Default Ungrounded downstream GFCI

Old home has ungrounded GFCI near the sink, trips with the test button, but does not trip with a GFCI tester, I know this is normal.(but dont really understand why) My question is on the other side of the sink the outlet is linked to the GFCI but does not have a test button. Power goes off when the test button on the first GFCI is pushed.
How does this protect anyone if you have to push the test button to cut power. I dont get it, make me understand.

Thanks, Steve



Steve Costa
Royal Home Inspections LLC.
Ohio Home Inspections
Serving Cuyahoga, Medina,
Summit, Lorain, Portage, Wayne
Stark, and Ashland Counties
Reply With Quote
  #2  
Old 3/7/07, 11:26 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded downstream GFCI

The gfci will work just fine without the grounding wire. It will sense when there is an imbalance and trip. If you used a wiggy with one probe in the receptacle and touched the other to a continuous water pipe it would trip.

Your tester tries to do the same thing by using the grounding path to shunt some current into, but with no grounding wire no current flows so none can turn up missing.
Reply With Quote
  #3  
Old 3/7/07, 11:28 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded downstream GFCI

Here is a good explaination in Laymans terms, scroll down to the fourth post. http://forums.jlconline.com/forums/s...ad.php?t=35284
Reply With Quote
  #4  
Old 3/7/07, 11:30 PM
scosta's Avatar
scosta scosta is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Default Re: Ungrounded downstream GFCI

Thanks Brian, that was so simply explained, I got it.
Steve



Steve Costa
Royal Home Inspections LLC.
Ohio Home Inspections
Serving Cuyahoga, Medina,
Summit, Lorain, Portage, Wayne
Stark, and Ashland Counties
Reply With Quote
  #5  
Old 3/8/07, 9:29 AM
cbrands's Avatar
cbrands cbrands is offline
New User
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 97
Please Note: cbrands is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded downstream GFCI

alot of testers use a ground fault to test.
no ground to fault to...no trip.
Reply With Quote
  #6  
Old 3/8/07, 11:07 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: Ungrounded downstream GFCI

My understanding is a GFCI device (new version) will trip if there is no ground attached. You must become the ground for the device to work.

Put your hand in a sink full of water and put your finger in the small plughole! ("Here's your sign")

I don't think I'll try this one on a routine basis!
Reply With Quote
  #7  
Old 3/8/07, 11:55 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Ungrounded downstream GFCI

Awww...come on David. We have to have SOMEONE test that theory...lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 3/8/07, 1:17 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: Ungrounded downstream GFCI

So simple a caveman could do it.
Reply With Quote
  #9  
Old 3/8/07, 1:24 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Ungrounded downstream GFCI

lol...I love those commericals Doug...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 3/8/07, 1:41 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 197
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded downstream GFCI

Hmmmmmm, so by extension my AC with no ground wire but a bonding strip, with self-grounding GFCIs is well grounded since pushing the test button does trip them. Surely this is a test for if older BX with no bonding strip has an adequate grounding path through the metal outer?

Any takers? Should create some shouting.

Last edited by Ian Gills; 3/8/07 at 1:45 PM..
Reply With Quote
  #11  
Old 3/8/07, 1:45 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Ungrounded downstream GFCI

lol....no debate here......Older BX has no bonding strip and the internal testing feture of the GFCI also does not need the " bonding " path....but alas don't confuse the use of a GFCI to take the place of a properly installed EGC.

No shouting here......I have been ALL over the country and I hear all kinds of thoughts......I am just here to educate as I will leave the shouting to the ones who feel threatened...

P.S. you should not EXTEND an AC system from a cable that has no EGC to one that does.....the GFCI is a good safety enhancement for a (2) wire system that has no EGC.....not to replace the concept...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 3/8/07, 1:50 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 197
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded downstream GFCI

I thought the bonding path ensured a good ground. If GFCIs need a good ground to test trip, then surely a ground path is good with or without the strip, if the test trips.

Who needs a ground tester, when a GFCI could do the job, albeit for a little more labor?
Reply With Quote
  #13  
Old 3/8/07, 1:54 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Ungrounded downstream GFCI

Ahh...terminology thing going on here.....

1.) The call the EGC a " Equipment Grounding Conductor" but in reality it is a " Equipment Bonding Conductor" and it provides a low impedence path for aid in clearing a breaker....(edit: or fuse for that matter...

2.) The GFCI does not need a " Good Ground" to function as it has been explained on here many times how a GFCI functions and the EGC of a system plays no effect on how it functions.

The TEST that trips is in relation to the Ungrounded and Grounded conductors and not the " GROUNDING" conductor which is why some GFCI testers wont trip it....but alas you need the " Dummy Testers" to verify reverse polarity ( guess you could also do that with a voltage ticker" but it also tells you other things.....

Still the proper way to test a GFCI is at the device itself.......the testing devices like the GB and Suretest are great for confirmation but can be fooled....so expensive or cheap...worth having.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 3/8/07 at 1:59 PM..
Reply With Quote
  #14  
Old 3/8/07, 2:05 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 3,853
Default Re: Ungrounded downstream GFCI

Quote:
Originally Posted by dedwards
So simple a caveman could do it.
Let's leave my family out of this, OK?





"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #15  
Old 3/8/07, 2:06 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Ungrounded downstream GFCI

lol....is it only me but the one I like the best is the original caveman...the one that is on the conveyor belt and in the original commericals...I don't like the one they use in that therapist one......sorry....I just had to say that.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Ungrounded GFCI srinner Electrical 29 11/30/07 11:15 AM
GFCI Safety Notice rcooke Electrical 1 10/30/07 1:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical 28 10/4/06 10:31 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM
UL Information about Testing of GFCIs jtedesco1 Electrical 0 2/5/06 5:38 PM


All times are GMT -4. The time now is 11:05 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts