I'm more concerned about the plug assembly and lack of GFCI than anything else. Comments?
UF 12-2 cable, going to unknown location. As a special bonus, pic 3 is the masthead leading to the Zinsco panel. |
| Find an InterNACHI certified Nebraska Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Was their a garden pond? I've seen that a couple of times with the cable. I write it up as improper and tell my buyers to unplug until they get it fixed.
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#3
|
||||
|
||||
|
Sunlight and physical damage are concerns for UF cable. As for that plug at the end I don't know if that is allowable. I was under the impression it was to be wired within a junction box only.
From my nice old NEC 1999 Uses permitted 1) Type UF cable shall be permitted for use underground, including direct burial in the earth, as feeder or branch-circuit cable where provided with overcurrent protection of the rated ampacity as required in Section 339-4 339-3 Uses Not permitted. Type UF cable shall not be used in the following: 1) Service-entrance cables - 9) Where exposed to direct rays of the sun, unless identified as sunlight resistant 10) Where subject to physical damage Need the pro's to chime in.. Last edited by pbolliger; 7/15/09 at 9:19 PM.. |
|
#4
|
||||
|
||||
|
No, it's not.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
Eve if it was allowed the plug or rather the receptacle would need the plastic cover.
|
|
#6
|
|||
|
|||
|
Just figured I would explain the issue with Flexible Cord and NM or UF Cable. Neither NM Cable or UF Cable appear in the following statements. While NM Cable is kinda flexible but it is not in the table 400.4 describing flexible cords or cables.
400.4 Types. Flexible cords and flexible cables shall conform
to the description in Table 400.4. Types of flexible cords and flexible cables other than those listed in the table shall be the subject of special investigation. I am guessing most of the locations where you would apply an attachment plug to a cord and so on would demand it be flexible in nature...here is but one example when dealing with appliances. 422.16 Flexible Cords. (A) General. Flexible cord shall be permitted (1) for the connection of appliances to facilitate their frequent interchange or to prevent the transmission of noise or vibration or (2) to facilitate the removal or disconnection of appliances that are fastened in place, where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance or repair and the appliance is intended or identified for flexible cord connection. Paul W. Abernathy Last edited by pabernathy; 7/19/09 at 12:41 PM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Help. What is the correct way to report a breaker that is too big. | gromicko | Electrical Inspections | 77 | 5/10/12 6:13 PM |
| Glade plug ins could lead to fires | gmendes | Miscellaneous Discussion for Inspectors | 1 | 6/20/07 10:53 PM |
| Romex connected to male plug... OK? | ghawley | Electrical Inspections | 20 | 3/4/07 6:05 PM |
| Romex wire connected to standard male plug. | ghawley | Electrical Inspections | 2 | 3/2/06 1:35 PM |
| Plug in Water Heater? | fmorales | Electrical Inspections | 7 | 2/10/06 9:25 AM |