Default Upgrade 60 amps to 100 amps

Looking for some advice, I did an inspection for a friend a couple of weeks ago and found the following with the electrical service. It is a 900 sq ft cottage style bungalow, it has 3/0 copper SEC coming in rated up to 110 amps if I am not mistaken, Main panel is rated to 125 amps , Main breaker is a double pole 60 amp breaker. Seller and agent claimed the home had 120 amp service 2x60= 120, I advised them that it was actually 60 amps not 120 amps that what is marked on the breaker is that breakers amperage and you do not multiply by 2 for a double pole breaker. Anyways my friend has been shopping for insurance and only one company will insure him because it is only 60 amp service and not 100 amp and that company is at an increased premium. My question is given the stats above would changing the 60 amp breaker to a 100 amp breaker be sufficient to upgrade this to 100 amp service or does more have to be done. I am not an electrician and I don't pretend to be, so any experienced advice would be welcome. Thank You.



JERRY BETTENCOURT
HOMETEST HOME INSPECTIONS
www.hometestinspections.com
www.hamiltonthermalimaging.com
hometestinspections@hotmail.com
I will keep my thoughts positive because my thoughts become my words. I will keep my words positive because my words become my actions. I will keep my actions positive because my actions become my values. I will keep my values positive because my values become my DESTINY!
United Family Martial Arts Student Creed
Reply With Quote
  #2  
Old 7/17/08, 7:41 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,068
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Upgrade 60 amps to 100 amps

Hi Jerry,

If you are correct about it being a Copper 3/0 SEC then that is rated for 200 amps If the panel is rated for 125 amps then that is the maximum size of a replacement main breaker.

It would need checking out properly but it sounds like it's do-able.

Regards

Gerry



"Never underestimate the difficulty of changing beliefs with false facts."
(some RWNJ not called Mike)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 7/17/08, 7:52 PM
Jerry Bettencourt Jerry Bettencourt is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Stoney Creek, ON
Posts: 516
Default Re: Upgrade 60 amps to 100 amps

Gerry,

You are correct I did not re-check the report before I posted this, it is 3 awg copper service conducter that would be rated up to 110amps not 3/0 copper that would service up to 225 amps according to the table I have. It indeed is 3 awg not 3/0. Thank you for your reply.



JERRY BETTENCOURT
HOMETEST HOME INSPECTIONS
www.hometestinspections.com
www.hamiltonthermalimaging.com
hometestinspections@hotmail.com
I will keep my thoughts positive because my thoughts become my words. I will keep my words positive because my words become my actions. I will keep my actions positive because my actions become my values. I will keep my values positive because my values become my DESTINY!
United Family Martial Arts Student Creed
Reply With Quote
  #4  
Old 7/17/08, 8:10 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,068
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Upgrade 60 amps to 100 amps

Quote:
Originally Posted by jbettencourt
Gerry,

You are correct I did not re-check the report before I posted this, it is 3 awg copper service conducter that would be rated up to 110amps not 3/0 copper that would service up to 225 amps according to the table I have. It indeed is 3 awg not 3/0. Thank you for your reply.
Hi Jerry, sounds like a 100 amp breaker would work fine

Regards

Gerry



"Never underestimate the difficulty of changing beliefs with false facts."
(some RWNJ not called Mike)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 7/17/08, 9:07 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 964
Default Re: Upgrade 60 amps to 100 amps

Quote:
Originally Posted by jbettencourt
Looking for some advice, I did an inspection for a friend a couple of weeks ago and found the following with the electrical service. It is a 900 sq ft cottage style bungalow, it has 3/0 copper SEC coming in rated up to 110 amps if I am not mistaken, Main panel is rated to 125 amps , Main breaker is a double pole 60 amp breaker. Seller and agent claimed the home had 120 amp service 2x60= 120, I advised them that it was actually 60 amps not 120 amps that what is marked on the breaker is that breakers amperage and you do not multiply by 2 for a double pole breaker. Anyways my friend has been shopping for insurance and only one company will insure him because it is only 60 amp service and not 100 amp and that company is at an increased premium. My question is given the stats above would changing the 60 amp breaker to a 100 amp breaker be sufficient to upgrade this to 100 amp service or does more have to be done. I am not an electrician and I don't pretend to be, so any experienced advice would be welcome. Thank You.
Hi Jerry,

I would use the weakest link which is the 60 Amps Breakers; therefore a 60 Amps entrance.

Not to say that a 100 Amps Breakers wouldn't work...



Marcel Gratton # NCA00376, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
to many amps shegert Electrical 6 7/19/08 10:30 PM
service upgrade Mike Whitt Electrical 3 1/25/08 1:43 PM
Canadian homeowners can be paid to upgrade rcooke Canadian Inspectors 2 9/20/07 7:19 AM


All times are GMT -4. The time now is 7:35 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts