Old home has ungrounded GFCI near the sink, trips with the test button, but does not trip with a GFCI tester, I know this is normal.(but dont really understand why) My question is on the other side of the sink the outlet is linked to the GFCI but does not have a test button. Power goes off when the test button on the first GFCI is pushed.
How does this protect anyone if you have to push the test button to cut power. I dont get it, make me understand. Thanks, Steve |
|
#2
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
The gfci will work just fine without the grounding wire. It will sense when there is an imbalance and trip. If you used a wiggy with one probe in the receptacle and touched the other to a continuous water pipe it would trip.
Your tester tries to do the same thing by using the grounding path to shunt some current into, but with no grounding wire no current flows so none can turn up missing. |
|
#3
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here is a good explaination in Laymans terms, scroll down to the fourth post. http://forums.jlconline.com/forums/s...ad.php?t=35284
|
|
#4
|
||||
|
||||
|
Please Note:
scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks Brian, that was so simply explained, I got it.
Steve |
|
#5
|
||||
|
||||
|
Please Note:
cbrands is a non-member guest and is in no way affiliated with InterNACHI or its members.
alot of testers use a ground fault to test.
no ground to fault to...no trip. |
|
#6
|
||||
|
||||
|
My understanding is a GFCI device (new version) will trip if there is no ground attached. You must become the ground for the device to work.
Put your hand in a sink full of water and put your finger in the small plughole! ("Here's your sign") I don't think I'll try this one on a routine basis! |
|
#7
|
||||
|
||||
|
Awww...come on David. We have to have SOMEONE test that theory...lol
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#8
|
||||
|
||||
|
So simple a caveman could do it.
|
|
#9
|
||||
|
||||
|
lol...I love those commericals Doug...
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#10
|
|||
|
|||
|
Please Note:
Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hmmmmmm, so by extension my AC with no ground wire but a bonding strip, with self-grounding GFCIs is well grounded since pushing the test button does trip them. Surely this is a test for if older BX with no bonding strip has an adequate grounding path through the metal outer?
Any takers? Should create some shouting. Last edited by Ian Gills; 3/8/07 at 1:45 PM.. |
|
#11
|
||||
|
||||
|
lol....no debate here......Older BX has no bonding strip and the internal testing feture of the GFCI also does not need the " bonding " path....but alas don't confuse the use of a GFCI to take the place of a properly installed EGC.
No shouting here......I have been ALL over the country and I hear all kinds of thoughts......I am just here to educate as I will leave the shouting to the ones who feel threatened... P.S. you should not EXTEND an AC system from a cable that has no EGC to one that does.....the GFCI is a good safety enhancement for a (2) wire system that has no EGC.....not to replace the concept... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#12
|
|||
|
|||
|
Please Note:
Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
I thought the bonding path ensured a good ground. If GFCIs need a good ground to test trip, then surely a ground path is good with or without the strip, if the test trips.
Who needs a ground tester, when a GFCI could do the job, albeit for a little more labor? |
|
#13
|
||||
|
||||
|
Ahh...terminology thing going on here.....
1.) The call the EGC a " Equipment Grounding Conductor" but in reality it is a " Equipment Bonding Conductor" and it provides a low impedence path for aid in clearing a breaker....(edit: or fuse for that matter... 2.) The GFCI does not need a " Good Ground" to function as it has been explained on here many times how a GFCI functions and the EGC of a system plays no effect on how it functions. The TEST that trips is in relation to the Ungrounded and Grounded conductors and not the " GROUNDING" conductor which is why some GFCI testers wont trip it....but alas you need the " Dummy Testers" to verify reverse polarity ( guess you could also do that with a voltage ticker" but it also tells you other things..... Still the proper way to test a GFCI is at the device itself.......the testing devices like the GB and Suretest are great for confirmation but can be fooled....so expensive or cheap...worth having. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 3/8/07 at 1:59 PM.. |
|
#14
|
|||
|
|||
|
Quote:
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#15
|
||||
|
||||
|
lol....is it only me but the one I like the best is the original caveman...the one that is on the conveyor belt and in the original commericals...I don't like the one they use in that therapist one......sorry....I just had to say that.
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 2 | 1/8/11 8:04 PM |
| Ungrounded GFCI | srinner | Electrical Inspections | 29 | 11/30/07 11:15 AM |
| GFCI Safety Notice | rcooke | Electrical Inspections | 1 | 10/30/07 1:29 PM |
| The question asked on the new HI Study test here? | jtedesco1 | Electrical Inspections | 28 | 10/4/06 10:31 AM |
| UL Information about Testing of GFCIs | jtedesco1 | Electrical Inspections | 0 | 2/5/06 5:38 PM |