Is there anything wrong with underfusing? I know for A/C systems this is done for the surge, but what about for other applications? I am talking about a breaker that is to small for the wire it protects. I saw an 8 stranded copper on a 15 amp breaker. It feeds the electric start for the gas range.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Find an InterNACHI certified Alabama Home Inspector (and anywhere else in North America)
  #2  
Old 3/26/09, 4:38 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Underfusing

8 stranded?

What size wire was it? A breaker only accepts a limited amount of wire.

If a breaker is too small for the wire it protects, a nuisance tripping will occur if it becomes a problem.
Reply With Quote
  #3  
Old 3/26/09, 5:06 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 794
Default Re: Underfusing

8 stranded = 8 gauge. Sorry



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #4  
Old 3/26/09, 9:30 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Underfusing

Except for the problem of nusience tripping already mentioned, I don't really feel that there is any such thing as "underfused". The wire really doesn't care if it is being protected at less than it's rating.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #5  
Old 3/26/09, 9:42 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Underfusing

Quote:
Originally Posted by mmerino View Post
It feeds the electric start for the gas range.
Probably had an electric cook top before...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 3/30/09, 12:40 AM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Underfusing

I ran into this the other day, the original 40 amp circuit had been downgraded to 15 amp to run a small heater. As long as the larger wire fits the breaker without needing to be whittled down, no problem. Explaining this to my client, was a bit hard.

John Kogel
www.allsafehome.ca
Reply With Quote
  #7  
Old 3/30/09, 7:43 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Underfusing

except that that wire may be too big for the breaker. how was it attached?
Reply With Quote
  #8  
Old 3/30/09, 8:03 PM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 246
Default Re: Underfusing

you mentioned dropping the fuse size for A/C, normally if they change the size it is to allow for the start up current draw and it is allowed to increase the fuse/breaker to accommodate this. smaller fuse/breaker would prevent the wire from being overloaded
Reply With Quote
  #9  
Old 4/5/09, 1:38 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Underfusing

Many times this is done for voltage drop. As long as the termination is designed to handle the size conductor being placed on it, if the person chooses to run a 8 AWG to a 15 or 20A breaker then thats a design choice....and as long as the conductor and equipment is protected at is listing....does not matter.

I happen to look at a few breakers sitting here on my desk...an Classified Breaker and a homeline 15A and they both said 14-8 AWG are allowed with a single termination...so it depands on the breaker and it will list it on the label....check those labels fella's as this is not a rule of thumb issue....its a labeling issue.



Paul W. Abernathy
Reply With Quote
  #10  
Old 4/5/09, 4:32 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 794
Default Re: Underfusing

Quote:
Originally Posted by pabernathy View Post
Many times this is done for voltage drop. As long as the termination is designed to handle the size conductor being placed on it, if the person chooses to run a 8 AWG to a 15 or 20A breaker then thats a design choice....and as long as the conductor and equipment is protected at is listing....does not matter.

I happen to look at a few breakers sitting here on my desk...an Classified Breaker and a homeline 15A and they both said 14-8 AWG are allowed with a single termination...so it depands on the breaker and it will list it on the label....check those labels fella's as this is not a rule of thumb issue....its a labeling issue.
Paul, I understand what your saying about the breaker being able to accept that size wire. But, what about the breaker being able to accept the amount of electricity? What if the 8 AWG is carrying 40 amps? Is nuisance trips the only issue? How is the condustor or equipment protected?



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #11  
Old 4/5/09, 5:49 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Underfusing

You are reading WAY too much into the example.....if the load is 20A and the breaker is protected at 20A.......it would not matter if the wire was rated for 50A.....as long as the wire can handle the load and the circuit is protected accordingly based on the equipment rating ( which may say it needs a 20A OCPD )...having a larger conductor does not harm anything as long as the terminals can handle the size properly.



Paul W. Abernathy
Reply With Quote
  #12  
Old 4/5/09, 6:02 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Underfusing

Let me give you a better example.....( assuming the lugs are rated for the example ) can I have 4/0 CU on a 200A Breaker?...Sure I can, even if really I only needed 3/0CU ( commercial example )...point is as long as the conductor is sized to handle the load it can be used.

in the example above...I could have 500 CU kcMil if I wanted as long as the lugs to which the conductors are going to terminate allow it.



Paul W. Abernathy
Reply With Quote
  #13  
Old 4/5/09, 6:53 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 794
Default Re: Underfusing

Paul, I understand exactly what you are saying. As home inspectors we will not always know what the conductor services. If I know the 8 AWG conductor services a 10 amp appliance and is connected to a 15 amp breaker I am not going to be concerned.

But in the instance that there is no way of telling what the conductor services, is where I am concerned. If you do not know what the conductor services, you would report it to be corrected. Right?



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Find an InterNACHI certified Alabama Home Inspector (and anywhere else in North America)
  #14  
Old 4/5/09, 7:12 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Underfusing

No I agree not all HI's will. However, those that have the training and are checking the proper labeling, the nameplates and knowing the conductor sizes will be able to make a determination upon their inspection.

None of my statements reflect "WHAT AN HI" should do, they reflect better understanding into the question you asked only and not what should be done by inspectors during inspections.

If you are asking can you have a 8 AWG ( provided the terminals allow it ) on a 15A breaker...most certainly, is it a hazard most certainly not. Will it require a HI to be sharp and on his/her game...most certainly and if you are asking what a HI should do if they can't determine it....by all means put it in the report as I have said a million times...better to defer liability in the event you just don't know.



Paul W. Abernathy
Reply With Quote
  #15  
Old 4/5/09, 8:41 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 794
Default Re: Underfusing

Paul, thanks for your help. I have a better understanding now. I will be more diligent for this in the future.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 7:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts