Default Unable to confirm proper ground..

An unusually high number of homes that I have seen over the last month or so have a grounding electrode that exits the foundation and enters the earth. No stake...No anything. I don't know if this is a part of a Ufer ground or some other system that I can not determine. I indicate "unable to confirm proper grounding" on my reports, but I wish I could provide a better statement. Any suggestions
Attached Thumbnails
unable-confirm-proper-ground-gardner-007a.jpg  
Reply With Quote
  #2  
Old 10/15/06, 10:04 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unable to confirm proper ground..

The photo is kinda small, but that looks like a regular 8' driven ground rod. Or is it rebar from the foundation? Hard to tell from the photo.
Reply With Quote
  #3  
Old 10/15/06, 11:14 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unable to confirm proper ground..

The rod may be driven below grade. That is OK
Reply With Quote
  #4  
Old 10/16/06, 12:27 AM
gmathias gmathias is offline
New User
 
Join Date: Aug 2004
Location: Lewisburg, PA
Posts: 64
Please Note: gmathias is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unable to confirm proper ground..

Sorry about the size of the pic. There is a 4 awg copper wire going into the earth. Yes, it's probably attached to a rod somewhere, but I dug down about 6 to 8 inches and didn't find a rod.
Reply With Quote
  #5  
Old 10/16/06, 7:16 AM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unable to confirm proper ground..

That looks like a water pipe clamp. If so, to what is it attached?
Reply With Quote
  #6  
Old 10/16/06, 9:48 AM
gmathias gmathias is offline
New User
 
Join Date: Aug 2004
Location: Lewisburg, PA
Posts: 64
Please Note: gmathias is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unable to confirm proper ground..

The wire enters the earth, no clamp, no stake.
Reply With Quote
  #7  
Old 10/16/06, 9:50 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Unable to confirm proper ground..

Are you able to find the other end of it into the ground....some mistake the # 4 in 20' lengths as a proper grounding method.....while it would be in the foundation of concrete....not in the ground itself.

So I would say what you have listed on your reports based on the lack of information is about all you can put at this time.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 10/16/06, 9:55 AM
Joseph Hagarty's Avatar
Joseph Hagarty Joseph Hagarty is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 3,434
Default Re: Unable to confirm proper ground..

Not Inspected / (followed by a description of the limitation)



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #9  
Old 10/16/06, 10:38 AM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: Unable to confirm proper ground..

I have found on more than one occasion, the conductor going into the soil without any kind of rod or clamp, Period. Also routinely find the "water pipe" clamp is completely disentagrated or only small pieces left, or extremely corroded because the "Weaver" clamp is not made for burial or wet enviroment.
Reply With Quote
  #10  
Old 10/16/06, 11:12 AM
gmathias gmathias is offline
New User
 
Join Date: Aug 2004
Location: Lewisburg, PA
Posts: 64
Please Note: gmathias is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unable to confirm proper ground..

What do you report when you see the ground wire entering the ground? Do you recommend evaluation by an electrician?
Reply With Quote
  #11  
Old 10/17/06, 7:15 AM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unable to confirm proper ground..

Since the ground rod is driven before the landscaping is completed, it may be that the ground rod was buried below the finished grade by several feet of soil.
Reply With Quote
  #12  
Old 10/22/06, 12:43 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Unable to confirm proper ground..

I tug real hard on the conductor. If it can't be pulled up, I assume it's attached to a buried ground rod.

When I can't confirm a ground, I say: "We could not determine the point at which the panel is grounded. Typically, this ground is to a driven ground rod, a water pipe located at the main, at a water heater, or to a hose bib, but we could not find it at any of these locations. Therefore, it should be traced by an electrician or the panel should be regrounded."



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 10/22/06, 8:44 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unable to confirm proper ground..

Quote:
Originally Posted by jfunderburk
"We could not determine the point at which the panel is grounded. Typically, this ground is to a driven ground rod, a water pipe located at the main, at a water heater, or to a hose bib, but we could not find it at any of these locations. Therefore, it should be traced by an electrician or the panel should be regrounded."
I'm not sure if this is a real issue or no big deal, but I would consider re-wording this. An attachment to a ground rod or metallic water pipe at the main would be a grounding electrode (although neither actually "ground" the panel).
The connections at a water heater, hose bib, or anywhere other than the water main are simply the water bond. Again, this does not serve to ground anything.

I know it is just semantics, and most homeowners have no clue, but it is technically incorrect.
Reply With Quote
  #14  
Old 10/22/06, 5:59 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: Unable to confirm proper ground..

kind of like "outlet" and "receptacle"
Reply With Quote
  #15  
Old 10/22/06, 7:39 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unable to confirm proper ground..

Quote:
Originally Posted by dedwards
kind of like "outlet" and "receptacle"
True, but a little more important.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Electricians Check List pabernathy Electrical 74 12/5/07 7:39 PM
Ground Wires Inside a Panel mveitenhans Electrical 13 10/29/06 12:39 PM
Electrical Inspection Training for Home Inspectors jtedesco1 Education 6 4/27/06 11:43 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical 5 3/21/06 9:48 AM


All times are GMT -4. The time now is 9:42 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts