Default ungrounded 3 prong plugs

I have read in an inspection report (from someones website) that the fix can "be as simple as filling the ground slot with epoxy". Is this really a safe fix to do? I would not recommend this.



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/12/10, 12:07 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: ungrounded 3 prong plugs

Quote:
Originally Posted by dokeefe View Post
I have read in an inspection report (from someones website) that the fix can "be as simple as filling the ground slot with epoxy". Is this really a safe fix to do? I would not recommend this.
Seems strange but there would be nothing unsafe about it.
Reply With Quote
  #3  
Old 12/12/10, 12:11 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: ungrounded 3 prong plugs

Please post a link to that report. That sounds like a good read.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 12/12/10, 12:20 AM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: ungrounded 3 prong plugs

I'll have to go and try to find it. He does also state that a ground wire can also be run to the plug and also a gfci can be used. Seams like an amateur fix. I mean if you saw epoxy stuffed in a ground plug during an inspection wouldn't you call for it to be replaced?



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #5  
Old 12/12/10, 12:22 AM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: ungrounded 3 prong plugs

Here it is.
http://www.thehomeinspectionwebsite....ex.php?page=10



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #6  
Old 12/12/10, 12:22 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: ungrounded 3 prong plugs

Quote:
Originally Posted by dokeefe View Post
I'll have to go and try to find it. He does also state that a ground wire can also be run to the plug and also a gfci can be used. Seams like an amateur fix. I mean if you saw epoxy stuffed in a ground plug during an inspection wouldn't you call for it to be replaced?
Huh...yes.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 12/12/10, 7:43 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded 3 prong plugs

Sounds unsafe and that method is not supported by the NEC.
Reply With Quote
  #8  
Old 12/12/10, 7:49 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: ungrounded 3 prong plugs

Would it not be simpler to mark it Not a grounded outlet? or replace it with the right outlet.
The accept GFCI outlet on a renovation Permit for non grounded outlets.



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #9  
Old 12/12/10, 10:25 AM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,322
Default Re: ungrounded 3 prong plugs

Quote:
Originally Posted by dokeefe View Post

Reply With Quote
  #10  
Old 12/12/10, 1:04 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: ungrounded 3 prong plugs

Prescribing fixes like this is not a good idea.

It may be just a sample report with some verbiage from the manufacturer/software co. If you're gonna tell people to put a liquid form of anything in an outlet ... you should probably tell them to *turn the power off first*, if we're gonna tell some one to do that. As I doubt later telling someone "I'm sorry you got shocked, I didn't tell ya to put runny epoxy in there"

I haven't seen and doubt that this is a listed fix from any manufacturer.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770









Last edited by tspargo; 12/12/10 at 1:16 PM.. Reason: typo
Reply With Quote
  #11  
Old 12/12/10, 2:05 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: ungrounded 3 prong plugs

Quote:
Originally Posted by dokeefe View Post
Here's what Jason Micare, The Home Inspector, LLC said:

"Ungrounded 3-prong outlets ( I.E. near kitchen stove) should be improved. This can be as simple as filling the ground slot with epoxy. Alternatively, a grounded cable could be strung to this outlet, or a separate ground wire could be connected. Some electrical codes allow the installation of a ground fault circuit interrupter (GFCI) type outlet where grounding is not provided."

I say his statement is ill advised and borders on incompetent. ASHI inspector I see.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 12/12/10 at 2:08 PM..
Reply With Quote
  #12  
Old 12/12/10, 2:16 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: ungrounded 3 prong plugs

Here's what I would have said:

"One or more outlets in the *LOCATION(rooms-interior)* has an open ground. The absence of a ground is a shock or electrocution hazard in some instances and should be serviced by a licensed and competent electrician within the contingency period or before the close of escrow."

If the house is an older 2-wire system with 3 prong outlets, I might say this:

"Many outlets were the 3-prong type and nearly all were ungrounded. Although a ground isn't required of 2-prong outlets, if the receptacle is 3 prong and ungrounded it gives a false sense of safety. Grounding of all 3-prong outlets, reverting back to 2-prong outlets, or protecting them with ground fault circuit interrupters (GFCIs) is recommended for safety reasons."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 12/12/10, 2:22 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: ungrounded 3 prong plugs

Quote:
Originally Posted by belliott View Post
Seems strange but there would be nothing unsafe about it.
Not unsafe? Squirting liquid into an outlet is safe? How would anyone with a 3-prong appliance use it? Break off the ground pin?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/12/10, 2:33 PM
bemelander bemelander is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Grand Rapids, MI
Posts: 341
Default Re: ungrounded 3 prong plugs

My reply would be similar to what Joe said. But when I took my home inspection class 10 years ago filling the ground with epoxy was one of their recommendations.



Bill Emelander
Professional Edge Home Inspection
Grand Rapids and all of West Michigan
NACHI #03111914
www.proedgehi.com
Reply With Quote
  #15  
Old 12/12/10, 4:30 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: ungrounded 3 prong plugs

Quote:
Originally Posted by jfunderburk View Post
Not unsafe? Squirting liquid into an outlet is safe? How would anyone with a 3-prong appliance use it? Break off the ground pin?
That's the object--make the outlet unusable for a three pronged plug. There is a reason for the third prong--and that reason is negated by an ungrounded receptacle. It give a false sense of security when the homeowner sees a three-hole receptacle--he would assume that the receptacle is safe to use with a three-pronged plug. But it may not be.

Never use an electrical appliance (outlet, receptacle, toaster, etc) in any manner other than as designed by the engineer who designed the toaster, or whatever.

I'm not suggesting the use of epoxy--that is a no-no--nor should one label the receptacle as ungrounded--no one reads that, especially if the label is removed.

The best thing to do, short of running a proper three-wire, would be to install a GFCI. The GFCI would break the current before harm can be done--hopefully. And use an "ungrounded" label (for as long as it might last).

A third wire can, in some instances, be installed--provided it is properly installed.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin

Last edited by jwilliams4; 12/12/10 at 4:36 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
ungrounded outlets cjustason Electrical Inspections 3 3/29/10 8:09 PM
2 prong and 3 prong? gbrasseur Electrical Inspections 4 3/2/07 4:50 PM
Ungrounded plugs kblair1 Electrical Inspections 19 12/21/06 8:17 PM
Two prong outlets and GFCI's crichiii Electrical Inspections 8 3/15/06 10:41 PM


All times are GMT -4. The time now is 7:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts