Default ungrounded outlets!

I inspected a duplex on Friday that had grounded type of outlets throughout the building. Both living units were full of furniture since the inhabitants had not moved out yet. About one third of the electrical outlets were accessible for testing. EVERY outlet I tested in that duplex indicated NO GROUND CONNECTION. After I tested the third outlet in the inspection, I thought a trend had been established - no grounds! No grounding continued until I had tested all that were accessible; one third accessible), and I recorded it as such and told the realtor and prospective buyer. Then I got to the electrical service panel and found that there were not enough ground wires coming into the panel to ground all of the outlets in the unit!

The building was built in the early fifties and the interior walls were the same walls as in the fifties.

I told the realtor and prospective buyer that someone installed three prong grounding outlets into a two conductor wiring system with no ground wiring.
They asked why, and so did I. Then I mentioned it was to make the place look as though it had updated wiring when in fact, it did not.

Now the realtor calls me back and asks "how do I explain this to an electrician, cause he has to correct it before the sale will go through?"
I explained it to her again, several times, and finally she thinks she understands.

What else should I have done? How else could I explain it so she gets the concept? Isn't it a matter of deceit? Someone trying to fool someone else into a situation that isn't as it appears to be?
George Maher
Home - Safe Home, L.L.C.
Fargo, ND
Reply With Quote
  #2  
Old 5/29/07, 11:57 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: ungrounded outlets!

Sometimes it is not a sinister motive but purely economics or availability. The homeowner goes ditty bopping down to Wal-mart, finds the three pronged (grounded) receptacles are only 51 cents and the two prong are $2.50. Now he needs 30 receptacles, does the math and figures he can save $60 by just using the three prong. I see it here more often than not. Go back to the electrical archives as there are some detailed explanations on how to correct this IAW the NEC.
Reply With Quote
  #3  
Old 5/30/07, 12:06 AM
cbrands's Avatar
cbrands cbrands is offline
New User
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 97
Please Note: cbrands is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

Quote:
Originally Posted by dedwards
Sometimes it is not a sinister motive but purely economics or availability. The homeowner goes ditty bopping down to Wal-mart, finds the three pronged (grounded) receptacles are only 51 cents and the two prong are $2.50. Now he needs 30 receptacles, does the math and figures he can save $60 by just using the three prong. I see it here more often than not. Go back to the electrical archives as there are some detailed explanations on how to correct this IAW the NEC.
agreed.

although you can never rule out any sort of motive, this is usually done out of ignorance of the concepts behind their design.

many times, when explaining to clients that you just cant swap out outlets, they admit that they had no idea.
Reply With Quote
  #4  
Old 5/30/07, 1:05 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is online now
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,606
Default Re: ungrounded outlets!

They can simply install a GFCI for each circuit involved and then label the new outlets as having no ground, the labels are included with most GFCI's.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #5  
Old 5/30/07, 8:10 AM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 197
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

I would be interested in knowing what wiring they have? I have a 1950s house with armored cable with the conductor strip along the casing. I used to have two prong sockets but installed three prong sockets since the casing and conductor strip act as a ground. Perhaps they have the same wiring and so thought that the receptacles would be grounded while forgetting to test for ground? Or pehaps they have the older BX wiring (without the strip) which cannot be used for this? It may be as simple as them forgetting to use self-grounding receptacles if they have Armored Cable and have metal wall boxes.

Last edited by Ian Gills; 5/30/07 at 8:14 AM..
Reply With Quote
  #6  
Old 5/30/07, 11:56 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

I don't think there's a sinister plot at work here, just pure convience and simple economics. Bruce makes the suggestion that I always make in such situations, concerning adding GFCI receptacles upstream on each circuit. It violates no protocols, adds a measure of protection against shock hazard to those old two wire systems, and is the least inexpensive alternative. That makes agents real happy. I might add that grounding is desirable wherever computer equipment is to be located
Reply With Quote
  #7  
Old 5/30/07, 11:59 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: ungrounded outlets!

Quote:
Originally Posted by jbreazeale
I might add that grounding is desirable wherever computer equipment is to be located

MAN........how come my LapTop has no grounding plug on it's cord....maybe that is why my computer screens keep cracking...thehehehe



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 5/30/07, 1:17 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 197
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

That was very flippant of you Paul.

I made reference to a "conductor strip" in AC and normally you pick me up on this. It is not a conductor strip but just a piece of metal to ensure the integrity of the outer coating. Unlike you to let this pass!
Reply With Quote
  #9  
Old 5/30/07, 2:07 PM
gmaher gmaher is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Fargo, ND
Posts: 97
Please Note: gmaher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

This duplex has plastic covered cables coming into the electric service panels from all circuits, there are no wires coming in encased in metal conduit, solid or flexible. Yes, I believe the grounded outlets were probably installed just because they were cheaper, or the person doing it did not know exactly what he was doing, just enough to be dangerous.
Now I've got another "apartment" to do; a four-plex. Wonder what I'll find there!
Thanks guys.
George Maher
Home - Safe Home, L.L.C.
Fargo, ND
Reply With Quote
  #10  
Old 5/30/07, 5:59 PM
lcapaul's Avatar
lcapaul lcapaul is offline
Active Poster
 
Join Date: Jun 2005
Location: Rathdrum, ID
Posts: 1,598
Please Note: lcapaul is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

Maybe this will help

http://www.icgov.org/housing/documents/wiringalts.pdf
Reply With Quote
  #11  
Old 6/1/07, 1:02 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

Paul...wy u dis me, bro? u no dat be gud idee put dem grouns on dem puters!
De lawd gon' strike u down!
Reply With Quote
  #12  
Old 6/2/07, 8:24 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: ungrounded outlets!

Quote:
Originally Posted by Ian Gills
That was very flippant of you Paul.

I made reference to a "conductor strip" in AC and normally you pick me up on this. It is not a conductor strip but just a piece of metal to ensure the integrity of the outer coating. Unlike you to let this pass!
it's all good fella......we all make mistakes..thehehe...but now you have to define "flippant" for me...I am from Virginina you know.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 6/2/07, 8:26 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: ungrounded outlets!

Quote:
Originally Posted by jbreazeale
Paul...wy u dis me, bro? u no dat be gud idee put dem grouns on dem puters!
De lawd gon' strike u down!
lol....man you know I love ya...even if your ground issue cracked my computer screen...lol

No actually...they called me yesterday....strangest thing...I sent the laptop for a crack in the screen...a SMALL one and they said they had to replace the screen which I knew they would...but they said the mother board did not pass inspection either....go figure.....so they replaced that also...now I am worried about this Toshiba.....yikes....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 6/3/07, 12:27 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

Paul, you da guru. We all know that!
Reply With Quote
  #15  
Old 6/3/07, 1:15 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 1,756
Default Re: ungrounded outlets!

George -

Let me throw out a comment we might make in our reports that would explain the condition to an electrician.

"Ungrounded 3-prong electrical outlets were noted at many locations throughout the building. Have a competent and licensed electrician review the electrical system, the conditions and then repair or replace as needed to properly correct any electrical problems".
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Properly Testing GFCI Outlets tchristopher Electrical 17 3/17/07 12:19 PM
Replacing 2-prong outlets with GFCI outlets kshepard Electrical 7 6/24/06 7:58 AM
Two prong outlets and GFCI's crichiii Electrical 8 3/15/06 11:41 PM
20 amp with 15 amp outlets abishop Electrical 32 1/31/06 5:21 PM


All times are GMT -4. The time now is 1:54 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts