Hey everyone,

I came across a subpanel with a 90 amp service from the main panel outside. Included in the subpanel is the 40 amp breaker for the range along with everything else other than the HVAC system breakers. An electrician friend of mine told me they prefer to put the range breaker in the main panel outside and then to install a 100 amp service to the subpanel.

Any input on how to address this aparent inadequacy in a report?

P.S. I know to include a statement recommending a licensed electrician further evaluate, but I also don't want to raise red flags where none are due.

Thanks



Will R. Stafford

Promised Land Construction & Home Inspection

Home Inspector from Wilmington to Jacksonville NC and surrounding areas.

www.plchomeinspection.com

Jacksonville Home Inspector
Wilmington Home Inspector
Reply With Quote
Find an InterNACHI certified New Mexico Home Inspector (and anywhere else in North America)
  #2  
Old 5/12/09, 9:36 AM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: underamped subpanel??

To determine if the service is properly sized a demand load calculation would be performed.

The smallest service allowed to a dwelling today is 100 amps.
Reply With Quote
  #3  
Old 5/12/09, 9:52 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,745
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: underamped subpanel??

Hi Will,

Jim is correct about the only way to know is by doing a load calc, however you stated that there is a "main" panel feeding the interior "sub" and this panel also feeds the AC, question is what size is the "main" service?? in all likelyhood this is just fine, in fact it sounds an awful lot like this is a manufactured home (mobile home) as that is the way they are commonly wired.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #4  
Old 5/12/09, 10:00 AM
Will R. Stafford's Avatar
Will R. Stafford Will R. Stafford is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Holly Ridge, NC
Posts: 8
Default Re: underamped subpanel??

Thank you gentlemen. That's some good info. The main panel has a supply of 200 amps. Although this situation may exist in manuf. homes, it seemed to me that my client will experience problems with such a system. My report comment is as follows. I'd appreciate your input.

Service to the sub panel is 90 amps. This appears to
be an underrated supply for items such as the range, the dryer, the water heater, and the
other circuits to be in the same panel. This may cause an excessive amount of breaker
overload while multiple circuits are being used. It is recommended that a licensed electrician
evaluate and repair/replace as needed.





Will R. Stafford

Promised Land Construction & Home Inspection

Home Inspector from Wilmington to Jacksonville NC and surrounding areas.

www.plchomeinspection.com

Jacksonville Home Inspector
Wilmington Home Inspector
Reply With Quote
  #5  
Old 5/12/09, 10:54 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,692
Default Re: underamped subpanel??

Quote:
Service to the sub panel is 90 amps. This appears to
be an underrated supply for items such as the range, the dryer, the water heater, and the
other circuits to be in the same panel. This may cause an excessive amount of breaker
overload while multiple circuits are being used. It is recommended that a licensed electrician
evaluate and repair/replace as needed.
How do you know this?
What condition did you find at the time of inspection to support this?
Voltage drop, hot breaker, blinking lights?
You are going to cost someone a service call and likely get in an argument with several people. On what grounds?



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 5/12/09, 1:38 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,736
Send a message via MSN to bwiley
Default Re: underamped subpanel??

On the surface it does not sound improper or undersized in any manner, and is a very common installation in both manufactured homes and "stick built" homes in many areas.

Remember, you can look just as bad making a call that something is incorrect that isn't, as you can calling something correct that isn't.



If the opposite of pro is con, the opposite of progress must be...

www.qualityhomeinspectionsfl.com
Reply With Quote
  #7  
Old 5/12/09, 1:54 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,029
Default Re: underamped subpanel??

Quote:
Originally Posted by bwiley View Post
On the surface it does not sound improper or undersized in any manner, and is a very common installation in both manufactured homes and "stick built" homes in many areas.

Remember, you can look just as bad making a call that something is incorrect that isn't, as you can calling something correct that isn't.
Ditto. Without more information, you might be better off leaving this one alone.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 5/12/09, 2:32 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,216
Default Re: underamped subpanel??

He said that everything was in the sub panel except the hvac....

I would bet that it would be found incorrect by 20-40 amps if a load calc was done on an average size home and even worse if its more than 2500sf.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #9  
Old 5/12/09, 5:02 PM
Will R. Stafford's Avatar
Will R. Stafford Will R. Stafford is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Holly Ridge, NC
Posts: 8
Default Re: underamped subpanel??

I guess I'd rather address an issue that may be a concern to my client in the future. This is why I hoped to gain some useful information from the veterans out there...not some stupid attitude from someone who has to tear others down to feel better about himself.

Thank you to all those who contributed constructively. You are greatly appreciated!

I don't ever want to feel gunshy of asking an inteligent question. I'd like to use this resource as often as possible to ever increase my understanding in this field.



Will R. Stafford

Promised Land Construction & Home Inspection

Home Inspector from Wilmington to Jacksonville NC and surrounding areas.

www.plchomeinspection.com

Jacksonville Home Inspector
Wilmington Home Inspector
Reply With Quote
  #10  
Old 5/12/09, 5:45 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,216
Default Re: underamped subpanel??

Will, I'm looking real hard in this thread to find something that made you say that and I just don't see it ???????

Was it David Anderson's post? That post should not offend you, its good factual information. David is the source of some very good info on here, I recommend you read all of his posts about HVAC too.

Don't read anything extra into posts on here, some are just trolling for an argument but don't make something out of a simple strong opinion.

hope this helps!

by the way, your sample writeup is just fine for that issue you discovered.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #11  
Old 5/13/09, 12:13 AM
Will R. Stafford's Avatar
Will R. Stafford Will R. Stafford is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Holly Ridge, NC
Posts: 8
Default Re: underamped subpanel??

Thanks Bruce. You're absolutely right. I look forward to spending the time getting the valuable info out there. I actually had someone leave a very nasty comment on my personal webpage about my electrical inspection ability and was just irked. I'll keep it professional. Thanks again for your encouragement.



Will R. Stafford

Promised Land Construction & Home Inspection

Home Inspector from Wilmington to Jacksonville NC and surrounding areas.

www.plchomeinspection.com

Jacksonville Home Inspector
Wilmington Home Inspector
Reply With Quote
  #12  
Old 5/13/09, 11:26 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,692
Default Re: underamped subpanel??

I was very short on time yesterday, but I thought your question warranted a reply before you finished your report, or whatever. Sorry if my shortness was constrewed as being a smart *****.

Quote:
I don't ever want to feel gunshy of asking an inteligent question.
I agree. I always ask questions when needed. If we don't have the answers, consider them next time. If you really screwed up, go back. No one will fault you for being wrong and trying to correct it.

I try to ask things that we as HI's can determine without getting off tract, doing things outside the SOP. "Analysis" of any component is not our job (if you elect not to do so). When I call in another "expert" I have a list of things for them to do, and why they should be done. This can't always be done, but you should have the needed information to support your call (something that is actually happening). Something that is wrong.

The main point is that calling in another contractor without something substantial to base the call on will get you in arguments, and make you look bad (substantiated or not) to many people in the process. Electrical Contractor, Seller, Listing Agent, Selling Agent, Client, Clients friends (potential referrals) etc.

I got a call one time from a client who hired two Electrical Contractors to fix a burnt HVAC breaker. She was pissed because both of them said I was FOS and there was nothing wrong. She wanted to know who was going to pay those service calls. I was a mile down the road so I swung by and pulled the breaker (which looked like a lump of charcoal in the back and handed it to her. She asked; Why didn't they find that? "I'm sorry mam, but there are just some questions we can't answer"!

I'd rather you find yourself on this side of the argument.
I try not to tell people "what to do", but rather ask questions. There are too many things that must be assumed if you don't have the facts. Not until I have the needed facts will I recommend you do something.

As for those PM's, just hit the delete button!

p.s. Everyone that posted above, probably knows more about electrical than I do.
More "Experts" responded to you than that one backhanded PM!
Something you just have to get used to here.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission

Last edited by dandersen; 5/13/09 at 11:31 AM..
Reply With Quote
  #13  
Old 5/13/09, 6:08 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,736
Send a message via MSN to bwiley
Default Re: underamped subpanel??

Very well said and on the money, David.



If the opposite of pro is con, the opposite of progress must be...

www.qualityhomeinspectionsfl.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is this subpanel bonded correctly? jboni General Inspection Discussion 12 4/3/09 11:40 AM
Neutral/ground bond in subpanel gkeene Electrical 2 1/23/09 11:14 PM
Discolored service conductor, bonded subpanel dalvares Electrical 3 11/6/08 10:44 PM
Remote distribution panel or subpanel? rwilcox Electrical 57 1/11/08 7:49 PM
SubPanel bonded, ? lfoster Electrical 5 1/9/08 5:08 AM


All times are GMT -4. The time now is 12:53 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts