Does this look like a UFER tail? It is coming out of the slab. My concern is it appears it may be going to a UFER and is disconnected. Thank you.
|
|
#2
|
||||
|
||||
|
It's very possible that you're looking at the GEC, but it would be impossible to say for certain with just this picture.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Please Note:
pdoane is a non-member guest and is in no way affiliated with InterNACHI or its members.
I agree with Jeff,
Usually, around here at least, all signs of a UFER ground is hidden from view. Its usually attached to the foundation rebar prior to the pour. |
|
#4
|
||||
|
||||
|
Please Note:
cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
In the Seattle are the ufer connections has to be assessible. I usually find it behind a blank cover plate under the electric panel.
|
|
#5
|
||||
|
||||
|
Quote:
A cadweld is not required to be accessible. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Does this look like a copper conductor? Is it the size of #4 Copper?
If not it cannot be part of the ufer ground. If you could verify that this was rebars it might be part of the ufer. |
|
#7
|
||||
|
||||
|
Just some FYI as not always does the connection need to be accessible.... 250.68 Grounding Electrode Conductor and Bonding Jumper Connection to Grounding Electrodes. (A) Accessibility. All mechanical elements used to terminate a grounding electrode conductor or bonding jumper to a grounding electrode shall be accessible. Exception No. 1: An encased or buried connection to a
concrete-encased, driven, or buried grounding electrode shall not be required to be accessible. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
![]() |