Default Re: ungrounded outlets!

Quote:
Originally Posted by dbowers
"Ungrounded 3-prong electrical outlets were noted at many locations throughout the building. Have a competent and licensed electrician review the electrical system, the conditions and then repair or replace as needed to properly correct any electrical problems".
ANY electrical problems? That's casting a pretty broad net. Maybe that's what you intended?
Reply With Quote
  #17  
Old 6/3/07, 4:32 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

How about this one:

"The system of branch circuits in the home is an older two-wire, ungrounded system. This was the norm at the time the home was built. Modern branch circuit wiring is a three-wire system which provides a means of grounding each device on each circuit of the home. This provides extra protection against the possibility of shock hazard. While the present system is not considered defective, it is advisable in the interest of safety to upgrade. The least expensive method would be to install GFCI receptacles at the first device in each branch circuit, which will afford protection to the rest of the circuit. You may also wish to consider re-wiring of branch circuits. Consult a licensed electrician on any matters concerning wiring issues.
Reply With Quote
  #18  
Old 6/3/07, 5:31 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: ungrounded outlets!

ungrounded outlets!6/2/07 11:57 PMSeems we have a COWARD in the house..........Baby Coward....You know who you are....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 6/3/07 at 5:41 PM..
Reply With Quote
  #19  
Old 6/3/07, 10:04 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,307
Default Re: ungrounded outlets!

What is wrong with installing good (used or new) old two prong outlets like were in it on day one??

Rlb
Reply With Quote
  #20  
Old 6/3/07, 11:41 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: ungrounded outlets!

It is an option...and your perogative as well



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #21  
Old 6/4/07, 12:49 PM
dmcauley's Avatar
dmcauley dmcauley is offline
Active Poster
 
Join Date: Jan 2006
Location: Hoffman Estates, IL
Posts: 855
Please Note: dmcauley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

Jimmy,
Great post! Mind if I use this language? Been looking and working on this type of language for some time. Thanks!
Reply With Quote
  #22  
Old 6/4/07, 2:18 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

Sorry to interrupt
Quote:
Originally Posted by pabernathy
MAN........how come my LapTop has no grounding plug on it's cord....
The 2-prong laptop cord feeds a transformer. A low voltage secondary winding supplies power to the laptop. No direct connection to wall circuit. The guru knows this, but got distracted.

The general reason for grounding electronics is to carry off static charges which can wipe out sensitive computer chips. Although I believe they are making them more robust now than they were even 10 years ago.
Now back to....
Reply With Quote
  #23  
Old 6/4/07, 4:18 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

Paul....Why in the world would you get a brownie for anything said in this thread???? At the risk of recieving one myself....geeeeezze!!

Dennis: Feel free to use that comment. Some might argue that, since lots of homes of that era, if not most, have lighting/receptacle circuitry, tripping of the GFCI would put the lights out, too. I don't see this as much of a problem. I know the realtors like that comment better than "old wiring. need new. call sparky." The comment is explanatory, and doesn't unnecessarily alarm potential buyers. They are informed, and know they have viable options, among which is to simply leave it alone. Now, loose, worn out receptacles is another issue....
Reply With Quote
  #24  
Old 6/8/07, 8:20 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

Well, several days later I check, and sure enough, I got a brownie. Or a reddie. Or something. Oh, well.
Reply With Quote
  #25  
Old 6/9/07, 12:43 AM
Vince Santos's Avatar
Vince Santos Vince Santos is online now
InterNACHI Member
 
Join Date: Mar 2005
Location: Canton, MI - Serving Souteast Michigan
Posts: 1,746
Default Re: ungrounded outlets!

I believe the three prong outlets were installed because plenty of things you buy have a three prong plug making it necessary to have a three prong receptacle.




One or more open ground, three-pronged electric receptacles were found. This is a safety hazard due to the risk of shock. A qualified electrician should evaluate and make repairs as necessary. For example, replacing receptacles or correcting wiring circuits.

Grounding type receptacles began being required in residential structures during the 1960s. Based on the age of this structure and the presence of 2-pronged receptacles in some areas of this structure, an acceptable repair may be to simply replace the ungrounded 3-pronged receptacles with 2-pronged receptacles. However the following appliances require grounding type receptacles:


Computer hardware
Refrigerators
Freezers
Air conditioners
Clothes washers
Clothes dryers
Dishwashers
Kitchen food waste disposers
Information technology equipment
Sump pumps
Electrical aquarium equipment
Hand-held motor-operated tools
Stationary and fixed motor-operated tools
Light industrial motor-operated tools
Hedge clippers
Lawn mowers

This list is not exhaustive. Grounded circuits and receptacles should be installed in locations where such appliances will be used.



Vince Santos
StepByStep Home Services LC
(734) 748-9584
Providing Home Inspection Services to Southeast Michigan
facebook
ITA Trained and Certified

Reply With Quote
  #26  
Old 6/9/07, 1:05 AM
ekartal6 ekartal6 is offline
Active Poster
 
Join Date: Oct 2006
Location: Schaumburg, IL
Posts: 1,094
Please Note: ekartal6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

Mark,

Dan's type of disclaimer gives inspectors more protection. Since the electrician is coming out anyway a brief look around doesn't hurt. Most electricians I've had out for a specific problem perform a mini-inspection of their own which to be honest makes me feel a whole lot better.
Reply With Quote
  #27  
Old 6/10/07, 5:52 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: ungrounded outlets!

There is an older type of romex that was manufactured with only two conductors, no ground. By code, you cannot install a three prong receptacle on a circuit that does not contain a ground. In a bathroom, a ground wire may be connected to a water pipe. As mentioned, a correctly labeled GFCI will also work.
John Evans
Reply With Quote
  #28  
Old 6/10/07, 6:04 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ungrounded outlets!

Quote:
Originally Posted by jevans
There is an older type of romex that was manufactured with only two conductors, no ground. By code, you cannot install a three prong receptacle on a circuit that does not contain a ground. In a bathroom, a ground wire may be connected to a water pipe. As mentioned, a correctly labeled GFCI will also work.
Oh, my! Almost every word of what you've stated is profoundly untrue. You can install a 3-prong receptacle on the end of an existing ungrounded cable if it is GFCI protected. You CANNOT use the water pipe as the equipment ground in the US, but it is still legal in Canada.
Reply With Quote
  #29  
Old 6/10/07, 7:18 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: ungrounded outlets!

Quote:
Originally Posted by rbennett
What is wrong with installing good (used or new) old two prong outlets like were in it on day one??

Rlb
Nothing, but around here they cost $4 to $5 each.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #30  
Old 6/10/07, 11:58 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: ungrounded outlets!

We can inspect and describe. We cannot ascribe motives for what we find.

Best to keep that in mind.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Properly Testing GFCI Outlets tchristopher Electrical Inspections 17 3/17/07 12:19 PM
Replacing 2-prong outlets with GFCI outlets kshepard Electrical Inspections 7 6/24/06 7:58 AM
Two prong outlets and GFCI's crichiii Electrical Inspections 8 3/15/06 11:41 PM