Default Ungrounded plugs

I have a selection in my report software when report on ungrounded three prong outlets that reads. If no ground is present “repair” can be as simple as filling the ground slot with epoxy. I have been questioning this and removing it from my reports. Is this a common recommendation that any of you use.
Reply With Quote
  #2  
Old 12/14/06, 7:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Ungrounded plugs

This goes against the listing of the receptacle. I have seen it done, but I do not endorse this practice nor would I recommend it.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 12/14/06, 7:12 PM
Kenneth Blair Kenneth Blair is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Jacksons Gap, AL
Posts: 47
Default Re: Ungrounded plugs

Should I remove this sentence from my recommendations?
Reply With Quote
  #4  
Old 12/14/06, 7:16 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Ungrounded plugs

Quote:
Originally Posted by kblair1
I have a selection in my report software when report on ungrounded three prong outlets that reads. If no ground is present “repair” can be as simple as filling the ground slot with epoxy. I have been questioning this and removing it from my reports. Is this a common recommendation that any of you use.
If the receptacle is a 3 hole version that is illegally done....because it is a 2 wire setup.....explain they can use a GFCI on the circuit and follow the requirments that allow you to do this......and they can leave the 3 prong plugs in....if not....other suggestion would be to tell them to remove them and replace back with 2 prong recepts.

If they wish to ground the receptacles for use with 3 prong plugs...thats an option also...but they need to seek a qualified electrical contractor for information on that.....do not overstep the suggestions.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #5  
Old 12/14/06, 7:18 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded plugs

I would replace it with, "Have a licensed electrician replace the ungrounded three prong outlet with a two prong ungrounded outlet" or "Have the circuit rewired with a proper ground"

Anatol
Reply With Quote
  #6  
Old 12/14/06, 7:19 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Ungrounded plugs

Anatol....don't forget the GFCI option......



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #7  
Old 12/14/06, 8:05 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded plugs

Paul,
Most people are concerned more about powering their computers than personal safety. I will add the gfci option to my list.

Thanks,

Anatol
Reply With Quote
  #8  
Old 12/19/06, 1:22 PM
Frank J. Buttermore Frank J. Buttermore is offline
InterNACHI Member
 
Join Date: May 2005
Location: Howell, MI
Posts: 16
Default Re: Ungrounded plugs

The GFCI option is really "OK" ?

(I always recommend having a qualified elec. further evaluate and leave it a that...)

I also just posted a similiar question on this MB.....maybe you'll see it.
Also, just visited your site for the 1st time and registered. I don't post a lot but have always gotten some great eduacational info from you, Paul.

Thanks!



Frank Buttermore
HTI Inspection Services, LLC
Howell, MI
www.htiinspectionservices.com
Reply With Quote
  #9  
Old 12/19/06, 9:18 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Ungrounded plugs

I have a local authority, that does not allow gfci's to protect ungrounded circuits. Meaning he wants it to be either two prong, or rewired with an equipment ground. This is a report from another electrician, since he had to explain what the AHJ just told them to do.

Might want to get to know your AHJ, so you can prepare your clients for R/R stuff.

Just thinking out loud.

tom
Reply With Quote
  #10  
Old 12/21/06, 9:02 AM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ungrounded plugs

Quote:
Originally Posted by pabernathy
Anatol....don't forget the GFCI option......
Paul,
Does using a GFCI receptacle in place of an ungrounded repectacle, in your opinion, satisfy the requirements of 250.114? What I'm asking is, if I replace all my 2 prong ungrounded receptacles with 3 prong receptacles that are GFCI protected and correctly labeled, can I, per 250.114, plug my refridgerator in to it and still meet code.
Reply With Quote
  #11  
Old 12/21/06, 9:48 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Ungrounded plugs

Quote:
Originally Posted by fbuttermore
The GFCI option is really "OK" ? I always recommend having a qualified elec. further evaluate and leave it a that...
What good does "further evaluation" do to your client? You have already done the "evaluation." Now it's time for correction.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 12/21/06, 11:13 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Ungrounded plugs

Quote:
Originally Posted by tdietrich1
I have a local authority, that does not allow gfci's to protect ungrounded circuits. Meaning he wants it to be either two prong, or rewired with an equipment ground.
I happen to believe anything in the way of uping the safety factor is acceptacle. I am not talking about an isolated circuit for a computer here...simply installing a GFCI to protect personal protection on 2 wire setups...NEC accepts it....and if the lessor of the BEST thing...I accept it.

So are you saying that a local AHJ is Re-Writing Code on his own time?....Quite Interesting as I believe I could fight that argument if I was local but alas......most do not question the AHJ....

Yep...get to know your local AHJ...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 12/21/06, 11:22 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Ungrounded plugs

Quote:
Originally Posted by smcarthur
Paul,
Does using a GFCI receptacle in place of an ungrounded repectacle, in your opinion, satisfy the requirements of 250.114? What I'm asking is, if I replace all my 2 prong ungrounded receptacles with 3 prong receptacles that are GFCI protected and correctly labeled, can I, per 250.114, plug my refridgerator in to it and still meet code.
Steve,

IN my view the requirements of 250.114 simple allow for the use of a listed double insulated appliances, motor-operated hand -held tools, stationary and fixed motor operated tools and os on as to not requiring an equipment grounding connection.




250.114 Equipment Connected by Cord and Plug.


Under any of the conditions described in (1) through (4),
exposed non
current-carrying metal parts of cord-andplug-
connected equipment likely to become energized shall
be grounded.



Exception: Listed tools, listed appliances, and listed equipment

covered in (2) through (4) shall not be required to be
grounded where protected by a system of double insulation
or its equivalent. Double insulated equipment shall be distinctively
marked.


(1) In hazardous (classi
fied) locations (see Articles 500
through 517)
(2) Where operated at over 150 volts to ground



Exception No. 1: Motors, where guarded, shall not be required

to be grounded.
Exception No. 2: Metal frames of electrically heated appliances,
exempted by special permission, shall not be required
to be grounded, in which case the frames shall be
permanently and effectively insulated from ground.


(3) In residential occupancies:
a. Refrigerators, freezers, and air conditioners
b. Clothes-washing, clothes-drying, dish-washing machines;
kitchen waste disposers; information technology
equipment; sump pumps and electrical
aquarium equipment
c. Hand-held motor-operated tools, stationary and



fi
xed motor-operated tools, light industrial motoroperated
tools
d. Motor-operated appliances of the following types:
hedge clippers, lawn mowers, snow blowers, and
wet scrubbers
e. Portable handlamps




I don't see where the NEC limits the acceptacles of a Fridge on a GFCI if the client so chooses...but it also states that if the above applies it does not need a ground as well. Either way in my mind they both comply.












Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 12/21/06 at 11:28 AM..
Reply With Quote
  #14  
Old 12/21/06, 5:08 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Ungrounded plugs

Quote:
Originally Posted by pabernathy
So are you saying that a local AHJ is Re-Writing Code on his own time?....Quite Interesting as I believe I could fight that argument if I was local but alas......most do not question the AHJ....
Not rewriting, just omitting where you can use a GFCI on an ungrounded circuit.

I guess it's his job to make 'stronger' 'safer' rules, to protect those who pay his salary.

Go figure....

tom
Reply With Quote
  #15  
Old 12/21/06, 5:30 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: Ungrounded plugs

I have this in my report --- it is compiled from various donors on this board and tell me what you think...


The use of three-pronged ground-type receptacles on a two-wire electrical system gives the impression that safety protection is present in the circuit, when in reality it is not. Older style two-pronged receptacles are still available and should be installed to eliminate this false sense of security. Three-pronged receptacles may be more convenient (and often less expensive), but are often installed without giving consideration to this situation.
The use of a three-pronged plug in an ungrounded receptacle can be a safety concern. The plug has the grounding provision for a reason and electrical appliances should always be used for the function they were intended to perform.
All such installations should be labeled “No Equipment Ground” on each receptacle that applies. Grounding of all “three-pronged” receptacles or protection with a Ground Fault Circuit Interrupter (GFCI) on each is recommended for safety reasons, prior to the close of escrow or after taking possession of the property.

“Two-pronged” outlets are not grounded and should never be used with a “three-pronged” plug. Adapters have been devised for this usage, but there is still no adequate ground and such adapters are not always safe. Until the electrical system is upgraded for “three-pronged” usage, it would be prudent to not use adapters, extension cords, or “three-pronged” plugs in any way. Consider that “three-pronged” plugs have been engineered for use with a “three-pronged” grounded receptacle.

http://www.cpsc.gov/cpscpub/pubs/524.html



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Ungrounded GFCI srinner Electrical Inspections 29 11/30/07 11:15 AM
Ungrounded system Paul Sss Electrical Inspections 2 4/30/07 11:32 AM
Ungrounded downstream GFCI scosta Electrical Inspections 17 3/9/07 9:00 AM
plugs Rafael Electrical Inspections 5 1/19/07 5:17 PM


All times are GMT -4. The time now is 4:34 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts