Default Unusual Sub-Panel Wiring

Gents,

I saw an unusual method of wiring a sub-panel yesterday. The feed from the main panel is wired to the terminals of the 50 amp breaker in the sub-panel and not the normal Bus terminal lugs.

I assume that this is an attempt to create a "main" in a panel that does not have a main breaker attachment. The circuit is also protected by a 50 amp breaker in the Main Panel.

Is this acceptable?

Note: I am reporting the open knockouts.
Attached Thumbnails
unusual-sub-panel-wiring-img7.jpg  
Reply With Quote
  #2  
Old 1/5/06, 10:16 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,037
Default Re: Unusual Sub-Panel Wiring

The panel is being "back-fed" through the breaker. Not uncommon. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 1/5/06, 10:42 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unusual Sub-Panel Wiring

The backfed breaker should be fastened in place. 384-16 (g)
Reply With Quote
  #4  
Old 1/5/06, 10:47 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unusual Sub-Panel Wiring

In addition:

Markings on panelboards that employ plug-on units require the use of a hold-down kit when the units are back-fed and the field installed supply conductors are terminated on the plug-on unit. The marking indicates: “Back-fed _____ requires hold-down kit Cat. No._____ “ or the equivalent.

An identification of the applicable back-fed unit is specified in the first
blank-for example, circuit breaker, fused switch, or terminal kit; and the catalog number of the required hold-down kit is specified in the second blank.






Reference: UL Panelboard Marking Guide and Industry Standards




Back-Fed Devices



Plug-in-type overcurrent protection devices or plug-in type main lug assemblies that are back-fed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.



I don't see this "kit" in the picture?

This rule has been in the industry standards for at least 10 years, because of an electrocution..
Reply With Quote
  #5  
Old 1/5/06, 8:36 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Unusual Sub-Panel Wiring

Ok...Timothy...I am going to ask one question here not related to what has been posted.

Q: What size was the conductor that FED the panel shown here?

I will tell you why when you reply....Now i know what should be installed for the 50A breaker...and we all know the conductor can be larger...I just would like to know what size the wire was to this panel.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 1/5/06, 9:10 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 841
Default Re: Unusual Sub-Panel Wiring

Paul, you realy have me wondering what your going to say. I'm posting to track this thread in my email.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #7  
Old 1/5/06, 9:14 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Unusual Sub-Panel Wiring

lol.....well it really depends on what Timothy tells me here...lol

Besides.....I may have nothing as pictures are sometimes not great for thinking you see things....so I just want to know for piece of mind but I will wait for Timothy to let me know.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 1/5/06 at 10:00 PM..
Reply With Quote
  #8  
Old 1/6/06, 2:58 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 270
Default Re: Unusual Sub-Panel Wiring

Paul,

#6 copper THHN in plastic? (at least going in the ground and out of the ground) conduit buried - 4 leads - 50' from the main Panel.

The panel is mounted in a storage shed on a dock.

tg
Reply With Quote
  #9  
Old 1/6/06, 3:03 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Unusual Sub-Panel Wiring

Thanks Timothy......Next Question...

Is that GREEN TAPE wrapped around the Ground Wire?



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 1/6/06, 3:16 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 270
Default Re: Unusual Sub-Panel Wiring

Paul,

No, it is pvc insulation.

tg
Reply With Quote
  #11  
Old 1/6/06, 3:27 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Unusual Sub-Panel Wiring

Cool........thats why I did not want to post anything and wanted to ask the question because pictures sometimes dont tell the story...with the BRIGHT color of that cable....I have only seen it that bright when it was wrapped with Green Tape......which in the NEC would not be allowed on 6AWG and smaller cables....The risk of that is someone later can come along later and remove the tape and screw something up.

Anyway......I have learned...asking the questions is better than just posting since I could not zoom in on the picture....looked like tape sticking up on the end about 1 inch before it goes into the terminal block.

Anyway.......Just wanted to check....



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 1/6/06, 3:37 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 270
Default Re: Unusual Sub-Panel Wiring

Thanks for the info. Joe & Brian, I KNEW that something didn't look right. Thanks for the reminder.

Around here, a back-fed breaker is usually a DIY emergency generator connection point.

Thanks again, TG
Reply With Quote
  #13  
Old 1/10/06, 2:05 AM
Joseph Kormos's Avatar
Joseph Kormos Joseph Kormos is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Medinah, IL
Posts: 643
Default Re: Unusual Sub-Panel Wiring

It also looks as if a knock out is missing from the top of the box, and the copper pipe should also be capped just in case it is just attached to a shut off valve, and if the valve leaks...

Joe
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Electrical Safety Foundation International Links jtedesco1 Electrical 5 12/8/07 4:10 PM
Sub Panel Wiring tmartens Electrical 4 2/27/07 11:56 PM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 11:22 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts