Default Undersized service wire

I looked at a home today that was 15 years old. 200 amp service with 2/0 alum from the meter to the panel. I know it is not allowed now, but was it then? I wrote it up as not being up to currant standards, but an electrician should be consulted for proper application.




Fogarty Inspection Services Group of Knoxville TN
Sean Fogarty
Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.homeinspectionknoxville.com
Reply With Quote
Find an InterNACHI certified Delaware Home Inspector (and anywhere else in North America)
  #2  
Old 11/18/09, 11:32 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Undersized service wire

It's 150 amp service.

Take the lowest of Meter, SEC, Panel rating, main disco.

What is not allowed now?
What was it that you wrote up as to not being to current standards?

Last edited by rmaday; 11/18/09 at 11:39 PM..
Reply With Quote
  #3  
Old 11/18/09, 11:40 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,043
Default Re: Undersized service wire

I thought the possibility of using an udersized wire in between the meter and the panel. If it had 150 amp service why the 200 amp box? I understand the whole principle of the lowest, but if everything was 200 then wouldnt the smaller wire be incorrect? Or if the sec was 150 why would you use a 200 amp panel?




Fogarty Inspection Services Group of Knoxville TN
Sean Fogarty
Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.homeinspectionknoxville.com
Reply With Quote
  #4  
Old 11/18/09, 11:48 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Undersized service wire

Because that is what they bought. See that all the time. Also allows them to increase service later if the want to.
Reply With Quote
  #5  
Old 11/18/09, 11:51 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Undersized service wire

Was the main disco 200?
Reply With Quote
  #6  
Old 11/19/09, 12:02 AM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: Undersized service wire

Sean your a little confusing. Is the main disconnect 200 amp and the wire 2/0 Alum.
The panel can be bigger but not smaller.
If the wire is rated for a 150 amp breaker and a 200 amp is installed this is incorrect.
Hope this helps





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #7  
Old 11/19/09, 12:20 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,043
Default Re: Undersized service wire

Yes The main panel and the breaker were 200 amps. It was an outside panel. The meter base was directly above it and the wire that connected both was rated for 150 amps. Hope this clairifies things.




Fogarty Inspection Services Group of Knoxville TN
Sean Fogarty
Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.homeinspectionknoxville.com
Reply With Quote
  #8  
Old 11/20/09, 7:32 AM
psullivan psullivan is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Round Rock, TX
Posts: 6
Default Re: Undersized service wire

Since the disconnect is larger (200A) than the safe carrying capacity of the service entrance cable (i.e., 2/0 AL = 150A), then this is (and always has been) a problem. If the home's electrical components draw more than 150A of current, then the main disconnect breaker will allow it (until it reaches 200A), and the service entrance cable will heat up because it is undersized. Here's how I would write it up:

The service entrance cable is composed of AWG 2/0 Aluminum, and is capable of safely carrying 150 Amps of current. However, the main disconnect circuit breaker is rated at 200 Amps, and is not therefore not compatible with the service entrance cable. Recommend a qualified electrician evaluate and determine a course of corrective action for electrical safety.

Hope this helps ... Good Luck ...

Peter Sullivan
National Property Inspections
Round Rock, TX
Reply With Quote
  #9  
Old 11/20/09, 9:56 AM
Ed Padilla Ed Padilla is offline
InterNACHI Member
 
Join Date: Sep 2007
Location: Maitland, FL
Posts: 12
Default Re: Undersized service wire

Excellent info Peter. Thanks for sharing.
Reply With Quote
  #10  
Old 11/20/09, 10:10 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Undersized service wire

Ask yourself these two questions...

What is the overcurrent protection for the ciurrent coming into the panel?

What is the overcurrent protection for the SEC?
Reply With Quote
  #11  
Old 11/20/09, 10:38 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,043
Default Re: Undersized service wire

Here is what I wonder. Almost every house I look at, the sec from the transformer is always smaller until it gets to where it is clamped together in front of the weaterhead. The wire from the clamps to the meter are usualy the right size but not the sec. Is that not the power companies responsibility? Some of the older home I know the copper wire coming in is solid. Would solid copper be thinner than stranded with the same gauge?
Also why is the neutral wire sometimes smaller than the two hot feeds? Should it not be the same size.




Fogarty Inspection Services Group of Knoxville TN
Sean Fogarty
Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.homeinspectionknoxville.com
Reply With Quote
  #12  
Old 11/20/09, 11:10 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,585
Default Re: Undersized service wire

Quote:
Originally Posted by sfogarty View Post
Here is what I wonder. Almost every house I look at, the sec from the transformer is always smaller until it gets to where it is clamped together in front of the weaterhead. The wire from the clamps to the meter are usually the right size but not the sec. Is that not the power companies responsibility? Some of the older home I know the copper wire coming in is solid. Would solid copper be thinner than stranded with the same gauge?
Also why is the neutral wire sometimes smaller than the two hot feeds? Should it not be the same size.
If all your questions deal with the wire coming from the pole. Then the wires can be smaller because they claim these wires get more air movement around these wires thus keeping them from over heating. Kinda makes sense when you think about it. Also the SEC wire should have a smaller feed back to the transformer than wires feeding to the house thus that is why it is smaller.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
2 Service Disconnects tlarsen Electrical Inspections 11 8/21/09 9:41 AM
Clearence for service wire wwilson3 Electrical Inspections 9 8/19/09 10:21 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical Inspections 9 8/28/06 2:08 AM


All times are GMT -4. The time now is 6:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts