does not appear to even be a liquid tite fitting.
What will happen when this thing starts taking in water?

I don't think that quoting fancy UL listings about the product explains the logical installation requirements that should occur in a service entrance to a dwelling.

There are no Engineering Specifications and design requirements that would allow this type of installation on any Commercial jobs that I have done to date.

Isn't there a limited horizontal distance requirement for the main secondary feeders?
Just dose not look right.

JMHO

Marcel



</IMG></IMG>
Reply With Quote
  #22  
Old 12/31/06, 9:36 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

A Conduit Body is what I see and access is always required behind that cover.

Todd, quit busting my chops!
Reply With Quote
  #23  
Old 12/31/06, 9:47 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

Quote:
Originally Posted by mcyr
This LB shown does not appear to even be a liquid tite fitting.
What will happen when this thing starts taking in water?
That LB apears to have threaded hubs, and is rated for a wet location.

Quote:
Originally Posted by mcyr
I don't think that quoting fancy UL listings about the product explains the logical installation requirements that should occur in a service entrance to a dwelling.
True. That link was provided for completeness sake, and technical enlightenment for any that care to read this additional information. I will absolutely concede that the population of folks interested in that additional information might be quite small. The original poster's question was already answered in a direct manner in the posts that proceeded that link. The (perhaps sad) fact remains that the installation is compliant, excpet for the non-exposed LB cover.
Reply With Quote
  #24  
Old 12/31/06, 9:48 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,091
Default Re: Is this type of elbow OK for "buried" use?

Quote:
Originally Posted by jtedesco1
A Conduit Body is what I see and access is always required behind that cover.

Todd, quit busting my chops!


I think I said that.

Aw hell Joe give me a Kiss ....It is New years after all.

I was just razzing you.
Reply With Quote
  #25  
Old 12/31/06, 9:51 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,091
Default Re: Is this type of elbow OK for "buried" use?

If you can open it, it must be accesible to qualified personel. J boxes can not be made inaccesible.
Reply With Quote
  #26  
Old 12/31/06, 10:02 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

WRONG!

Boxes, Conduit Bodies, and Handhole Enclosures to Be Accessible

Boxes, conduit bodies, and handhole enclosures shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade.

Exception: Listed boxes and handhole enclosures shall be permitted where covered by gravel, light aggregate, or noncohesive granulated soil if their location is effectively identified and accessible for excavation.
Reply With Quote
  #27  
Old 12/31/06, 10:07 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

Guess what is type of information is included in between these [ ] brackets?

Come on who's the winner?

Oh, and by the way I don't see any gasket on the LB either!
Reply With Quote
  #28  
Old 12/31/06, 10:07 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this type of elbow OK for "buried" use?

Examples of boxes that can utilize that exception, and have the lid buried under light material, are enclosures such as Quazite boxes:


Last edited by Marc D. Shunk; 1/1/07 at 9:50 AM..
Reply With Quote
  #29  
Old 12/31/06, 10:34 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Is this type of elbow OK for "buried" use?

Most excellent.....great example Marc.......

Todd.....you mean
Code:
OutPut/Input x 100 = Efficiency Percentage



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #30  
Old 12/31/06, 10:34 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Is this type of elbow OK for "buried" use?

Man It is TOO late for Mathmatics fella......lol..heads will start expoding all over the place Todd.....and no we dont need a POLL on it...thehehe..



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 12/31/06 at 10:41 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fire rating abolt Structural Inspections 13 9/21/07 9:45 PM
Surface type panel box abolt Electrical Inspections 2 9/4/07 11:44 PM
Roof type & excessive leaking dmacy Exterior Inspections 7 9/12/06 1:07 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 4:38 AM