In the pic below the wire coming out of the ground is not rated. There is no conduit and it enters the box without cable clamp. Is it necessary to have conduit run the entire way or is UF wire sufficient. This goes partly under asphalt lot.
underground-conduit-required-100_0567-small-.jpg.jpg
Views:	136
Size:	71.4 KB
ID:	23196
Thanks



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #2  
Old 8/7/08, 11:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Underground, is conduit required or .......

UF does not require conduit, except for protection as it exits the ground.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 8/7/08, 11:55 PM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Underground, is conduit required or .......

Jeff is that the case even if it runs under parking lot?
Thanks.



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #4  
Old 8/8/08, 12:18 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Underground, is conduit required or .......


Here is the reference. . .

300.5 Underground Installations.

(D) Protection from Damage.
Direct-buried conductors and cables shall be protected from damage in accordance with (1) through (5).

(1) Emerging from Grade.
Direct-buried conductors and enclosures emerging from grade shall be protected by enclosures or raceways extending from the minimum cover distance required by 300.5(A) below grade to a point at least 2.5 m (8 ft) above finished grade. In no case shall the protection be required to exceed 450 mm (18 in.) below finished grade.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 8/8/08, 12:24 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Underground, is conduit required or .......

If it's under a "building," it must be in a raceway or conduit.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 8/8/08, 12:31 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Underground, is conduit required or .......

Quote:
Originally Posted by jgilleland
In the pic below the wire coming out of the ground is not rated. There is no conduit and it enters the box without cable clamp. Is it necessary to have conduit run the entire way or is UF wire sufficient. This goes partly under asphalt lot.
Attachment 23196
Thanks
Jack

You still doing that Pizza joint inspection report?----------
Reply With Quote
  #7  
Old 8/8/08, 1:10 AM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Underground, is conduit required or .......

They called me and asked if I knew what was needed to move the sign. Seems the road is scheduled to be widened. I referred them to an electrician and then got curious.



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #8  
Old 8/8/08, 1:28 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Underground, is conduit required or .......

Quote:
Originally Posted by jgilleland
They called me and asked if I knew what was needed to move the sign. Seems the road is scheduled to be widened. I referred them to an electrician and then got curious.
I'm busting your balls---
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 10:06 AM


All times are GMT -4. The time now is 5:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts