I was in a 1925 1-1/2 story home. One of the side attics was converted to a talk-in closet (better be short) but I found a romex feeder originating from an original 2-wire (K&T) receptacle and the ending higher up the wall with a 3 prong receptacle to power a TV. The feeder was stapled, but was a D-Y-I job. What is the opinion?

No, this was not an ungrounded GFI new receptacle.
Attached Thumbnails
unprotected-romex-walk-closet-romex1.jpg   unprotected-romex-walk-closet-romex2.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America)
  #2  
Old 4/23/09, 10:47 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Unprotected Romex in walk-in Closet

Branch Circuit, General-Purpose.
A branch circuit that
supplies two or more receptacles or outlets for lighting and
appliances.

Branch Circuit, Individual.
A branch circuit that supplies
only one utilization equipment.

Feeder.
All circuit conductors between the service equipment,
the source of a separately derived system, or other
power supply source and the final branch-circuit overcurrent
device.

What you are showing is a Branch Circuit just to be clear

Is it subject to physical damage? If yes, sleeve it in an approved raceway of the exposed portions to protect it. Is it secured to the box properly...can't tell. Is it supported not exceeding 4 1/2'...maybe, is it secured to the box? is their a BOX?...lol

Many potential variables with in the unknowns of this image....




Paul W. Abernathy
Reply With Quote
  #3  
Old 4/23/09, 11:00 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Unprotected Romex in walk-in Closet

It's a plaster and lath wall separating the bedroom from the closet. I belive the lower receptacle has a box since it is the original 2-wire receptacle. (K&T) is feeding this from the attic. You are correct, this is just a branch circuit feeding the receptacle that powers the TV on the upper bedroom wall.

Don't know if there is a box on the new receptacle. Taking off the cover plate is going beyond the SOP.

It could be subject to damage depending on how much stuff the client is going to stuff in the closet. A possible solution would be to have a licensed electrician enclose this in a vinyl raceway for protection but who am I to make suggestions like that LOL.

Thanks Paul.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #4  
Old 4/23/09, 11:20 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Unprotected Romex in walk-in Closet

I found a pic of the TV receptacle (the upper) from the bedroom side.
Attached Thumbnails
unprotected-romex-walk-closet-romex3.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #5  
Old 4/23/09, 11:35 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Unprotected Romex in walk-in Closet

Exposed electrical wiring inside the house would not pass muster here.

Call it out.
Reply With Quote
  #6  
Old 4/24/09, 12:10 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Unprotected Romex in walk-in Closet

Quote:
Originally Posted by bkelly2 View Post
Exposed electrical wiring inside the house would not pass muster here.

Call it out.
(A) Type NM.
Type NM cable shall be permitted as follows:
(1) For both exposed and concealed work in normally dry
locations except as prohibited in 334.10(3)
(2) To be installed or fished in air voids in masonry block
or tile walls

Now the issue ( without going over SOP...lol ) would be protecting it if it was determined to be subject to physical damage. I don't believe a strip of plastic would protect it......Code would call for :

334.15 Exposed Work.
In exposed work, except as provided
in 300.11(A), cable shall be installed as specified in
334.15(A) through (C).

(A) To Follow Surface.
Cable shall closely follow the surface
of the building finish or of running boards.

(B) Protection from Physical Damage.
Cable shall be
protected from physical damage where necessary by rigid
metal conduit, intermediate metal conduit, electrical metallic
tubing, Schedule 80 PVC conduit, or other approved
means. Where passing through a floor, the cable shall be
enclosed in rigid metal conduit, intermediate metal conduit,
electrical metallic tubing, Schedule 80 PVC conduit, or
other approved means extending at least 150 mm (6 in.)
above the floor.





Paul W. Abernathy
Reply With Quote
  #7  
Old 4/24/09, 12:12 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Unprotected Romex in walk-in Closet

Quote:
Originally Posted by gliebig View Post
It's a plaster and lath wall separating the bedroom from the closet. I belive the lower receptacle has a box since it is the original 2-wire receptacle. (K&T) is feeding this from the attic. You are correct, this is just a branch circuit feeding the receptacle that powers the TV on the upper bedroom wall.

Don't know if there is a box on the new receptacle. Taking off the cover plate is going beyond the SOP.

It could be subject to damage depending on how much stuff the client is going to stuff in the closet. A possible solution would be to have a licensed electrician enclose this in a vinyl raceway for protection but who am I to make suggestions like that LOL.

Thanks Paul.
lol....just bustin your chops fella.....lol. heck we could argue using a Suretest, Thermal Cam, Volt Meter and so on exceeds the SOP but whos looking right....



Paul W. Abernathy
Reply With Quote
  #8  
Old 4/24/09, 9:28 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Unprotected Romex in walk-in Closet

Quote:
Originally Posted by pabernathy View Post
Now the issue ( without going over SOP...lol ) would be protecting it if it was determined to be subject to physical damage. I don't believe a strip of plastic would protect it......Code would call for :

I've seen these type of materials used for cable and electrical raceways.

I would expect these to be acceptable.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #9  
Old 4/24/09, 6:58 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unprotected Romex in walk-in Closet

The ungrounded circuit should not have been extended. A new circuit with a grounding means should have been run.
Reply With Quote
  #10  
Old 4/25/09, 8:28 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Unprotected Romex in walk-in Closet

I would not unless it says it is listed to protect from physical damage...lol If the location is not subject to physical damage then sure....why not. Howewver, install NM Cable in it and it not be for physcal damage and well......thats another story.



Paul W. Abernathy
Reply With Quote
  #11  
Old 4/25/09, 4:14 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unprotected Romex in walk-in Closet

It is all a moot point anyway as Jim Port pointed out, as code prohibits extending an ungrounded circuit.
Reply With Quote
  #12  
Old 4/26/09, 1:36 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unprotected Romex in walk-in Closet

Quote:
Originally Posted by bkelly2 View Post
Exposed electrical wiring inside the house would not pass muster here.

Call it out.

Same here. Either remove it or redo it so the wire is inside the wall cavity.


www.MauiHomeInspections.com
Reply With Quote
  #13  
Old 4/28/09, 9:43 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Unprotected Romex in walk-in Closet

(C) Nongrounding Receptacle Replacement or Branch
Circuit Extensions.
The equipment grounding conductor
of a grounding-type receptacle or a branch-circuit extension
shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system
as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure
where the branch circuit for the receptacle or
branch circuit originates
(4) For grounded systems, the grounded service conductor
within the service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar
within the service equipment enclosure

FPN: See 406.3(D) for the use of a ground-fault circuitinterrupting
type of receptacle.



Paul W. Abernathy
Reply With Quote
Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America)
  #14  
Old 4/28/09, 10:00 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Unprotected Romex in walk-in Closet

Even though plaster can be a pain to work with as is concrete, I guarantee there were no steel reinforcing bars as described in 250.50! I called it a safety issue to be evaluated by a licensed electrician based on extending an ungrounded branch circuit.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
reason to walk the roof psiposs Exterior Inspections 64 5/13/07 11:55 PM
Romex wire connected to standard male plug. ghawley Electrical Inspections 2 3/2/06 1:35 PM


All times are GMT -4. The time now is 7:22 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts