Default UL Standards #20 and #498

I'm looking for a copy of these standards.

Any help is greatly appreciated!

Thanks!




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #2  
Old 11/15/07, 10:34 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: UL Standards #20 and #498

Does this work for you ?

http://ulstandardsinfonet.ul.com/cat...scatframe.html
Reply With Quote
  #3  
Old 11/15/07, 10:55 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: UL Standards #20 and #498

Wow!

I just want these 2 standards not $600 worth of all of them.

I'm looking for the actual statement in writing that the UL indicates as a temperature threshold for problematic electrical components such as switches, receptacles, breakers, etc.

I have learned that it's reported to be 30°C (54°F) temperature difference between a component and ambient temperature. This threshold is supposed to be the defining indicator (from UL) of whether an electrical component is problematic or not.

I would just like to have this in writing rather than stating that I learned it in a class.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #4  
Old 11/15/07, 11:07 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: UL Standards #20 and #498

30c is 86f
Different equipment will have different thresholds. Breakers usually have 40c 104f molded in them but I couldn't get NFPA interested in that when I asked about a panel full of AFCIs in a comment for the 2008 ROC.

U/L is a standards organization. They make money selling standards, not giving them away. I agree with you, when this gets adopted as law they should lose that protection ... but it isn't true.

Last edited by Greg Fretwell; 11/15/07 at 11:13 PM..
Reply With Quote
  #5  
Old 11/15/07, 11:13 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: UL Standards #20 and #498

Quote:
Originally Posted by Greg Fretwell
30c is 86f
You're right...I wrote it down wrong and didn't do the math myself.

(why I want it in writing)

Thanks




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #6  
Old 11/15/07, 11:19 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: UL Standards #20 and #498

Quote:
Originally Posted by Greg Fretwell
Different equipment will have different thresholds. Breakers usually have 40c 104f molded in them but I couldn't get NFPA interested in that when I asked about a panel full of AFCIs in a comment for the 2008 ROC.

U/L is a standards organization. They make money selling standards, not giving them away. I agree with you, when this gets adopted as law they should lose that protection ... but it isn't true.
Is there a rule of thumb with existing documentaion to back it up in existence? Or should it be more based on mfg statements and recommendations?




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #7  
Old 11/16/07, 10:30 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: UL Standards #20 and #498

Quote:
Originally Posted by Greg Fretwell
30c is 86f
Different equipment will have different thresholds. Breakers usually have 40c 104f molded in them but I couldn't get NFPA interested in that when I asked about a panel full of AFCIs in a comment for the 2008 ROC.
lol........you trouble maker you....thehehehe.......



Paul W. Abernathy
Reply With Quote
  #8  
Old 11/16/07, 10:44 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: UL Standards #20 and #498

Even if you find the exact text of those specific standards, it probably will be necessary to also understand the conditions under which UL sets those parameters. For example, I would almost bet that they are based on a device operating at rated load in a 40C ambient, as that is the baseline ambient for many electrical devices. Thus, the 'rule-of-thumb' mentioned may not accurately represent an acceptable temperature rise under real-world conditions.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #9  
Old 11/16/07, 11:29 AM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: UL Standards #20 and #498

I understand what you're saying.

But a wall switch or receptacle in a typical house should not be typically exposed to a 40C (104F) ambient (surrounding) temp. The ambient temp should be more in the 20C to 25C range. The UL standard is supposed to say that a switch that is 30C above the surrounding wall temp has a problem. If it's 28C above the surroundings, it's probably ok

I don't know... I want to see the standard and read for myself what the intentions are.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #10  
Old 11/16/07, 6:08 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: UL Standards #20 and #498

The 40 deg. marking refers to the max. ambient the component is intended to operate at. Not the max. component temp.

If the mfg. wants a higher marking. his component has to be tested and pass at the higher ambient temp for the max rise of all parts contained therein.
Reply With Quote
  #11  
Old 11/16/07, 6:11 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: UL Standards #20 and #498

Quote:
Originally Posted by wwarner
I don't know... I want to see the standard and read for myself what the intentions are.
Some libraries have some UL standards. They are often very expensive and UL 498 is very thick as it covers many types of components.
Reply With Quote
  #12  
Old 11/16/07, 6:15 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: UL Standards #20 and #498

Quote:
Originally Posted by mlarson
Some libraries have some UL standards. They are often very expensive and UL 498 is very thick as it covers many types of components.
Thanks Michael




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #13  
Old 11/16/07, 7:12 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: UL Standards #20 and #498

In the case of a breaker, all I have been told is, that is what temperature it was calibrated, not the maximum temperature it will operate.
Reply With Quote
  #14  
Old 11/16/07, 7:21 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: UL Standards #20 and #498

Quote:
Originally Posted by Greg Fretwell
In the case of a breaker, all I have been told is, that is what temperature it was calibrated, not the maximum temperature it will operate.
Thanks Greg




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #15  
Old 11/16/07, 9:58 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: UL Standards #20 and #498

Quote:
Originally Posted by wwarner
You're right...I wrote it down wrong and didn't do the math myself.

(why I want it in writing)

Thanks
OK here's the deal...

My original statement is correct:
Quote:
I have learned that it's reported to be 30°C (54°F) temperature difference between a component and ambient temperature. This threshold is supposed to be the defining indicator (from UL) of whether an electrical component is problematic or not.
and here is why... (infrared guys pay attention!)

The UL states that A difference of 30°C between ambient temperature and the temperature of electrical component indicates a problematic component. Soooo... doing the math...

Let's say the ambient temperature of the wall is a 0°C and the measured temperature of the light switch is 30°C. this is a difference of 30° which indicates a problem acording to UL.

Now using the Fahrenheit scale 0°C =32°F (the measured temperature of the wall) and 30°C =86°F (the measured temperature of the light switch) which is a difference of 54° on the Fahrenheit scale.

Pretty darn confusing if you do ask me, but doing research of other technical papers this is the same way they list temperature differences.

Makes sense now don't it!




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...

Last edited by wwarner; 11/16/07 at 10:12 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 7:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts