Default Ungrounded Distribution Panel

This was quite a "miss." Not only did the city inspector miss it, this panel had been inspected several times for resale of the property. The current owners were completely unaware of the condition.

The panel is not even equipped with a grounding terminal that would fit the EGC from the service equipment.
Attached Thumbnails
ungrounded-distribution-panel-20111011_04.jpg   ungrounded-distribution-panel-20111011_05.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Need a home inspection in Tennessee? Check out InterNACHI's listing of Tennessee certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/11/11, 5:07 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Ungrounded Distribution Panel

Awesome... send that to Paul. I'm sure he would get a 'kick' out of it!
Reply With Quote
  #3  
Old 10/11/11, 8:10 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded Distribution Panel

Quote:
Originally Posted by jpope View Post

The panel is not even equipped with a grounding terminal that would fit the EGC from the service equipment.
That's probably the reason why it wasn't terminated, someone would get back to it later.
Reply With Quote
  #4  
Old 10/11/11, 8:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Ungrounded Distribution Panel

Quote:
Originally Posted by Robert Meier View Post
That's probably the reason why it wasn't terminated, someone would get back to it later.
That was my thought as well... I wonder how many more were like that. This was a townhouse community.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 10/11/11, 9:04 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded Distribution Panel

Quote:
Originally Posted by jpope View Post
That was my thought as well... I wonder how many more were like that. This was a townhouse community.
Ouch. Could be a big problem. Doesn't say much about all of the inspectors that came along before you. Nice job.
Reply With Quote
  #6  
Old 10/11/11, 9:30 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Ungrounded Distribution Panel

Quote:
Originally Posted by jpope View Post
That was my thought as well... I wonder how many more were like that. This was a townhouse community.
Marketing oppourtunity!
Reply With Quote
  #7  
Old 10/12/11, 8:55 PM
An HI An HI is offline
Active Poster
 
Join Date: Oct 2011
Location: cyberspace
Posts: 196
Please Note: An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded Distribution Panel

Quote:
Originally Posted by jpope View Post
This was quite a "miss." Not only did the city inspector miss it, this panel had been inspected several times for resale of the property. The current owners were completely unaware of the condition.

The panel is not even equipped with a grounding terminal that would fit the EGC from the service equipment.
Are they not using anti-oxidant paste with aluminum wire in your neck of the woods?
Reply With Quote
  #8  
Old 10/12/11, 10:13 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded Distribution Panel

Quote:
Originally Posted by An HI View Post
Are they not using anti-oxidant paste with aluminum wire in your neck of the woods?
Maybe if they were going to use it they were going to install it when the lug was installed. BTW, there is no requirement for its use, unless called for by the manufacturer. I have never seen a roll of wire with any instructions.
Reply With Quote
  #9  
Old 10/12/11, 10:16 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded Distribution Panel

Quote:
Originally Posted by Jim Port View Post
Maybe if they were going to use it they were going to install it when the lug was installed. BTW, there is no requirement for its use, unless called for by the manufacturer. I have never seen a roll of wire with any instructions.
I agree, and have heard numerous times that it's required because the conductors are aluminum. I've yet to come across any lug that said you must use it with aluminum conductors.
Reply With Quote
  #10  
Old 10/13/11, 8:10 AM
An HI An HI is offline
Active Poster
 
Join Date: Oct 2011
Location: cyberspace
Posts: 196
Please Note: An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded Distribution Panel

Quote:
Originally Posted by Robert Meier View Post
I agree, and have heard numerous times that it's required because the conductors are aluminum. I've yet to come across any lug that said you must use it with aluminum conductors.
The oxidation that forms on the exterior of bare aluminum is resistant to current flow (while on copper, it is conductive)


http://www.inspectapedia.com/aluminum/alreduce.pdf
See Page 4.

Anti-oxident paste is required on aluminum wire by the AHJ in my area.
Reply With Quote
  #11  
Old 10/13/11, 12:40 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded Distribution Panel

Quote:
Originally Posted by An HI View Post
The oxidation that forms on the exterior of bare aluminum is resistant to current flow (while on copper, it is conductive)


http://www.inspectapedia.com/aluminum/alreduce.pdf
See Page 4.

Anti-oxident paste is required on aluminum wire by the AHJ in my area.

Your link didn't work.

This is an old debate. IMO using the paste is a good idea but the notion that it's required is false. A local code would be a different issue altogether. Every terminal that I've seen that was listed for use with aluminum conductors said nothing about the required use of anti-oxidant paste. If I had to guess I would say that as part of the product's listing it's required to be manufactured for use without the anti-ox.
Reply With Quote
  #12  
Old 10/13/11, 8:11 PM
An HI An HI is offline
Active Poster
 
Join Date: Oct 2011
Location: cyberspace
Posts: 196
Please Note: An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded Distribution Panel

Quote:
Originally Posted by Robert Meier View Post
Your link didn't work.
Just worked for myself.
Reply With Quote
  #13  
Old 10/13/11, 8:35 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded Distribution Panel

Quote:
Originally Posted by An HI View Post
Just worked for myself.
I tried it just now and it worked.

Great article.
Reply With Quote
Need a home inspection in Tennessee? Check out InterNACHI's listing of Tennessee certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 10/13/11, 9:01 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Ungrounded Distribution Panel

Did not work for me earlier either ... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #15  
Old 10/16/11, 9:40 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Ungrounded Distribution Panel

That InspectApedia article primarily discusses older aluminum wire from the 1960's (called "old technology" wire) which was made differently than current AA-8000 series aluminum wire that doesn't need anti-oxident paste at connections ... http://en.wikipedia.org/wiki/Aluminum_wire



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Sub distribution panel 'over qualified' ? lfoster Electrical Inspections 7 4/12/09 7:56 AM
Electric Panel dmozzillo Electrical Inspections 26 1/26/09 1:18 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 7:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts